<font size=3>Brian:<br><br>
We reviewed the installation instructions and found them lacking in a few
regards:<br><br>
1. The Xantrex system allows for bypass of the inverters only with
external devices and they do not allow choosing between inverter, utility
*or* generator.<br><br>
2. The diagram on page 2-36 shows nine 2 pole breakers.&nbsp; Today I
counted the spaces available for breakers and again this evening via job
photographs, and I see only room for eight 2 pole breakers.&nbsp; I will
check this again tomorrow, but I do not think the Xantrex suggested
breaker arrangement will actually fit.<br><br>
I have been toying with this dilemma.&nbsp; With 5 breakers on the
output, one could contrive to select between utility, generator *or*
inverter for output bypassing.&nbsp; This, unfortunately, leaves
inadequate room for inverter input breakers.<br><br>
I think the ideal scenario would use two Power Distribution Panels.&nbsp;
One would be dedicated to AC and the other to DC (this would be even ore
ideal if the PDP did not cost an unbelievable amount of money).&nbsp; A
power flow diagram of how Xantrex suggests this be wired and also of
another concept I have been developing are on our web site at:&nbsp;
<a href="http://millersolar.com/practices/Technical_Procedures/xw/3XW.html" eudora="autourl">http://millersolar.com/practices/Technical_Procedures/xw/3XW.html<br><br>
</a>Thanks for the input.<br><br>
William Miller<br><br>
<br>
At 10:00 PM 4/28/2009, you wrote:<br>
<blockquote type=cite class=cite cite>Content-Language: en-US<br>
Content-Type: multipart/alternative;<br>
<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab>boundary=&quot;_000_69FFF3377EEF8747A4FDE2CC20CD1DEDA66442A92DREDEXCHaeesol_&quot;<br><br>
William,<br>
&nbsp;<br>
In the Xantrex \u201cXW Power System Installation Guide\u201d, pages 2-34 to 2-37,
there is a parts list and some diagrams on the wiring of a 3-inverter
system. The parts list calls for two 5 ft (62\u201d hole-to-hole) 4/0 battery
cables to connect the third inverter up to the Distribution Panel.<br>
&nbsp;<br>
Also shown is the use of an external bypass switch to make up for the
lack of enough AC breaker spaces in a single Distribution Panel. It shows
a breaker/interlock panel, but a 2-pole manual transfer switch will also
work. Either way, it should be rated for at least 200A.<br>
&nbsp;<br>
Brian Teitelbaum<br>
AEE Solar<br>
&nbsp;<br>
&nbsp;<br>
&nbsp;<br>
<b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
<b>On Behalf Of </b>William Miller<br>
<b>Sent:</b> Tuesday, April 28, 2009 8:49 PM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> [RE-wrenches] 3 Xantrex XW system<br>
&nbsp;<br>
Friends:<br><br>
We are in the midst of installing our first 3 XW system.&nbsp; Several
questions arose during our work today.&nbsp; I appreciate input any of
you might have.<br><br>
1.&nbsp; Did you find the leads from the Xantrex connection ki long
enough for the third inverter?<br><br>
2.&nbsp; How many AC sources did you connect?<br><br>
3.&nbsp; Did you provide bypass capabilities?<br><br>
4.&nbsp;&nbsp; How did you interlock the bypass capabilities?<br><br>
5.&nbsp; Did you use one or two Power Distribution Panels?<br><br>
6.&nbsp; Can you offer any advice on how best to connect this
equipment?<br><br>
Thanks in advance.<br><br>
William Miller<br>