<font size=3>Geoff:<br><br>
We installed a large-ish system for the state of California
(<a href="http://mpandc.com/Portfolio/Commercial/Cal_Trans/cal_trans_gorda.html" eudora="autourl">http://mpandc.com/Portfolio/Commercial/Cal_Trans/cal_trans_gorda.html</a>)&nbsp;
This is a location with homes, an office and workshops that has had a
generator or two running 24/7 for decades.<br><br>
The premise was that a large generator system could handle the peak loads
and the battery based PV system would handle the off peak loads.&nbsp;
There was no load segregation, but instead the design relied on a
&quot;quick response,&quot; multi sync-able generator system.&nbsp; The
three generators were to start, sync and assume any loads in excess of
those that the inverters were capable of handling.<br><br>
The premise was fatally flawed.&nbsp; There is no generator system that
can respond to loads quickly enough.<br><br>
There is a design philosophy that was violated on this project:&nbsp; Any
power system needs to be sized large enough to handle the maximum load
that is possible to apply to the system.<br><br>
We are now contracted to double the inverter capacity.&nbsp; The load
studies were re-run but are still inconclusive.&nbsp; We agreed to the
capacity of our installation, but we made no commitment as to the ability
of our equipment to handle unknown loads.<br><br>
Load studies are critical to every design and each power source needs to
adhere to the results of those studies.<br><br>
Good luck.<br><br>
William Miller<br><br>
<br><br>
<br><br>
At 06:48 PM 3/12/2009, you wrote:<br><br>
<blockquote type=cite class=cite cite>Thanks Drake and 
others...<br><br>
&nbsp;<br><br>
I will ping SMA on this... and perhaps with utility &quot;special
case&quot; approval a non-typical window could be allowed (with
additional anti island logic switchgear)...<br><br>
&nbsp;<br><br>
keep on slingin panels everyone!<br><br>
For a brighter energy future,<br><br>
Geoff Greenfield<br>
President<br>
Third Sun Solar &amp; Wind Power Ltd.<br>
340 West State Street, Unit 25<br>
Athens, OH 45701<br><br>
740.597.3111&nbsp;&nbsp;&nbsp;&nbsp; Fax 740.597.1548<br>
<a href="http://www.third-sun.com/" eudora="autourl">www.Third-Sun.com</a><br><br>
Clean Energy - Expertly Installed<br><br>
<br><br>
<br><br>
<br>
----- &quot;Drake Chamberlin&quot;
&lt;drake.chamberlin@redwoodalliance.org&gt; wrote: <br>
&gt; This should be possible.&nbsp; I have discussed what it might take
to set <br>
&gt; up a system like that in the Gambia, with wind generators.&nbsp; It
would <br>
&gt; take a control system with differential current sensors and other
<br>
&gt; features.&nbsp; The UL 1741 specifications would probably need to be
<br>
&gt; opened up on multiple direct grid tie inverters. There would be a
<br>
&gt; practical limit on the percentage of feed to the generator mini
grid.<br>
&gt; This being said, I've not received much encouragement with this
<br>
&gt; idea.&nbsp; There are a lot of factors to consider.<br>
&gt; At 09:35 AM 3/11/2009, you wrote:<br>
&gt; &gt;Undoubtably many of us are getting interesting project requests
as <br>
&gt; &gt;folks want to sprinkle magic stimulus dust on things to make
solar <br>
&gt; &gt;panels grow...<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;We have a project with a huge electrical load, pumping water for
a <br>
&gt; &gt;medium sized city.&nbsp; They want solar... great.&nbsp;
Easy.<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;They had a power outage and kept running with 2.6 MW of diesel
<br>
&gt; &gt;generators.&nbsp; They are interested in solar's ability to do
<br>
&gt; &gt;&quot;backup&quot;.&nbsp; I don't think that many batteries will
fit in my pickup <br>
&gt; &gt;truck, and I hate working with 300/0 wire.<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;<br>
&gt; &gt;QUESTION:&nbsp; (and maybe its an easy one and the SMA guys will
say, <br>
&gt; &gt;sure, we did that in Greece).&nbsp; Is it viable to set up a
micro-grid <br>
&gt; &gt;in this scenario and run an island-mode, with available solar
<br>
&gt; &gt;reducing the genny plant demand?&nbsp; Should I just say
&quot;forget it&quot; or, <br>
&gt; &gt;at this MW scale, would the switchgear and effort be
practical?<br>
&gt; &gt;<br>
&gt; &gt;</font></blockquote></body>
</html>