<font size=3>Jeff:<br><br>
Can your client maintain batteries?<br><br>
The IBE 85N-13 is 627 AH of FLA.&nbsp; One string is too small, two
strings is too large, so you may need to keep looking.&nbsp; I would add
that we have had only one failure in 20 plus years of use.<br><br>
The MK-8A8DLTP&nbsp; Deka is 245 amp hours of AGM.&nbsp; Three strings
would meet your requirements and is within most installers recommended
string maximum.&nbsp; We have had excellent results with the VRLA
batteries although the oldest sites are floating on grid.&nbsp; The
off-grid installations we have (that cycle daily) are newer so we have
less data.<br><br>
Good luck.<br><br>
William Miller<br><br>
<br>
At 08:45 PM 3/5/2009, you wrote:<br>
</font><blockquote type=cite class=cite cite><font face="arial" size=2>Hi
wrenches,<br>
I am looking for a quality battery to use in the 700-900 amp hour
range.&nbsp; Anyone have any suggestions as to a good product in this
range?<br>