<div>Seems that I remember that the APC and other backups are not a sine wave but a modified wave? But it's been a while.</div>
<div> </div>
<div>Bob <br><br></div>
<div class="gmail_quote">On Wed, Feb 11, 2009 at 9:52 AM, Howie Michaelson <span dir="ltr"><<a href="mailto:howie@suncatchervt.com">howie@suncatchervt.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">I installed an off-grid system with identical symptoms:<br><br>OB VFX 3648 dual stack<br>Buderus GB142-24<br>
Kohler 12 kW propane genny<br><br>The boiler runs fine on the inverter power, but will occasionally error<br>out (6A) and shut down while the generator is running (usually after it<br>has been on for hours). The plumber installed an APC uninterruptable<br>
power supply/surge suppressor (not sure of the model) before the boiler,<br>but when running on the internal inverter, the symptoms seemed to get<br>worse. When running on just the surge suppressor portion, the symptoms<br>
were the same as if the APC wasn't in-line. We've checked the grounding<br>at the genny, made sure the neutral was isolated except for the main<br>panel, still the same problem. Seems this is a Buderus issue (or at least<br>
not an inverter one) - see:<br><br><a href="http://www.buderus.net/Support/TechnicalInfoForums/tabid/132/forumid/15/threadid/4334/scope/posts/Default.aspx" target="_blank">http://www.buderus.net/Support/TechnicalInfoForums/tabid/132/forumid/15/threadid/4334/scope/posts/Default.aspx</a><br>
<br>I haven't been able to make the boiler run reliably when the genny is on,<br>which is a problem in our climate, when the client goes away in the<br>winter...<br><br>Howie<br>--<br>Howie Michaelson<br>NABCEP Certified Solar PV Installer<br>
<br>Sun Catcher, LLC<br>Renewable Energy Systems Sales and Service<br>VT Solar & Wind Incentive Program Partner<br><a href="http://www.suncatchervt.com/" target="_blank">http://www.SunCatcherVT.com</a><br>(cell) 802-272-0004<br>
(home) 802-439-6096<br>
<div class="Ih2E3d"><br><br>On Wed, February 11, 2009 7:47 am, Darryl Thayer wrote:<br>> Some of the hot surface ignitors I have seen draw a lot of current, in the<br>> order of amps. I would expect the inverter to drop out if it were<br>
> overloaded however. Also does the magnum drop voltage at very low loads?<br>> Where the furnace controls can not function due to low voltage or poor<br>> wave shape.<br>><br>> Darryl<br>><br>><br>>><br>
</div>
<div class="Ih2E3d">>> This may be true about high frequency switching interfering<br>>> with something, but I believe the problem with this ignitor<br>>> is that it is a very poor design. Judging by what I read on<br>
>> their company forum, it doesn't look like they have a<br>>> clue about<br>>> this problem. Maybe you can go inside the Buderus and<br>>> filter something there or maybe you can fine another product<br>
>> to try ?<br>>><br>>> boB<br><br><br><br></div>
<div>
<div></div>
<div class="Wj3C7c">_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>Options & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>