<font size=3>Peter:<br><br>
I have built several of these portable display units.&nbsp; Allow me to
free associate some issues:<br><br>
1. Who will deploy unit?&nbsp; Our trailer has been damaged more than
once due to improper hitching, towing, backing, and mis-handling.&nbsp;
If you are at every event, then no problem, but it ties up your
weekends.&nbsp; If others will tow trailer, write up SOPs and get a
signature assuming liability.<br><br>
2. Will the unit be able to solar charge while parked?&nbsp; We have
developed a method of folding panels for travel and storage where most of
the panels are exposed to sunlight and can keep the unit charged.&nbsp;
It was parked in a spot for a while with limited sun exposure in the
winter and this caused problems with self discharge, but we remedied that
by revising SOPs.<br><br>
3. How do you handle loads in excess of capacity?&nbsp; This applies to
loads exceeding the inverter capacity and those exceeding storage
capacity.<br><br>
The last time our unit went out (to the Wiener Dog Races) it was parked
by the promoters in the shade.&nbsp; It was supposed to power a PA only
but the hot dog vendor plugged in and depleted the batteries by
11:00AM.&nbsp; The unit was scheduled to power a fundraiser that night,
but I was unable to retrieve the unit due to it being surrounded by
booths until late that afternoon.&nbsp; This lead to frantic grid
charging to get batteries recharged in time for the evening 
gig.<br><br>
Other times, we have powered lights for a street concert.&nbsp; During
the summer, twilight comes later and we have adequate battery
capacity.&nbsp; During winter months, twilight is earlier and there is
not enough battery capacity.&nbsp; The loads are somewhat greater than 20
amps.&nbsp; We have access to one 20 Amp circuit, but when applied to the
Outback inverter, the inverter transferred loads and we tripped the 20
amp breaker which is behind a locked door.&nbsp; I wish we had used a
Xantrex inverter with true generator support so the inverter could assist
and defray battery loss without applying the entire load to the input
circuit.&nbsp; We eventually installed a 24 volt battery charger that can
charge batteries from a current limited AC Source and increase battery
life with a given load.<br><br>
4. Stability when parked:&nbsp; We have had a trailer blow over with
panels tilted up.&nbsp; We still need some type of outriggers.<br><br>
5. Stability when towing:&nbsp; You need side to side balance and a 60/40
front to back weight distribution.&nbsp; We numbered all components of
any appreciable mass and then wrote a simple spreadsheet to calculate
moment (mass times distance from axle, plus in front, minus in
back).&nbsp; We moved batteries around until left to right moment
difference was near zero and front to back moment was near a 60/40 ratio
with the hitch positive.&nbsp; I have a friend that supports weight and
balance software for the maritime industry and he ratified this
process.<br><br>
Good luck,<br><br>
William Miller<br><br>
At 08:49 AM 1/19/2009, you wrote:<br>
<blockquote type=cite class=cite cite>We are designing a &quot;Mobile
Solar Power Center&quot; to power Eco-Events and the<br>
like in Southern California. We will have 1,600 Wp of solar panels, 6 kWh
of<br>
24 V AGM battery backup and a 1kW / 120 VAC inverter. I am designing
the<br>
system from scratch, and I wondered if anyone else out there has 
put<br>
together a similar system and was inclined to share notes. When I'm
finished<br>
I'd be glad to do the same.<br><br>
One stumbling block I have right now, is to find a DC rated 70A
in-line<br>
fuse, to put between the battery bank and the input to the inverter. 70A
may<br>
seem an odd value, but it is the best choice for the surge rating of
the<br>
inverter I'll be using (Xantrex Prosine 1000). Does anyone have a source
for<br>
DC-rated in-line fuses? <br><br>
Thanks in advance, -Peter<br><br>
Peter T. Parrish, President<br>
California Solar Engineering, Inc.<br>
820 Cynthia Ave., Los Angeles, CA 90065<br>
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885<br>
CA Lic. 854779, NABCEP Cert. 031806-26<br>
peter.parrish@calsolareng.com <br><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a></font></blockquote></body>
</html>