<font size=3>Nick:<br><br>
I just finished the first phase of a large project for the state of
California using a quad stack.&nbsp; The generators are three phase but
the campus is all split phase.&nbsp; They were able to center tap one
winding of the generators and use the two phases on either side.&nbsp; I
was skeptical, thinking that the phase angle would be 120 degrees, not
180 degrees as required for the quad stack, but an oscilloscope proved
the 180 degree phase angle.&nbsp; The quad stack is happy with the two
phases of the three phase.&nbsp; Let me repeat that this is only possible
because the winding on the generator between the two phases we are using
was center tapped and bonded to create a neutral.<br><br>
I was told that many large three phase generators have a 12 winding
configuration.&nbsp; I belive that this configuration will allow the
center tap to be made.&nbsp; You should verify this will not void any
warranties or damage the generator.<br><br>
The down side is that there is some loss of generator capacity, but it
was far less than I predicted, somewhere about 80% of name
plate.<br><br>
I have pictures of the PV and inverters on our web site, but not of the
generators.&nbsp; I think they are 30 KVA Kohlers.&nbsp; As a side note,
the generator system is very unique.&nbsp; There are three generators and
they can run one, two or three in synchronization, as needed.&nbsp; Also,
the inverter system does not through-put power.&nbsp; The generator
control system switches the generators off the main buss moments before
switching the inverters onto the main buss.&nbsp; To further complicate
things, the generators must be loaded at close to capacity at all times
to reduce emissions.&nbsp; There is a load bank that switches in and out
to accomplish this.&nbsp; It took Kohler Corporate many trips to get this
working, and I'm not sure I really belive they have all of the bugs out
yet.<br><br>
Good Luck,<br><br>
William Miller<br><br>
<br>
At 09:03 PM 1/14/2009, you wrote:<br>
<blockquote type=cite class=cite cite>Hi Nick,<br><br>
Why you want the change from single to 3 phase?<br>
Pretty big difference that.<br><br>
<br>
jay<br><br>
peltz power<br><br>
<br>
On Jan 14, 2009, at 4:56 PM, Nick Houser wrote:<br><br>
<blockquote type=cite class=cite cite>Has anybody done&nbsp; (or even
TRIED) this?&nbsp; The Quad stack is exactly&nbsp; <br>
like page 20 of the manual. Owner<br>
refuses to let me convert the Quad panel to three phase as he won't&nbsp;
<br>
give up the forth inverter' contribution.<br>
Ditto repacing or converting the generator. Related question:&nbsp;
If&nbsp; <br>
the transformer is a viable option, how do<br>
I size it? Help. please, I'm running out of options. Nick
Houser,&nbsp;&nbsp; <br>
Off Grid Services, Powell River, BC<br>
offgridnick@telus.net&nbsp;&nbsp;&nbsp; 604-483-4898&nbsp; Fell free to
contact me off&nbsp; <br>
list, and Happy New Year. ALL!!!!!<br><br>
-- <br>
Using Opera's revolutionary e-mail client:
<a href="http://www.opera.com/mail/" eudora="autourl">http://www.opera.com/mail/</a><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br>
</blockquote><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>