<font size=3>Nik:<br><br>
Ian Woofenden mailed me the same letter which has apparently been
circulating on the internet of late.&nbsp; Ian asked for my response for
a potential column or at least a reply to a letter to the editor for Home
Power.&nbsp; Below is what I wrote back.&nbsp; If I missed any points, I
appreciate any feedback from my colleagues.<br><br>
There are valid concerns, in my opinion, that exist about fire fighter
safety.&nbsp; Unfortunately, the letter you forwarded is only partly
rational.&nbsp; In California, there are competing Fire Departments that
are attempting to create regulations for PV installs to accommodate fire
fighter safety concerns.&nbsp; The two top agencies are the Cal Fire and
the LAFD.&nbsp; Preliminary documents from both agencies are on our web
site under resources:&nbsp;
<a href="http://mpandc.com/resources/resources.html" eudora="autourl">http://mpandc.com/resources/resources.html</a>&nbsp;
They are near the top of the list.<br><br>
The implications of the roof edge set backs are severe.&nbsp; We did a
quick analysis of the 20 jobs we did previous to the issuance of these
preliminary standards and, of the residential jobs, about 90% would be
infeasible with the new setbacks.<br><br>
One of the agencies, I recall it was the LAFD, allowed quick release
hardware to suffice if minimum setbacks could not occur.&nbsp; We created
some concepts for quick release mounting and presented them to DPW, but
they never contacted us back.&nbsp; As more and more jurisdictions
require setbacks, I am hoping some manufacturer can take these concepts
and create a product that will allow installations closer to the roof
edges than either of the above requirements would allow.<br><br>
This is a topic that will be very important in the next year.&nbsp;
Thanks for brining it up.<br><br>
William Miller<br><br>
Ian:<br><br>
The firefighters letter states facts for the most part.&nbsp; The two
areas I disagree with is the length of time that a PV feeder remains
energized after being tarped and the presence of PV feeder voltages at
night.&nbsp; The time required for covered PV modules to de-energize
should be no greater than five minutes by statute and confirmed by
independent lab testing.&nbsp; After sunset PV voltage will not be
present.<br><br>
The 2005 National electrical code addresses these safety issues as
related to fire fighters by requiring the PV feeders either have a
disconnect located prior to the feeder entering the building envelope or
the feeders need to be inside a metallic conduit.&nbsp; I believe future
code editions may further improve safety by requiring minimum spacing
below roof surfaces for this conduit to be installed.<br><br>
Firefighters can be assured of safety from PV voltage hazards if they
follow two rules (in addition to turning off any disconnects
provided):&nbsp; 1. Do not break the modules, and 2. Do not cut through
metallic conduits.&nbsp; I can not comment on the likelihood of
electrocution by voltages following a stream of water, but I am sure
there is information out there on this issue.<br><br>
Ian, I hope this answers your questions.&nbsp; Please feel free to
reformat this to fit your needs.&nbsp; If my name will be on it, run it
by me for review.<br><br>
William Miller<br><br>
<br>
At 01:07 PM 1/5/2009, you wrote:<br>
<blockquote type=cite class=cite cite>I just got this email forwarded
from a coworker that volunteers as a firefigher. Your comments are
welcome:<br><br>
Forwarded Message:<br><br>
At this past Monday's Twp. Chief's meeting, I went to the presentation
put on by the State of NJ last night at Amwell Valley Fire concerning
solar panels and the danger they present to the Fire Service.<br><br>
The presentation lasted for about 2 1/2 hours and was what I believe time
well spent.&nbsp; It really opened my eyes to the potential danger and
problems they will be for us for any dwelling fire we will encounter
where they are present.&nbsp; I'm going to attempt to give everyone a
quick snapshot of what was covered.<br>
<br>
The thing to know with solar panels are that they cannot be shut down -
they are ALWAYS ENERGIZED.&nbsp; And they are energized with up to 600
volts of DC current.&nbsp; For example, you cannot put an ax through them
to open up a roof to vent - your putting the ax through 600 volts.&nbsp;
If fire is infringing upon solar panels on the roof it will compromise
the integrity of the panels.&nbsp; You then have 600 volts of live
electrical energy - and what don't you do when you have live electrical
energy? - you don't put water on it.&nbsp; Even if the roof burned
through and the panels fell into the structure, unless the panels were
destroyed (de-energized) by the fire and/or falling into the structure,
they can still have the potential to be live,they&nbsp; have to be
treated as such and have the potential of 600 volts of DC current.<br>
A basic solar system consists of:&nbsp; The solar panels themselves; a
combination box; a disconnect box; and a inverter.&nbsp; The panels all
feed into a combination box.&nbsp; The combination box (which is almost
always located on the roof) takes in all the energy and sends it to a
disconnect box.&nbsp; The disconnect box takes the energy and then sends
it into the inverter which converts the DC current into AC current.&nbsp;
>From there the AC energy &quot;pushes&quot; into the structure's normal
electrical system.<br><br>
The combination box has fuses in it that come from the solar panels
themselves.&nbsp; If you access that box, you can pull all the fuses
inside and &quot;kill&quot; anything after the combination box.&nbsp; But
remember the panels are still live and have up to 600 volts in
them.&nbsp; If you &quot;kill&quot; the energy at the disconnect box -
anything up to that box is still energized - the solar panels, the
combination box, the line going from the combination box into the
structure and into the disconnect box are all still energized.&nbsp; The
power company pulling the meter for normal service has no effect
whatsoever on the solar panel system - it is all still live and has up to
600 volts of DC current.&nbsp; The only &quot;good&quot; thing when it
comes to the disconnect box and the inverter is that they need to be
co-located with the normal service panel for the structure and each
should be marked as appropriate.<br><br>
Even if it's nighttime and the solar panels have not been exposed to
direct sunlight for several hours, they still are energized and can kill
you.&nbsp; It is estimated that the panels would need to be covered with
an opaque tarp for 7-10 days before the panels will
&quot;de-energized&quot; down to minuscule levels.&nbsp; (although the
handouts specify that this is an option for safety steps - it is not
accurate per the presenter)<br>
In closing there are people who have greater minds and resources than we
do in developing a process to safely handle fires which may involve these
systems - such as the NFPA, OSHA, etc.&nbsp; Per the presenter, the
situation - and these organizations, are now starting to become aware of
the potential problems.&nbsp; So far in the State of NJ, there is no
recorded injury to a Firefighter being caused by coming into contact with
a solar panel system.&nbsp; Ironically, New Jersey comes in 2nd when it
comes to solar panel system installations in the nation, behind
Califorina.<br><br>
The final question which was asked really put things in prospective -
someone asked that since Califorina is number one when it comes to Solar
Panel Syatem installations, &quot;...what do their Firefighters do when a
structure fire involves these systems?&quot;&nbsp; Answer was &quot;...
they let it burn!&quot;<br><br>
Please, I'm not suggesting that we adopt this strategy.&nbsp; But the
reality is - I really don't have an answer and it seems as if the Fire
Service industry, nor the Solar Panel Companies, don't either.<br><br>
Just - please be aware and please be careful if you roll up to a
structure where a solar panel system is installed - bottom line, if can
kill you.<br><br>
<br>
&lt;End Forwarded Message&gt;<br><br>
Is this even possible? &quot;Even if it's nighttime and the solar panels
have not been exposed to direct sunlight for several hours, they still
are energized and can kill you.&nbsp; It is estimated that the panels
would need to be covered with an opaque tarp for 7-10 days before the
panels will &quot;de-energized&quot; down to minuscule levels.
&quot;<br><br>
And are there documented cases where firefighters let a house burn
because it had PV on the roof?<br><br>
Thanks again,<br>
nik<br>