<div>The MPPT controllers have revolutionized how we can do off grid systems. Wider panel choices and greatly reduced wire cost. Have you ever run or remember running&nbsp;600 watts (or more) of 12 volt panels 150&#39; or so? It was going to&nbsp;take 4 huge wires to counter the voltage drop&nbsp;or move the building closer to the clearing!</div>

<div>&nbsp;</div>
<div>Having to ability to drop a higher panel voltage to battery voltage is a godsend.</div>
<div>&nbsp;</div>
<div>Thanks for the MPPT controllers,</div>
<div>&nbsp;</div>
<div>Bob Ellison</div>
<div>&nbsp;</div>
<div>&nbsp;<br><br></div>
<div class="gmail_quote">On Thu, Dec 11, 2008 at 7:55 AM, Wind-sun.com <span dir="ltr">&lt;<a href="mailto:windsun@wind-sun.com">windsun@wind-sun.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
<div bgcolor="#ffffff">
<div><font face="Calibri" size="2">For larger off grid systems - pretty much anything over 600 watts - we have been recommending only MPPT type controllers, such as the Outback &amp; Xantrex. Since they can match almost any panel size to any battery size, it has reduced our dependence on the often hard to get 12 volt panels.</font></div>

<div><font face="Calibri" size="2"></font>&nbsp;</div>
<div>..................................................................................................<br>Northern Arizona Wind &amp; Sun - Electricity From The Sun<br>Solar Discussion Forum: <a href="http://www.wind-sun.com/ForumVB/" target="_blank">http://www.wind-sun.com/ForumVB/</a><br>
..................................................................................................</div>
<blockquote style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
<div class="Ih2E3d">
<div style="FONT: 10pt arial">----- Original Message ----- </div>
<div style="BACKGROUND: #e4e4e4; FONT: 10pt arial"><b>From:</b> <a title="allan@positiveenergysolar.com" href="mailto:allan@positiveenergysolar.com" target="_blank">Allan Sindelar</a> </div></div>
<div class="Ih2E3d">
<div style="FONT: 10pt arial"><b>To:</b> <a title="re-wrenches@lists.re-wrenches.org" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">&#39;RE-wrenches&#39;</a> </div>
<div style="FONT: 10pt arial"><b>Sent:</b> Wednesday, December 10, 2008 1:16 PM</div>
<div style="FONT: 10pt arial"><b>Subject:</b> [RE-wrenches] Module Voltage Question for Off-Grid Designers</div>
<div><br></div></div>
<div>
<div></div>
<div class="Wj3C7c">
<p><font face="Times New Roman">Wrenches,</font> <br><font face="Times New Roman">Here&#39;s an issue I haven&#39;t seen directly addressed, and I would like to know what the rest of you are doing.</font> <br><font face="Times New Roman">It&#39;s getting harder to get 24V nominal modules. Because the bulk of industry growth is high-voltage grid-tied applications, modules no longer have to be a standard voltage. Just pick the number of modules to best fit the chosen inverter&#39;s string voltage range.</font></p>

<p><font face="Times New Roman">But for off-grid, the odd cell counts and resulting &quot;nontraditional&quot; DC input voltages challenge the traditional rules of off-grid design. I may be fighting a losing battle here, as the industry changes so rapidly and fundamentally. I have been trying to stay with 72-cell modules for offgrid, as this most readily combines with existing systems with 36-cell modules (12V) and 72-cell modules (24V). </font></p>

<p><font face="Times New Roman">For example, I will use the new Canadian Solar 170-200W modules. They are 60-cell modules, with a Vmppt of around 28 volts - too low to charge 24V batteries with a standard charge controller. We can use them in any new systems with an MX60 or similar voltage-converting MPPT controller. Two or three in series would charge a 24V battery; 3 in series would charge 48V. Four in series would violate Code, as low-temp voltage would easily exceed 150V. </font></p>

<p><font face="Times New Roman">Unless 60-cell modules remain a standard in the future, any future array additions would have to be on their own charge controller, in order to match a different I-V curve and MPP voltages into the same battery bank. Is this prohibitive? No, it just runs counter to the longstanding standards of off-grid design that allow modules to be added in the future: these modules will not add well to existing systems, and will not easily allow additional dissimilar modules to be added later. </font></p>

<p><font face="Times New Roman">I had this same objection to using Day4 modules, although they were better at 16Vnom. Three made up a standard 48V array, so strings could be combined with two-module strings of similar 24Vnom modules.</font></p>

<p><font face="Times New Roman">Who else is trying to stay with 24V modules? Anyone still using 12V modules in off-grid (residential-scale, not little apps) designs? Who has a crystal ball and knows what modules will be like in 20 years, or even two years? Wat are the rest of you doing?</font></p>

<p><font face="Times New Roman">Thanks, as usual.</font> <br><font face="Times New Roman">Allan</font> <br><font face="g">Allan Sindelar</font> <br><a href="mailto:allan@positiveenergysolar.com" target="_blank"><u></u><u><font face="g" color="#0000ff" size="2">allan_(at)_positiveenergysolar.com</font></u></a> <br>
<font face="g" size="2">NABCEP certified solar PV installer</font> <br><font face="g" size="2">Positive Energy, Inc.</font> <br><font face="g" size="2">3225A Richards Lane</font> <br><font face="g" size="2">Santa Fe NM 87507</font> <br>
<font face="g" size="2">505 424-1112</font> </p></div></div>
<p>
<hr>

<div class="Ih2E3d">
<p></p>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
<br></div>
<p></p></p></blockquote></div><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>List rules &amp; etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check out participant bios:<br><a href="http://www.members.re-wrenches.org/" target="_blank">www.members.re-wrenches.org</a><br>
<br><br></blockquote></div><br>