My favorite is the Sharp 175 for off-grid and solar pumping
applications; a sturdy, well built and consistent module for most
applications. You can even get them fairly often!<br>
<br>
Matt T<br>
<br>
Kirpal Khalsa wrote:
<blockquote
 cite="mide925cf120812101333y4d5f9d41j1956dcaf1d948fdc@mail.gmail.com"
 type="cite">Allen..Greetings....yes indeed it is an issue. we have
been addressing with multiple charge controllers per system. we don't
fight the current (not electrical).&nbsp; In the future the way i see it-
the electronics will be more flexible and be able to handle the larger
variety of string voltages.&nbsp; For example the long long long awaited
apollo solar t100 which will allow voltages to exceed the 150V limit we
have had for a long time.&nbsp; They have apparently even lined up some
breakers which will work with these greater voltages.&nbsp; 3 modules in a
series will no longer be a maximum.&nbsp; I understand midnite solar also
has a charge controller which will allow the 150V max to go by the way
side.&nbsp; We are trying to be flexible as modules become less standard and
hope that the electronics will allow us to address thesee challanges as
time goes by.<br>
  <br>
One thing that we would love to see is more large wattage modules with
j boxes rather than pre-wired MC cables.&nbsp; In many of our off grid
systems the array is located in readily accesible locations and
crafting a fence or sticking the array over 8 feet of the ground is a
big hassle/extra expense.&nbsp; This has proven to be a bigger concern for
us rahter than the voltage variety.&nbsp; If you know of any 72 cell or for
that matter 60 cell modules&nbsp; which allow flex conduit between j boxes
we would love some info.......<br>
  <br>
  <br>
-- <br>
Sunny Regards,<br>
Kirpal Khalsa<br>
NABCEP Certified Solar PV Installer<br>
Renewable Energy Systems LLC<br>
  <br>
  <br>
  <div class="gmail_quote">On Wed, Dec 10, 2008 at 12:16 PM, Allan
Sindelar <span dir="ltr">&lt;<a
 href="mailto:allan@positiveenergysolar.com">allan@positiveenergysolar.com</a>&gt;</span>
wrote:<br>
  <blockquote class="gmail_quote"
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
    <div>
    <p><font face="Times New Roman">Wrenches,</font>
    <br>
    <font face="Times New Roman">Here's an issue I haven't seen
directly addressed, and I would like to know what the rest of you are
doing.</font>
    <br>
    <font face="Times New Roman">It's getting harder to get 24V nominal
modules. Because the bulk of industry growth is high-voltage grid-tied
applications, modules no longer have to be a standard voltage. Just
pick the number of modules to best fit the chosen inverter's string
voltage range.</font></p>
    <p><font face="Times New Roman">But for off-grid, the odd cell
counts and resulting "nontraditional" DC input voltages challenge the
traditional rules of off-grid design. I may be fighting a losing battle
here, as the industry changes so rapidly and fundamentally. I have been
trying to stay with 72-cell modules for offgrid, as this most readily
combines with existing systems with 36-cell modules (12V) and 72-cell
modules (24V). </font></p>
    <p><font face="Times New Roman">For example, I will use the new
Canadian Solar 170-200W modules. They are 60-cell modules, with a Vmppt
of around 28 volts - too low to charge 24V batteries with a standard
charge controller. We can use them in any new systems with an MX60 or
similar voltage-converting MPPT controller. Two or three in series
would charge a 24V battery; 3 in series would charge 48V. Four in
series would violate Code, as low-temp voltage would easily exceed
150V. </font></p>
    <p><font face="Times New Roman">Unless 60-cell modules remain a
standard in the future, any future array additions would have to be on
their own charge controller, in order to match a different I-V curve
and MPP voltages into the same battery bank. Is this prohibitive? No,
it just runs counter to the longstanding standards of off-grid design
that allow modules to be added in the future: these modules will not
add well to existing systems, and will not easily allow additional
dissimilar modules to be added later. </font></p>
    <p><font face="Times New Roman">I had this same objection to using
Day4 modules, although they were better at 16Vnom. Three made up a
standard 48V array, so strings could be combined with two-module
strings of similar 24Vnom modules.</font></p>
    <p><font face="Times New Roman">Who else is trying to stay with 24V
modules? Anyone still using 12V modules in off-grid (residential-scale,
not little apps) designs? Who has a crystal ball and knows what modules
will be like in 20 years, or even two years? Wat are the rest of you
doing?</font></p>
    <p><font face="Times New Roman">Thanks, as usual.</font>
    <br>
    <font face="Times New Roman">Allan</font>
    <br>
    <font color="#888888"><font face="g">Allan Sindelar</font>
    <br>
    <a href="mailto:allan@positiveenergysolar.com" target="_blank"><u><font
 color="#0000ff" face="g" size="2">allan_(at)_positiveenergysolar.com</font></u></a>
    <br>
    <font face="g" size="2">NABCEP certified solar PV installer</font>
    <br>
    <font face="g" size="2">Positive Energy, Inc.</font>
    <br>
    <font face="g" size="2">3225A Richards Lane</font>
    <br>
    <font face="g" size="2">Santa Fe NM 87507</font>
    <br>
    <font face="g" size="2">505 424-1112</font>
    </font></p>
    </div>
  </blockquote>
  </div>
  <br>
  <br clear="all">
  <br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

  </pre>
  <pre wrap="">
<hr size="4" width="90%">

Internal Virus Database is out of date.
Checked by AVG - <a class="moz-txt-link-freetext" href="http://www.avg.com">http://www.avg.com</a> 
Version: 8.0.176 / Virus Database: 270.9.15/1833 - Release Date: 12/5/2008 7:08 PM

  </pre>
</blockquote>
</body>
</html>