<TITLE>Re: [RE-wrenches] load side taps and NEC 240.21</TITLE>
</HEAD>
<BODY>
<FONT SIZE="4"><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>The 2008 NEC broaden this 120% allowance to include commercial facilities. There are some additional requirements to be aware of in order to use the 120% allowance.<BR>
<BR>
<BR>
On 12/5/08 7:10 PM, &quot;Mark Frye&quot; &lt;markf@berkeleysolar.com&gt; wrote:<BR>
<BR>
</SPAN></FONT></FONT><BLOCKQUOTE><FONT SIZE="4"><SPAN STYLE='font-size:11pt'><FONT COLOR="#0000FF"><FONT FACE="Arial">120% allowance is only &quot;..For a dwelling unit....&quot;.<BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT COLOR="#0000FF"><FONT FACE="Arial">Clearly this is a load side Point of Connection. If it is a &quot;dwelling unit&quot;&quot; then the 120% allowance is applicable. If it is not a &quot;dwelling unit&quot;, then there is no room to connect under NEC 2008.<BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT FACE="Arial">Mark Frye</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT FACE="Arial">Berkeley Solar Electric Systems</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT FACE="Arial">303 Redbud Way</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT FACE="Arial">Nevada City, &nbsp;CA 95959</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT FACE="Arial">(530) 401-8024</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT COLOR="#0000FF"><FONT FACE="Arial"><U>www.berkeleysolar.com</U></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <a href="http://www.berkeleysolar.com/">&lt;http://www.berkeleysolar.com/&gt;</a> </FONT><FONT FACE="Arial"> </FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
<BR>
&nbsp;<BR>
<BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="100%"></FONT><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org [<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org]">mailto:re-wrenches-bounces@lists.re-wrenches.org]</a> <B>On Behalf Of </B>August Goers<BR>
<B>Sent:</B> Friday, December 05, 2008 5:01 PM<BR>
<B>To:</B> RE-wrenches<BR>
<B>Subject:</B> Re: [RE-wrenches] load side taps and NEC 240.21<BR>
</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><BR>
</FONT></SPAN><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Jerry - <BR>
<BR>
A line tap typically occurs between the utility meter and the main breaker - not after the main breaker on the load side. It seems that you are describing a load side tap which follows the 120% rule under 2008 NEC; I might be misunderstanding the situation. Please clarify. There are few folks out there who are able handle these large commercial grade interconnections and I think it is well worth discussing.<BR>
<BR>
Good luck! -August <BR>
<BR>
<BR>
August Goers<BR>
<BR>
Luminalt Energy Corporation<BR>
4000 Irving Street <BR>
San Francisco, CA 94122<BR>
<BR>
<BR>
Office: 415.564.7652<BR>
Mobile: 415.559.1525<BR>
august@luminalt.com<BR>
www.luminalt.com<BR>
<BR>
<BR>
</SPAN></FONT><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><HR ALIGN=CENTER SIZE="1" WIDTH="100%"><B>From:</B></SPAN><SPAN STYLE='font-size:10pt'> William Miller &lt;wrmiller@charter.net&gt;<BR>
<B>To:</B> RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<BR>
<B>Sent:</B> Friday, December 5, 2008 4:11:15 PM<BR>
<B>Subject:</B> Re: [RE-wrenches] load side taps and NEC 240.21<BR>
</SPAN></FONT><SPAN STYLE='font-size:10pt'><FONT FACE="Arial"><BR>
Jerry:<BR>
<BR>
At a recent John Wiles seminar, John declared that this scenario is not a <BR>
tap and is therefore not covered under the tap rule. This was news to me, <BR>
but Wiles is considered some sort of guru in compliance discussions.<BR>
<BR>
William Miller<BR>
<BR>
<BR>
At 03:43 PM 12/5/2008, you wrote:<BR>
<BR>
&gt;Wreches,<BR>
&gt;<BR>
&gt;<BR>
&gt;I have a system where we are tapping onto the bus bars of a 1200 amp panel <BR>
&gt;fed by a 1200 amp main breaker. The easy place to tap onto the bus bars <BR>
&gt;is the load side of the breaker using the existing bolts.<BR>
&gt;<BR>
&gt;<BR>
&gt;The inverter and utility fused disco are about 200 ft away, and the tap <BR>
&gt;conductors travel about15ft in EMT conduit before leaving the <BR>
&gt;building. After that the circuit is outdoors. NEC 240.21(B)5 allows taps <BR>
&gt;of unlimited length for conductors located outside of a building, except <BR>
&gt;at the point of load (in this case supply) termination.<BR>
&gt;<BR>
&gt;<BR>
&gt;Can 20ft of conductor inside the building be covered by being &quot;at the <BR>
&gt;point of load termination&quot;, or do I have to comply with NEC 240.21(B)2 and <BR>
&gt;have an OCPD within 25'?<BR>
&gt;<BR>
&gt;<BR>
&gt;The construction foreman for this project is buddies with the inspector, <BR>
&gt;so getting a signed permit won't be a problem but I want this to be a code <BR>
&gt;compliant system. Can anyone lend some insight to the spirit of <BR>
&gt;240.21(B)2 and 5?<BR>
&gt;<BR>
&gt;<BR>
&gt;Sorry if this has been discussed before, but searching didn't yield any <BR>
&gt;results.<BR>
&gt;<BR>
&gt;<BR>
&gt;Best,<BR>
&gt;<BR>
&gt;Jerry Caldwell<BR>
&gt;<BR>
&gt;Recurrent Energy<BR>
&gt;<BR>
&gt;_______________________________________________<BR>
&gt;List sponsored by Home Power magazine<BR>
&gt;<BR>
&gt;List Address: RE-wrenches@lists.re-wrenches.org<BR>
&gt;<BR>
&gt;Options &amp; settings:<BR>
&gt;<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR>
&gt;<BR>
&gt;List-Archive: <BR>
&gt;<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR>
&gt;<BR>
&gt;List rules &amp; etiquette:<BR>
&gt;www.re-wrenches.org/etiquette.htm <a href="http://www.re-wrenches.org/etiquette.htm">&lt;http://www.re-wrenches.org/etiquette.htm&gt;</a> <BR>
&gt;<BR>
&gt;Check out participant bios:<BR>
&gt;www.members.re-wrenches.org <a href="http://www.members.re-wrenches.org">&lt;http://www.members.re-wrenches.org&gt;</a> <BR>
<BR>
<BR>
_______________________________________________<BR>
List sponsored by Home Power magazine<BR>
<BR>
List Address: RE-wrenches@lists.re-wrenches.org<BR>
<BR>
Options &amp; settings:<BR>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR>
<BR>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR>
<BR>
List rules &amp; etiquette:<BR>
www.re-wrenches.org/etiquette.htm<BR>
<BR>
Check out participant bios:<BR>
www.members.re-wrenches.org<BR>
<BR>
<BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="95%"></FONT><FONT FACE="Consolas, Courier New, Courier">_______________________________________________<BR>
List sponsored by Home Power magazine<BR>
<BR>
List Address: RE-wrenches@lists.re-wrenches.org<BR>
<BR>
Options &amp; settings:<BR>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR>
<BR>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR>
<BR>
List rules &amp; etiquette:<BR>
www.re-wrenches.org/etiquette.htm<BR>
<BR>
Check out participant bios:<BR>
www.members.re-wrenches.org<BR>
<BR>
</FONT></SPAN></FONT></BLOCKQUOTE><FONT SIZE="4"><SPAN STYLE='font-size:10pt'><FONT FACE="Consolas, Courier New, Courier"><BR>
</FONT></SPAN><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>David Brearley, Technical Editor<BR>
<I>SolarPro</I> magazine <BR>
NABCEP Certified PV Installer &#8482;<BR>
david.brearley@solarprofessional.com<BR>
Direct: 541.261.6545<BR>
Fax: &nbsp;541.512.0343<BR>
<B><BR>
</B>Visit our Web site at solarprofessional.com<BR>
</SPAN></FONT></FONT>