<html><head><style type='text/css'>p { margin: 0; }</style></head><body><div style='font-family: Times New Roman; font-size: 12pt; color: #000000'><P>Thanks Tump... I'll play with the setpoints.</P>
<P>&nbsp;</P>
<P>On the x-fer switch, I was assuming that the built in X-fer would be used to switch the inverter critical loads to the AC1 (main panel).&nbsp; My suggestion was to add a second upstream to power these loads from the genny should there be an inverter failure AND a power outage.&nbsp; Just an option.<BR><BR></P>
<DIV>For a brighter energy future,<BR><BR>Geoff Greenfield<BR>Founder and CEO<BR><FONT size=4><STRONG>Third Sun Solar &amp; Wind Power Ltd.<BR></STRONG></FONT>340 West State Street, Unit 25<BR>Athens, OH 45701<BR><BR>740.597.3111 &nbsp; &nbsp; Fax 740.597.1548<BR>www.Third-Sun.com<BR><BR><EM><FONT size=4>Clean Energy - Expertly Installed<BR></FONT></EM><BR><BR><BR><BR></DIV><BR><BR>----- "Tump" &lt;tump@hughes.net&gt; wrote: <BR>&gt; 
<STYLE>p { margin: 0; }</STYLE>

<DIV><SPAN class=968373415-25112008><FONT face=Arial color=#0000ff size=2>The XW would have the inverter by-pass breakers assembly if you installed it w/ the conduit box, so the second&nbsp;transfer switch is not necessary. </FONT></SPAN></DIV>
<DIV><SPAN class=968373415-25112008></SPAN><SPAN class=968373415-25112008><FONT face=Arial color=#0000ff size=2>Reset your gen AC&nbsp;"transfer" cycles to their minimum as well as your generator low voltage parameters to 110 volts (IF it is a quality gen set &amp; it produces a constant 120V), you should see no more lag transferring off the gen.Make sure you reset the settings in ALL the VFXs.</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>&gt; <FONT face=Tahoma size=2>-----Original Message-----<BR>&gt; <B>From:</B> re-wrenches-bounces@lists.re-wrenches.org [mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Geoff Greenfield<BR>&gt; <B>Sent:</B> Tuesday, November 25, 2008 9:39 AM<BR>&gt; <B>To:</B> RE-wrenches<BR>&gt; <B>Subject:</B> Re: [RE-wrenches] Integrating with a whole house generator<BR>&gt; </FONT></DIV>
<DIV style="FONT-SIZE: 12pt; COLOR: #000000; FONT-FAMILY: Times New Roman">&gt; 
<P>It all depends on the homeowners expectations (and what THEY think is a reasonable critical load).&nbsp; Your scheme looks like it would work - (I might include a second X-fer switch to run the inverter supported loads off the genny if the grid AND the inverter are out).</P>
<P>&nbsp;</P>
<P>Second issue is transfer speed and power drop out.&nbsp; I am not sure of the XW, but I have found that outback is a very quick and clean switch (no computer/com drops) from grid to backup... like a UPS.&nbsp; However... it is NOT as smooth when turning off the genny on back up mode.&nbsp; Lights all fade as genny coughs off and inverter kicks back over to batts.&nbsp; I always make sure customer computer has a deadicated UPS.<BR>&gt; </P>
<DIV>For a brighter energy future,<BR>&gt; Geoff Greenfield<BR>&gt; Founder and CEO<BR>&gt; <FONT size=4><STRONG>Third Sun Solar &amp; Wind Power Ltd.<BR>&gt; </STRONG></FONT>340 West State Street, Unit 25<BR>&gt; Athens, OH 45701<BR>&gt; 740.597.3111 &nbsp; &nbsp; Fax 740.597.1548<BR>&gt; www.Third-Sun.com<BR>&gt; <EM><FONT size=4>Clean Energy - Expertly Installed<BR>&gt; </FONT></EM><BR>&gt; </DIV><BR>&gt; ----- "William Miller" &lt;wrmiller@charter.net&gt; wrote: <BR>&gt; &gt; Friends:<BR>&gt; &gt; I am bidding an installation in which the customer owns a whole house <BR>&gt; &gt; generator. &nbsp;The generator is 30 KVA and we will be installing a 4.5 or 6.0 <BR>&gt; &gt; KVA XW system. &nbsp;Obviously, the inverter will not power the entire <BR>&gt; &gt; house. &nbsp;If we segregate the non-critical loads and connect them to a <BR>&gt; &gt; grid-fed panel, the generator will not power them. &nbsp;If we let the generator <BR>&gt; &gt; run every time there is an outage, this negates the need for a inverter <BR>&gt; &gt; system. What to do?<BR>&gt; &gt; The transfer switch sends a two wire start signal to the generator upon a <BR>&gt; &gt; grid outage. &nbsp;After the transfer switch senses generator voltage, it <BR>&gt; &gt; effects a transfer.<BR>&gt; &gt; My brainstorm is to intercept that two wire start signal. &nbsp;I will connect <BR>&gt; &gt; it instead to the XW inverter. &nbsp;We will segregate the loads, feeding the <BR>&gt; &gt; critical loads from the XW and the Non-critical loads from the output of <BR>&gt; &gt; the transfer switch. &nbsp;In the case of a grid outage, the critical loads will <BR>&gt; &gt; receive uninterrupted power. &nbsp;The Non-critical loads will not have power <BR>&gt; &gt; unless the generator is started by the XW. &nbsp;Once the XW (or the home owner) <BR>&gt; &gt; starts the generator, the transfer will occur. &nbsp;We will put a control panel <BR>&gt; &gt; in the house so the home-owner can start the generator if the No-critical <BR>&gt; &gt; loads are needed.<BR>&gt; &gt; This seems clever to me, but I am biased. &nbsp;Am I missing something???<BR>&gt; &gt; William Miller<BR>&gt; &gt; _______________________________________________<BR>&gt; &gt; List sponsored by Home Power magazine<BR>&gt; &gt; List Address: RE-wrenches@lists.re-wrenches.org<BR>&gt; &gt; Options &amp; settings:<BR>&gt; &gt; http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR>&gt; &gt; List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR>&gt; &gt; List rules &amp; etiquette:<BR>&gt; &gt; www.re-wrenches.org/etiquette.htm<BR>&gt; &gt; Check out participant bios:<BR>&gt; &gt; www.members.re-wrenches.org</DIV></BLOCKQUOTE><BR>&gt; _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options &amp; settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules &amp; etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org </div></body></html>