color=#000080 size=2>In 2008, we have had to replace our standard Sq. D HU361RB 
used since our beginnings, with the Sq. D H361RB (U stands for 
unfused).&nbsp;&nbsp; Was there some sort of code change NEC or CBC maybe that 
made most jurisdictions in So Cal suddenly start requiring fused DC 
disconnects?&nbsp; Typically, we fill the fused Sq. D. box with 15A 5" 
fuses.</FONT></SPAN></DIV>
<DIV><FONT face=Tahoma color=#000080 size=2></FONT>&nbsp;</DIV>
<DIV align=left>
<DIV align=left><SPAN 
style="FONT-SIZE: 10pt; COLOR: rgb(51,51,153); FONT-FAMILY: Tahoma">
<DIV align=left>
<DIV><SPAN 
style="FONT-SIZE: 10pt; COLOR: rgb(51,51,153); FONT-FAMILY: Tahoma"><SPAN 
class=218293818-21112008><FONT color=#000080>Peter 
D.</FONT></SPAN></SPAN></SPAN></DIV></DIV></DIV></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>William 
Miller<BR><B>Sent:</B> Friday, November 21, 2008 9:43 AM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] DC Rating of 
Disconnects<BR></FONT><BR></DIV>
<DIV></DIV>Peter:<BR><BR>I am resending, the first version inexplicably deleted 
some text:<BR><BR>An arc is created in the process of disconnecting any current 
under load.&nbsp; DC circuits have an enhanced ability to sustain that 
arc.&nbsp; PV circuits exacerbate this problem as a short or load is 
disconnected because they can sustain a short but the voltage rises drastically 
as a circuit is disconnected.<BR><BR>This all justifies the added expense of a 
DC rated disconnect.&nbsp; We use the Square D HU361 without hesitation.&nbsp; 
There are few alternatives available and none with any significant cost 
savings.&nbsp; In selecting a disconnect, a design-build contractor must use the 
highest Voc possible. Make sure you are entering the 690.7 table with the record 
low temperature for the location.<BR><BR>If we used a disconnect without the 
correct rating we would open ourselves to unacceptable liability exposure and, 
worse yet, would not experience that pleasant feeling one gets when you know 
you've done the job right.<BR><BR>William Miller<BR><BR><BR>At 09:11 AM 
11/21/2008, you wrote:<BR>
<BLOCKQUOTE class=cite cite="" type="cite"><FONT face=arial color=#0000ff 
  size=2>
  <HR>
  </FONT><FONT face=tahoma size=2><B>From:</B> Peter Parrish [<A 
  href="mailto:peter.parrish@calsolareng.com" 
  eudora="autourl">mailto:peter.parrish@calsolareng.com</A>] <BR><B>Sent:</B> 
  Friday, November 21, 2008 9:10 AM<BR><B>To:</B> 'RE-wrenches'<BR><B>Cc:</B> 
  'Peter Parrish'<BR><B>Subject:</B> DC Rating of Disconnects<BR></FONT><FONT 
  face=arial>&nbsp;<BR>I am looking into using the PV Powered PVP2000 inverter 
  for some small, low voltage designs. The string Voc will be around 200 Vdc, 
  worst case.<BR>&nbsp;<BR>Since the PVP2000 doesnt come with a DC disconnect, 
  I am wondered what other wrenches who install the PVP2000 have been doing 
  about this. I hate to spend $150 on a 600 V AC/DC disco such as the SD HU361RB 
  to provide the means of disconnection. I believe that the 240 V AC discos such 
  as the SD DU221RB have no DC rating.<BR>&nbsp;<BR>From an academic point of 
  view, I wonder why the smaller discos are not dual rated, since we all know 
  that the real-time voltage difference in a 240 V AC system can be 41% greater 
  than 240 V.<BR>&nbsp;<BR>In any event, any Code-compliant solutions would be 
  greatly appreciated.<BR>&nbsp;<BR>- Peter<BR></FONT><BR><FONT face=arial 
  color=#000080 size=2>Peter T. Parrish, 