Hey Kelly,<br><br>I think that&#39;s probably the best solution. I don&#39;t think it should be necessary with Sunny Boys in gridtied system, but it&#39;s certainly the safest bet. I&#39;m not sure if all SB&#39;s come with the right firmware, or if it&#39;s a special option, but they can be programmed to allow for a wide grid frequency window. This is used in the AC coupled arrangement with the Sunny Island. When the Sunny Island&#39;s batteries are full it starts to raise the grid frequency slightly. The SB&#39;s read this as an instruction to reduce their output and pull their arrays off MPP. At a defined frequency, the SB&#39;s shut down entirely.<br>
<br>So, the stories of SB&#39;s frying generators in off grid, AC coupled systems makes me think that the tight frequency window required for grid-tied systems had been replaced by the wider window used for communication with the Sunny Island. It was one of the first prototypes of these systems so it might be a little different now, but I installed a system that allowed the SI supported grid to range from 50Hz all the way up to 54Hz before the SB&#39;s shut down. That could allow quite a bit of backfeeding of the generator and might explain the generators being fried in these SI/SB AC coupled systems. I would think that with regular gridtied SB&#39;s they&#39;d shut down before damaging the generator.<br>
<br>Bottom line, though, I&#39;d probably install the NC relay powered off the generator input to be safe.<br><br>Dana<br clear="all"><br>-- <br>Dana Brandt<br>Ecotech Energy Systems, LLC<br><a href="http://www.ecotechenergy.com">www.ecotechenergy.com</a><br>
<a href="mailto:dana@ecotechenergy.com">dana@ecotechenergy.com</a><br>360.510.0433<br><br><br><div class="gmail_quote">On Thu, Nov 20, 2008 at 9:57 AM, Kelly Keilwitz, Whidbey Sun &amp;  Wind <span dir="ltr">&lt;<a href="mailto:kelly@whidbeysunwind.com">kelly@whidbeysunwind.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">All,<br>
I suppose a normally-closed relay on the inverter output, with coil<br>
energized from the generator (i.e. It opens when the genny is on) might be<br>
easier than a NO relay on the grid-side. Anyone do it this way?<br>
<font color="#888888"><br>
-Kelly<br>
</font><div class="Ih2E3d"><br>
<br>
On 11/20/08 9:30 AM, &quot;Kelly Keilwitz&quot; &lt;<a href="mailto:kelly@whidbeysunwind.com">kelly@whidbeysunwind.com</a>&gt; wrote:<br>
<br>
&gt;<br>
&gt; The relay seems like a reasonable solution. However, if the main panel is<br>
&gt; entirely backed up by the genny, to power the relay from the grid (only)<br>
&gt; requires a line-side tap, yes? Is there a simple solution that Im missing?<br>
&gt;<br>
<br>
<br>
<br>
<br>
<br>
</div><div><div></div><div class="Wj3C7c">_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</div></div></blockquote></div><br><br>