<DIV><SPAN class=359494905-10092008>Jeff,</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>Re remote starting, we have had experience 
with these generators as being two-wire and easy to control:</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>&nbsp;&nbsp;&nbsp; -all Kohler LP from the 
old 6.5RMY through 20RY</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>&nbsp;&nbsp;&nbsp; -Onan RS20000 - I 
understand the new units are 2-wire like Kohler. This one was.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>&nbsp;&nbsp;&nbsp; -Coleman 10kW with Honda 
engine.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>All required two wires only and no 
additional hardware.</SPAN></DIV>
<DIV><SPAN class=359494905-10092008>Allan</SPAN></DIV>
<DIV><SPAN class=359494905-10092008></SPAN>&nbsp;</DIV>
<DIV></DIV>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left><FONT face=Tahoma 
size=2>-----Original Message-----<BR><B>From:</B> 
re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Jeff 
Yago<BR><B>Sent:</B> Wednesday, September 03, 2008 9:43 AM<BR><B>To:</B> 
RE-wrenches<BR><B>Subject:</B> Re: [RE-wrenches] Remote generator 
start<BR><BR></FONT></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: Arial, sans-serif">
<DIV>I know this subject has come up from time to time in small pieces, but 
would like a collective set of answers.&nbsp; As you know, some generators are 
very easy to remote start from an inverter using only a simple relay and 2-wire 
connection.&nbsp; Make the contact and the generator starts and runs, break the 
contact and it stops.&nbsp; The Kohler line of generators have this start and 
stop control and was easy to connect to the spare relay in the old Trace 
SW40&nbsp;inverter and the newer Outback inverters.</DIV>
<DIV>&nbsp;</DIV>
<DIV>What&nbsp;generators in the 8 to 15 kW range have you found easy to remote 
start from an inverter, and which models or brands were a nightmare?&nbsp; 
</DIV>
<DIV>&nbsp;</DIV>
<DIV>What other&nbsp;hardware or controls were required to get it to 
work?&nbsp;&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>How many control wires were required out to the generator?</DIV>
<DIV>&nbsp;</DIV></DIV></BODY></HTML>