<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD><TITLE>Surrette Battery Question</TITLE>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.6000.16674" name=GENERATOR></HEAD>
<BODY>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2>Allan,</FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff size=2>These 
are (2) cell 4 volt batteries (4,416wh each battery (4v x 1104)), 
correct?&nbsp;How many does your client have?&nbsp;I'll guess (6) of them, if 
that's the case they have &nbsp;26.5kWh of rated storage. </FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff size=2>The pv 
array total is approx 2kW (about 60A rated current at max power).&nbsp; So 
depending on how the math is done the charge rate is C/13 (26.5kWh/2kW), or C/18 
(1104ah/60). I'm&nbsp;thinking that this is a good charge rate for New Mexico. 
If the array and MX60&nbsp;are&nbsp;working properly, and the client's are not 
using more watt hours than the system is designed for, the batteries should be 
getting adequate charging. As you know these Surrette's need to charge to 
relatively higher voltages than other makes of lead acids. 29.6VDC sounds good 
to me. Surrette may want that bulk raised a bit with older age cells if 
performance is dipping?</FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff size=2>A 
couple of additional thoughts. 1) TriMetric voltage readings can vary from MX60 
voltage readings which may account for that 31.1 to 31.4v difference. 2) Remind 
your client's that&nbsp;equalization questions are best answered by the use of a 
hydrometer (or refractometer) to test the SG of every cell. If they are 
relatively equal (within .015 basis points lowest cell to highest cell ) than 
your batteries are equalized and it really does not matter that the voltage did 
not go up to some arbitrary number. It is more important that lead acid cells 
are regularly fully charged at a high enough voltage to significantly gas each 
cell for a long enough period of time. This is where absorption time is so 
important. Equalize charges (controlled over voltage charge)&nbsp;on a regular 
basis (every month or two) need to be done more on systems that do not regularly 
reach their fully charged state as often as they should. I coach my client's 
(and program their TriMetric's) to see to it that their battery banks receive a 
full charge at least every 10 days. </FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2>Best,</FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff size=2>Dave 
Palumbo</FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff 
size=2>Independent Power LLC</FONT></SPAN></DIV>
<DIV><SPAN class=078164613-02082008><FONT face=Arial color=#0000ff size=2>Hyde 
Park, VT</FONT></SPAN></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> 
  re-wrenches-bounces@lists.re-wrenches.org 
  [mailto:re-wrenches-bounces@lists.re-wrenches.org]<B>On Behalf Of </B>Allan 
  Sindelar<BR><B>Sent:</B> Friday, August 01, 2008 10:19 PM<BR><B>To:</B> RE 
  Wrenches<BR><B>Subject:</B> [RE-wrenches] Surrette Battery 
  Question<BR><BR></FONT></DIV><!-- Converted from text/rtf format -->
  <P><FONT face=Arial>Wrenches,</FONT> <BR><FONT face=Arial>In late 2003 we 
  installed a 24V set of Rolls-Surrette 4-KS-21PS 6V 1104 A/hr batteries in the 
  off-grid system of a long-time client. The client's system had a democracy 
  array of around 800 watts of tracked PV. In early 2005 we added 1,280 watts of 
  additional PV, and the client hasn't run the generator since; the system 
  rarely drops below 80% and fills to 100% most days in sunny New Mexico. 
  Batteries are located in a basement, so temperatures stay relatively constant, 
  although it will vary slightly seasonally. MX60 controller is temperature 
  compensated, with 29.6 VDC bulk and 31.4 VDC EQ set points.</FONT></P>
  <P><FONT face=Arial>The problem is that the client reports being unable to 
  achieve previous EQ voltages, and this inability appears to be a new 
  development. The system is otherwise performing well. As the client is sharp 
  and pays close attention to the system's operation, I'm not ready to blame 
  user ignorance (with one possible exception; read on). This may be an issue of 
  seasonally warm temperatures, but I'm not sure this would explain the full 0.4 
  VDC reduction in voltage. I told him that I would post his problem to this 
  list, and also request advice from Surrette Battery.</FONT></P>
  <P><FONT face=Arial>Here is the client's description of the symptoms:</FONT> 
  <BR><FONT face=Arial>I'm concerned that I am unable to equalize batteries at 
  this time.&nbsp; Up</FONT> <BR><FONT face=Arial>until June of this year the 
  Tri-Metric readings during equalizing indicated</FONT> <BR><FONT 
  face=Arial>holding voltage at 31.1, with maximum amps gain of around 
  52.&nbsp;&nbsp; Three weeks</FONT> <BR><FONT face=Arial>ago, when set on 
  equalize, the maximum voltage reading was 30.7, with</FONT> <BR><FONT 
  face=Arial>maximum amps of 46; this was reached around noon, and by around 
  1:30 pm</FONT> <BR><FONT face=Arial>voltage/amps began its typical afternoon 
  drop-off.&nbsp; I attempted equalizing</FONT> <BR><FONT face=Arial>on two 
  other occasions since then--the last time this past Saturday, with</FONT> 
  <BR><FONT face=Arial>clear skies up until mid-afternoon--but having the same 
  results.&nbsp; So, the</FONT> <BR><FONT face=Arial>question is: are my 
  batteries beginning their decline? We've had this set</FONT> <BR><FONT 
  face=Arial>for 4 1/2 years, so it would seem a bit too early for this, given 
  that these</FONT> <BR><FONT face=Arial>batteries are expected to last 7-10 
  years.</FONT> </P>
  <P><FONT face=Arial>Second issue, possibly related:</FONT> </P>
  <P><FONT face=Arial>On another matter, I have been using deionized water for 
  the batteries for</FONT> <BR><FONT face=Arial>as long as we've been using 
  photovoltaics (since 1991), as it is my</FONT> <BR><FONT 
  face=Arial>understanding that deioinized water is virtually the same as 
  distilled</FONT> <BR><FONT face=Arial>water--I just checked Wikipedia on this 
  (using "deionized and distilled</FONT> <BR><FONT face=Arial>water" as the 
  search phrase), and this appears to be the case.</FONT> </P>
  <P><FONT face=Arial>I don't know the answer to this question, as we have 
  always recommended distilled water only in batteries, and have never faced 
  this question.</FONT></P>
  <P><FONT face=Arial>Any help would be appreciated.</FONT> </P>
  <P><FONT face=g>Allan Sindelar</FONT> <BR><A 
  href="mailto:allan@positiveenergysolar.com"><U></U><U><FONT face=g 
  color=#0000ff size=2>allan_(at)_positiveenergysolar.com</FONT></U></A> 
  <BR><FONT face=g size=2>NABCEP certified solar PV installer</FONT> <BR><FONT 
  face=g size=2>Positive Energy, Inc.</FONT> <BR><FONT face=g size=2>3225A 
  Richards Lane</FONT> <BR><FONT face=g size=2>Santa Fe NM 87507</FONT> 
  <BR><FONT face=g size=2>505 424-1112</FONT> </P><BR>
  <P><FONT face=g>Allan Sindelar</FONT> <BR><A 
  href="mailto:allan@positiveenergysolar.com"><U></U><U><FONT face=g 
  color=#0000ff size=2>allan_(at)_positiveenergysolar.com</FONT></U></A> 
  <BR><FONT face=g size=2>NABCEP certified solar PV installer</FONT> <BR><FONT 
  face=g size=2>Positive Energy, Inc.</FONT> <BR><FONT face=g size=2>3225A 
  Richards Lane</FONT> <BR><FONT face=g size=2>Santa Fe NM 87507</FONT> 
  <BR><FONT face=g size=2>505 424-1112</FONT> </P></BLOCKQUOTE></BODY></HTML>