In a message dated 12/16/2000 5:57:22 PM Pacific Standard Time,
toddcory@jps.net writes:


I thought it could also be the gen freq., but if it was so out of whack so as
to cause the inverter to disconnect from the generator, why would it
reconnect
again with no load? If the theory of less load = worse frequency is carried
to
this condition as well, with NO load it would be even more out of acceptable
range, and the Trace should not even synch with it to begin with.



Upon initial connection the charger loads the genset and brings the freq
down. So no problem. Once the load is reduced,the freq goes out of spec.

Don
- - - - - - -