Drake and Don,
 
My understanding of 690-4(c) is that it allows you to daisy chain the conduit runs of modules within a single source circuit. A rack of 8 modules wired in a 24 volt series-parallel configuration could qualify as a single source circuit. In theory, this allows you to run one conduit whip for each panel assembly (rack). In practice, since most modules have 1/2 inch knock outs, you may be limited by the wire volume allowed in 1/2 inch conduit. The module j-box will also limit the number of wires you can run through it. In my installations I commonly run two series strings through one 1/2 inch conduit.
 
Each series string is still required to have its own supplementary overcurrent device (supposedly to protect the modules per UL). So if you want to run one whip for this rack you would still have to have a fuse/combiner box on the rack.
 
The "rated at 50 volts" language is ambiguous. The history of this article suggests the intent to limit it to 24 volt nominal systems. The inspectors I have dealt with have always allowed 24 volt nominal systems to be wired this way. Some have allowed 48 volt nominal systems to be wired this way. I have submitted a proposal to amend the 2002 NEC to clear up the language and allow 48 volt nominal systems to be wired this way.
----- Original Message -----
From: Drake Chamberlin - Electrical Energy
To: RE-wrenches@topica.com
Sent: Monday, April 10, 2000 10:02 AM
Subject: Module Wiring Made Easy? [RE-wrenches]

Hey Wrenches,
 
There has been a change in the wording of the 99 Code that might make array wiring easier.  The use of a combiner box might become a rare thing on domestic PV systems.  Let me know if you think this is correct.
 
In the old code it appeared that every series set of modules needed to have its output run directly to an overcurrent device in a combiner box.  Connections could not be made in another module's junction box, if removal of that module would disrupt the "grounded conductor" of another set.
 
This is how it has often been interpreted in Colorado anyway.  With this method, a rack of 8 modules wired for 24 volts requires four flexible conduit "whips" coming down to a combiner box with four fuses.  There are often positive and negative busbars to which the system conductors are connected.  Below is the old wording. 
 
*************************************************************************************************
690-4(c) 1996 NEC
 
 (c) Module Connection Arrangement. The connections to a module or panel shall be so arranged that removal of a module or panel from a photovoltaic source circuit does not interrupt a grounded conductor to another photovoltaic source circuit.
 
************************************************************************************************
The new code goes into detail about the meaning of "source circuit."  It now appears that a source circuit is any configuration of modules rated at 50 volts or less, terminating in a single over current device.  Here is the section.
 
**********************************************************************************************
 
690-4(c) 1999 NEC
 
(c) Module Connection Arrangement. The connections to a module or panel shall be arranged so that removal of a module or panel from a photovoltaic source circuit does not interrupt a grounded conductor to another photovoltaic source circuit. Sets of modules interconnected as systems rated at 50 volts or less, with or without blocking diodes, and having a single overcurrent device shall be considered as a single-source circuit. Supplementary overcurrent devices used for the exclusive protection of the photovoltaic modules are not considered as overcurrent devices for the purpose of this section.
 
*******************************************************************************************
 
The first sentence of the new code reads exactly like the old.  To simplify the changes, we can eliminate it.   The changed part has a lot of modifying wording.  Although necessary to consider, we can eliminate the modifiers for present purposes.  The reduced statement boils down to:
 
Sets of modules interconnected as systems rated at 50 volts or less having a single overcurrent device shall be considered as a single-source circuit. 
 
This would seem to imply that a rack of 8 modules wired in a 24 volt series-parallel configuration is a single source circuit.  It would therefore need only one whip going to a disconnect, rather than 4 whips connecting to a combiner box. 
 
The series sets apparently may be paralleled in the module junction boxes now.  If true, this will not only save hundreds of dollars in materials and labor on large systems, it will also make arrays look a lot cleaner. 
 
Here is an example of how an array might be designed with the new code. 
 
Eight Siemens SP 75s wired in series-parallel for 24 volts, have a short circuit rating of 19.2 amps (4.8 X 4) .  Multiply that times 1.25 twice (to comply with code) and you get 30 amps.  A pair of number 10 THWN-2 wires should satisfy any inspector.  (* Note:  The rating of THWN-2 comes on many THHN conductors).
 
So two #10 AWG wires can be used instead of eight.  One conduit is needed instead of four.  One overcurrent device is needed instead of four.  The wiring can be run directly to a fused disconnect, rather than to a combiner box first.  A 16 module, 24 volt array can have two whips run to a 2 pole fused disconnect. 
 
Due to the language, it looks hopeful that this rule will also apply to 48 volt systems.  The code now seems to say that photovoltaic source circuits are "Sets of modules interconnected as systems rated at 50 volts or less."  The word "rated" seems to imply nominal voltage rather than the actual measured, operating voltage. 
 
Wrenches, let us know if we are on track.
 
                                                                  Drake Chamberlin
 
                                                                  Don Wallingford