<div dir="ltr"><div>Hi Ray,</div><div><br></div><div>RE. the <i>NEC</i> Chapter 9 Table 8 resistance adjustment formula: I believe temperature T2 is the operating temperature of the conductor - not necessarily ambient temperature... unless I'm mistaken?</div><div><br></div><div>Corey Shalanski</div><div>Jah Light Solar</div><div>Portland, Jamaica</div><div><br></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Sat, Mar 21, 2026 at 7:20 PM Ray Walters <<a href="mailto:ray@solarray.com">ray@solarray.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;border-left-color:rgb(204,204,204);padding-left:1ex"><div class="msg-7238687081896949649"><span style="font-family:"Times New Roman",serif;font-size:12pt">I remember doing some measurements on a long wire run, and being
      surprised that the actual voltage drop was much less than the
      calculations.  That's when I found a small note at the bottom of
      the NEC Table 8 conductor properties used for official VD
      calculations.   The resistance is listed at 167 F (75C), so if you
      use the adjustment equation in Note 2, it is much less VD, and
      corresponds to reality.  For underground conductors, I might use
      25C.  Use common sense.  </span><br><div>
    <p>The formula is R2=R1 (1+ a(T2-75))</p>
    <p>I made a spread sheet about 15 years ago, that uses that formula
      for doing wire sizing.  Happy to share, if anyone is interested.</p>
    <p>Ray Walters<br>
      Remote Solar</p></div>
</div></blockquote></div></div>