<div dir="ltr"><div>Hi wrenches,<br>I've got a service call that needs a ~50kVA inverter, 3 phase (could be 208 or 480)<br>I'm replacing an older system, and the existing stringing is set up with:<br>3 strings, with each strings calculations ending up at:<br>~359Vmp (Hottest Conditions)<br>-510Voc (Cold)<br>40A Imp, 42.8A Isc<br><br>So, I'm hitting 2 issues:<br>(A) Vmp too low for many newer inverters<br>(B) Newer inverters want to land each string individually, and this system merged the strings in DC Cominers at the array, so I would prefer to give the 40A input to 1 terminal if possible to avoid a 300' repull. (I have 3 pairs of #4, and would have to repull 15 pairs of #10. It's possible, but not preferred)<br><br>If anyone has a brand of inverters I should investigate that may work, please let me know.<br>Thanks,</div><div>Travis</div><div><br></div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr">Travis Knipple<div>Senior Engineer</div><div>Hudson Solar Solutions LLC</div><div>Rhinebeck, NY 12572</div><div>518-539-8040 x408 | <a href="mailto:travis@hudsonsolarsolutions.com" target="_blank">travis@hudsonsolarsolutions.com</a></div><div><br></div><div><img src="https://ci3.googleusercontent.com/mail-sig/AIorK4wuT0Jf3z34mlt7_aUK-QOs2RIbM5kO1oBpUVNKSFuc5ADydVvuRPMkmhWoT1Bglre_AATVNHA1BkN_" width="96" height="75"></div><div>PVIP# PV-111821-013612<br><br></div><div><br></div></div></div></div>