    <p>We're not the only ones wondering about best settings for LFPs. 
      I've noticed over the years both Simpliphi and Fortress have
      changed their recommended charge settings substantially.  Fortress
      seems to have gone to a higher voltage and very low absorb time. 
      Considering they're roughly the same cells inside on all of these,
      I find the variations in settings interesting.  </p>
    <p>Beware, some batteries like the Simpliphi will literally let the
      smoke out if they go over 60 v.  I was excited about the 15 cell
      (48 v nominal) HomeGrid batteries, since they would be closer to
      lead acid voltages. However, we ended up having quite a bit of
      firmware troubles, and the "outdoor" enclosure and heating left a
      lot to be desired.  </p>
    <p> Like William, I don't consider myself quite an expert on LFP,
      but I've done systems with Blue Planet, LiFe Blue, Simpliphi,
      Fortress, Homegrid, and Midnite. Even though I had a hard time
      finding charge settings, the Midnite Powerflo 16 has been my
      favorite so far.  I just did a system with a Rosie and a pair of
      Powerflo s.  Every possible load on in the house, then kicked the
      well pump, and it didn't even blink the LED lights.  </p>
    <p>Ray Walters<br>
      Remote Solar</p>
    <div class="moz-cite-prefix">On 1/26/2026 9:51 AM, Maverick Brown
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:97112DD1-2B68-47A1-8231-625874083F37@mavericksolar.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      I have never believed any LFP battery maker that has 58.4V for
      charge voltage. That’s 3.65 Volts per cell in a 16S configuration.
      If you have any cell imbalance inside the pack, one cell could go
      above the upper limit of 3.65Vpc.
      <div><br>
      </div>
      <div>I have installed serval brands of LFP batteries, some great
        brands and some not as great.</div>
      <div><br>
      </div>
      <div>In pretty much all cases, I used 3.45Vpc (55.2V) as the
        Absorb and then set other voltages as appropriate based on that.
        In several cases, I also enabled EQ and set it to 3.5Vpc (56)
        just to make sure that cell balancing has a chance. If the
        voltage is too low, you will see a wider battery to battery SOC
        spread. I have corrected that by increasing the Absorb time
        and/or bump up the ABS Voltage.</div>
      <div><br>
      </div>
      <div>Many battery companies have been integration guides for their
        battery to Outback or Scheider. I have digested this to see what
        the ranges are for open charging. It would be good to get more
        details about: </div>
      <div> Cell balancing activation voltage</div>
      <div> Method for reading the cell voltages internal to batteries
        (a few companies have simple cables and easy apps for such,
        Pytes and Fortress)</div>
      <div> Method for reading individual battery SOC (Pytes has a
        serial cable and an app; Fortress has Guardian comm box, and
        there are others)</div>
      <div>
        <div><br>
        </div>
        <div>It would be good for long term health and understanding for
          wrenches to have more information…</div>
        <div><br>
        </div>
        <div>Here is my current working document on charging open loop.
          Let me know what you would do differently. Any suggestions are
          appreciated. I will send the XLS version to anyone who wants
          it.</div>
        <div><br>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div>
        <div><br id="lineBreakAtBeginningOfMessage">
          <div>
            <meta charset="UTF-8">
            <div dir="auto"
style="word-wrap: break-word; -webkit-nbsp-mode: space; line-break: after-white-space;">
              <div
style="color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant-caps: normal; font-weight: normal; letter-spacing: normal; text-align: start; text-indent: 0px; text-transform: none; white-space: normal; word-spacing: 0px; -webkit-text-stroke-width: 0px;">Maverick
                Brown<br>
                Off-Grid Solar Commander since 2006<br>
                <b>Maverick Solar Enterprises, Inc.</b></div>
              <div
style="color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant-caps: normal; font-weight: normal; letter-spacing: normal; text-align: start; text-indent: 0px; text-transform: none; white-space: normal; word-spacing: 0px; -webkit-text-stroke-width: 0px;"><b> •
                  Solar Commander Remote Power</b></div>
              <div
style="color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant-caps: normal; font-weight: normal; letter-spacing: normal; text-align: start; text-indent: 0px; text-transform: none; white-space: normal; word-spacing: 0px; -webkit-text-stroke-width: 0px;"><b> •
                  SunFlow Systems Cathodic Protection <br>
                </b><a class="moz-txt-link-abbreviated" href="mailto:maverick@mavericksolar.com">maverick@mavericksolar.com</a><br>
                512-460-9825<br>
              </div>
            </div>
          </div>
          <div><br>
            <blockquote type="cite">
              <div>On Jan 25, 2026, at 3:48 PM, Jason Szumlanski via
                RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org"><re-wrenches@lists.re-wrenches.org></a>
                wrote:</div>
              <br class="Apple-interchange-newline">
              <div>
                <div dir="auto">
                  <div>The specs for this particular battery list a
                    charging voltage up to 58.4V. I believe the BMS
                    protection level is set at 60V, but I need to
                    confirm with the manufacturer when they open on
                    Monday. </div>
                  <div dir="auto"><br>
                  </div>
                  <div dir="auto">I just noticed that the AIOs responded
                    to a relatively high load and entered a re-bulk type
                    of behavior. But the voltage stayed withing an
                    acceptable range. I'm not clear on how the AIO
                    handles re-bulk and also why the float voltage
                    setpoint isn't being respected (or how absorb time
                    is determined). </div>
                  <div><br>
                  </div>
                  <div data-smartmail="gmail_signature">
                    <div dir="ltr"><br>
                      Jason Szumlanski
                      <div><span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal
                          Solar Designer | Florida Solar Design Group</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                        <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP
                          Certified Solar Professional (PVIP)</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                        <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida
                          State Certified Solar Contractor CVC56956</span></div>
                      <div><font color="#333333"
face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida
                          Certified Electrical Contractor EC13013208</font></div>
                    </div>
                  </div>
                </div>
                <br>
                <div class="gmail_quote gmail_quote_container">
                  <div dir="ltr" class="gmail_attr">On Sun, Jan 25,
                    2026, 12:48 PM Zeke Yewdall via RE-wrenches <<a
                      href="mailto:re-wrenches@lists.re-wrenches.org"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>>
                    wrote:<br>
                  </div>
                  <blockquote class="gmail_quote"
style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
                    <div dir="ltr">
                      <div>I see on the Lithionics spec sheet it says a
                        charged voltage of 57.6 volts   This seems very
                        high for a 16 cell LFP battery.  I am used to
                        using 55 to 56 volts, maybe 56.5 volts at most
                        on a 16 cell LFP.  I suspect that the 57.6 is
                        the protection voltage of the BMS, not the
                        appropriate absorb voltage setting.  I have seen
                        this error a lot on lithium battery spec sheets,
                        where they give the overvoltage protection
                        level, which is not an appropriate absorb
                        setting for typical solar equipment.</div>
                      <div><br>
                      </div>
                      <div>Not everyone will agree with me, but the way
                        I set up absorb voltages when doing open loop
                        lithium battery systems is to NEVER let the BMS
                        do anything.  if the BMS shuts off charging,
                        that means that I already failed... the charge
                        controller or inverter should have stopped
                        charging before the BMS feels the need to
                        protect the cells.  Same with low voltage
                        disconnect... if the BMS shuts off due to low
                        voltage, I already failed -- I should have shut
                        the load off before the BMS felt the need to
                        turn of discharge to protect the cells.  The BMS
                        is like an airbag...only to react in cases of
                        emergency when the rest of the system doesn't
                        work properly.</div>
                      <div><br>
                      </div>
                      <div>Open loop equipment (all of the traditional
                        outback/magnum/schneider, etc stuff, plus any
                        AIO's in open loop setup) is designed to always
                        have a battery in the system to stabilize the DC
                        bus voltage.  Without the stabilizing effect of
                        the battery, voltage spikes can occur.  I find
                        that many charge controllers, especially the
                        midnite classic and victron ones, can actually
                        keep the system fairly stable without batteries,
                        but charging from inverters is more
                        questionable, and especially charging from any
                        DC generators can cause severe spikes if the
                        battery disconnects. I have fried equipment when
                        a lithium battery disconnected from a large
                        kohler DC generator and the generator couldn't
                        react fast enough to keep it from spiking to 75
                        volts or more.  This is why you never want the
                        BMS to disconnect... which means setting absorb
                        at a level where the BMS never feels
                        threatened.  Lithium battery manufactures giving
                        the voltage at which the BMS disconnects as the
                        "charge to" voltage does not help the
                        situation.  That may work when charging it with
                        a dedicated lithium battery charger, without
                        anything else connected to the battery while
                        it's charging.  But in a functioning solar
                        system with charging from multiple sources and
                        loads all occurring at the same time, we need to
                        be smarter than the battery, IMO.</div>
                      <div><br>
                      </div>
                      <div>Zeke</div>
                      <div><br>
                      </div>
                    </div>
                    _______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    Pay optional member dues here: <a
                      href="http://re-wrenches.org/"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
                    <br>
                    List Address: <a
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Change listserver email address & settings:<br>
                    <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    There are two list archives for searching. When one
                    doesn't work, try the other:<br>
                    <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                    <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List rules & etiquette:<br>
                    <a href="http://www.re-wrenches.org/etiquette.htm"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out or update participant bios:<br>
                    <a href="http://www.members.re-wrenches.org/"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
                    <br>
                  </blockquote>
                </div>
                <span id="cid:19bf71cbc031a4e9c551"><51V110A-8D-MODULE-REV2
                  (1).pdf></span><span id="cid:19bf71fb6e1d2076c872"><Screenshot_20260125_155512_Chrome.jpg></span><span
                  id="cid:19bf71fe2247cb03bcd3"><Screenshot_20260125_155550_Chrome.jpg></span><span
                  id="cid:19bf72005e4aa19e2064"><Screenshot_20260125_155623_Chrome.jpg></span><span
                  id="cid:19bf7201c54844606465"><Screenshot_20260125_155722_Chrome.jpg></span>_______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a><br>
                <br>
                List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address & settings:<br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                There are two list archives for searching. When one
                doesn't work, try the other:<br>
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                <br>
                List rules & etiquette:<br>
                <a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a><br>
                <br>
              </div>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>