    <p>Its really hard to find charge settings for Midnite Powerflow,
      but Midnite tech support told me the #s are printed on the side of
      the battery.  Definitely not 57.6v, which sounds way too high.</p>
    <p>Charge : 56.16 vdc<br>
      Float: 54 vdc</p>
    <div class="moz-cite-prefix">On 1/25/2026 11:20 AM, William Bryce
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAEQmjP6Do-=zE51WgWRCnVLfB-3vbSc-zeoP-42GbUA2O1J_=A@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">This is more of a programming / battery issue than
        an inverter inverter. In looking at the system settings, you are
        pushing the voltages of LFP to the max. This will cause the BMS
        to protect the battery. The "Spikes are caused by the BMS
        operation not the inverter (the current has to go someplace),
        the BMS FET's open under load the voltage will spike. The BMS
        should be the last resort in regards to battery charging
        protection.
        <div><br>
        </div>
        <div>All LFP batteries (cells) are mostly the same, and are made
          by 5 companies. The upper and lower voltages are set for LFP
          cell makers. The battery (pack) builders then program the BMS,
          and post on specification sheets the recommended setting
          voltages. With <u>lower quality cells and lower warranties</u>,
          you will see the voltages are set <u>higher.</u> When using
          A+ cells and long warranties you will see<u> lower</u> top
          voltage settings.<br>
          <div><br>
          </div>
          <div>Here are the recommended voltages for a 48V LFP (16S)
            pack when using A+ cells from CATL, BYD, and EVE  (this is
            from the cell manufacturers recommendations)</div>
          <div><strong style="color:rgb(0,0,0)"><br>
            </strong></div>
          <div><strong style="color:rgb(0,0,0)">Charging range:</strong><span
              class="gmail-Apple-converted-space"
              style="color:rgb(0,0,0)"> </span><strong
              style="color:rgb(0,0,0)">~52 V to 56 V</strong><br>
          </div>
          <div>
            <li style="color:rgb(0,0,0)">
              <p><strong>Full resting:</strong><span
                  class="gmail-Apple-converted-space"> </span><strong>~54.6
                  V</strong></p>
            </li>
            <li style="color:rgb(0,0,0)">
              <p><strong>Nominal operation:</strong><span
                  class="gmail-Apple-converted-space"> </span><strong>~51–53
                  V</strong></p>
            </li>
            <li style="color:rgb(0,0,0)">
              <p><strong>Stop discharging (resting):</strong><span
                  class="gmail-Apple-converted-space"> </span><strong>~48
                  V</strong></p>
              <p><strong>Recommended MAX voltage is 56.8V (for normal
                  use) 58.2 </strong><strong>Absolute MAX (chemistry
                  limit) Cell damage</strong></p>
            </li>
          </div>
          <div>You need to update the MNP AIO system firmware to V7. It
            is now the only AIO that has true charging control for LA
            (that works) the changes made were recommended by a highly
            qualified LA battery rep who is also a part of this list.  
            Set the absorb setting as you need, but be aware that it
            does not start the adsorb until the current drops below ~ 10
            amps or so.</div>
        </div>
      </div>
      <br>
      <div class="gmail_quote gmail_quote_container">
        <div dir="ltr" class="gmail_attr">On Sun, Jan 25, 2026 at
          12:48 PM Zeke Yewdall via RE-wrenches <<a
            href="mailto:re-wrenches@lists.re-wrenches.org"
            moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>>
          wrote:<br>
        </div>
        <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;border-left-color:rgb(204,204,204);padding-left:1ex">
          <div dir="ltr">
            <div>I see on the Lithionics spec sheet it says a charged
              voltage of 57.6 volts   This seems very high for a 16 cell
              LFP battery.  I am used to using 55 to 56 volts, maybe
              56.5 volts at most on a 16 cell LFP.  I suspect that the
              57.6 is the protection voltage of the BMS, not the
              appropriate absorb voltage setting.  I have seen this
              error a lot on lithium battery spec sheets, where they
              give the overvoltage protection level, which is not an
              appropriate absorb setting for typical solar equipment.</div>
            <div><br>
            </div>
            <div>Not everyone will agree with me, but the way I set up
              absorb voltages when doing open loop lithium battery
              systems is to NEVER let the BMS do anything.  if the BMS
              shuts off charging, that means that I already failed...
              the charge controller or inverter should have stopped
              charging before the BMS feels the need to protect the
              cells.  Same with low voltage disconnect... if the BMS
              shuts off due to low voltage, I already failed -- I should
              have shut the load off before the BMS felt the need to
              turn of discharge to protect the cells.  The BMS is like
              an airbag...only to react in cases of emergency when the
              rest of the system doesn't work properly.</div>
            <div><br>
            </div>
            <div>Open loop equipment (all of the traditional
              outback/magnum/schneider, etc stuff, plus any AIO's in
              open loop setup) is designed to always have a battery in
              the system to stabilize the DC bus voltage.  Without the
              stabilizing effect of the battery, voltage spikes can
              occur.  I find that many charge controllers, especially
              the midnite classic and victron ones, can actually keep
              the system fairly stable without batteries, but charging
              from inverters is more questionable, and especially
              charging from any DC generators can cause severe spikes if
              the battery disconnects. I have fried equipment when a
              lithium battery disconnected from a large kohler DC
              generator and the generator couldn't react fast enough to
              keep it from spiking to 75 volts or more.  This is why you
              never want the BMS to disconnect... which means setting
              absorb at a level where the BMS never feels threatened. 
              Lithium battery manufactures giving the voltage at which
              the BMS disconnects as the "charge to" voltage does not
              help the situation.  That may work when charging it with a
              dedicated lithium battery charger, without anything else
              connected to the battery while it's charging.  But in a
              functioning solar system with charging from multiple
              sources and loads all occurring at the same time, we need
              to be smarter than the battery, IMO.</div>
            <div><br>
            </div>
            <div>Zeke</div>
            <div><br>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          Pay optional member dues here: <a
            href="http://re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
          <br>
          List Address: <a
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address & settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          There are two list archives for searching. When one doesn't
          work, try the other:<br>
          <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
          <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules & etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            rel="noreferrer" target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true"
            class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>