<html>
<head>
<meta http-equiv="Content-Type" content="text/html; charset=us-ascii">
<style type="text/css" style="display:none;"> P {margin-top:0;margin-bottom:0;} </style>
</head>
<body dir="ltr">
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
So I like this concept but if I was physically close from solar to gen then I'd just add dedicated PV conductors and move PoI to gen line side. But solar is on other side of home separated only by Texas hard scrabble rock that is nearly impervious to trenching.<br>
<br>
Now if I had wireless controlled contactors....??? Is such a thing made?</div>
<div class="elementToProof" id="Signature">
<div style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div style="direction: ltr; text-align: left; text-indent: 0px; background-color: rgb(255, 255, 255); margin: 0px; font-family: "Segoe UI", "Segoe UI Web (West European)", -apple-system, BlinkMacSystemFont, Roboto, "Helvetica Neue", sans-serif; font-size: 15px; color: rgb(36, 36, 36);">
<b>Howard "Scot" Arey</b></div>
<div style="direction: ltr; text-align: left; text-indent: 0px; background-color: rgb(255, 255, 255); margin: 0px; font-family: "Segoe UI", "Segoe UI Web (West European)", -apple-system, BlinkMacSystemFont, Roboto, "Helvetica Neue", sans-serif; font-size: 15px; color: rgb(36, 36, 36);">
<b>Owner, Solar CenTex</b></div>
<div style="direction: ltr; text-align: left; text-indent: 0px; background-color: rgb(255, 255, 255); margin: 0px; font-family: "Segoe UI", "Segoe UI Web (West European)", -apple-system, BlinkMacSystemFont, Roboto, "Helvetica Neue", sans-serif; font-size: 15px; color: rgb(36, 36, 36);">
254-300-1228 </div>
<div style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
</div>
<div id="appendonsend"></div>
<hr style="display:inline-block;width:98%" tabindex="-1">
<div id="divRplyFwdMsg" dir="ltr"><font face="Calibri, sans-serif" style="font-size:11pt" color="#000000"><b>From:</b> RE-wrenches <re-wrenches-bounces@lists.re-wrenches.org> on behalf of Zeke Yewdall via RE-wrenches <re-wrenches@lists.re-wrenches.org><br>
<b>Sent:</b> Wednesday, January 21, 2026 2:55 PM<br>
<b>To:</b> RE-wrenches <re-wrenches@lists.re-wrenches.org><br>
<b>Cc:</b> Zeke Yewdall <zeke@darkforestsolar.com><br>
<b>Subject:</b> Re: [RE-wrenches] Will IQ8 microinverters backfeed a generator during grid interruptions</font>
<div> </div>
</div>
<div>
<div dir="ltr">
<div>In that case, we're getting way off track and way more complicated :P  </div>
<div><br>
</div>
<div>Just put a contactor between the PV array and the POI using the NC contacts, with the coil powered off the generator.  Then the PV array can never backfeed the generator because it'll be turned off anytime the generator is running.</div>
<div><br>
</div>
<div>Zeke</div>
<div><br>
</div>
<div>------------------</div>
<div dir="ltr"><br>
</div>
<div dir="ltr"><br>
</div>
<div dir="ltr">Thanks but I'm just trying to grid-tie a small Enphase array without ESS where the point of interconnection is on the customer side of the generator/ATS.<br>
<br>
Trying to use existing wires in place to simplify and lower costs...but the generator is my constraint because I need the PoI to be on line side of the ATS.<br>
<br>
Howard "Scot" Arey<br>
Owner, Solar CenTex<br>
254-300-1228</div>
<div><br>
</div>
<div><br>
</div>
</div>
</div>
</body>
</html>