<div dir="ltr"><div>I do not know how they do it in Texas, but in Colorado, it's pretty typical to run a 200A (38kW continuous) service from a 10kVA transformer.  Or even several houses with 100 to 200A services from a single 10 or 15kVA transformer.  If all even a few of the houses start drawing anywhere near their full amperage for a long period of the time (grow operations were the common reason for this) the transformer explodes.  They are apparently relying on the very low typical load factor for residential services. Many of these are older services installed in the 70's to 90's, but some are newer ones and still not a 25kVA transformer for a 200A service that would seem more reasonable.  A grid tied PV system will often load the transformer much higher than typical residential loads because of the long hours of operation.</div><div><br></div><div>I've had two ESS/PV systems recently where they required a transformer upgrade before they would allow me to backfeed at full system capacity. Both were all in one inverters, not separate PV and ESS inverters.  In one case I had 10.135kW CEC rating of inverter capacity on a 10kVA transformer, but in the other case they calculated that I could not go over 6.6kVA of export on a 10kVA transformer for some reason -- this was on a brand new service, new construction, so I was quite surprised by this limit.  2kW seems insanely low for a 25kVA transformer to me.  In both of my cases in Colorado, they are upgrading the transformers to 25kVA at very little cost to the customer -- $300, which I figure is 10% or less the actual cost -- so we opted for the transformer upgrade rather than limiting export.  Sounds like Oncor is charging actual cost for the transformer upgrade?</div><br><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr">Zeke Yewdall<div>PV Engineer</div><div>NABCEP #031508-89</div><div><a href="mailto:zeke@darkforestsolar.com" target="_blank">zeke@darkforestsolar.com</a></div><div>303-523-3592</div></div></div></div></div></div>