<div dir="ltr">Thank you, Wrenches, as always for your spirited dialog.  It has been a common practice of our company for a long time to pair MC4 connectors and PV wire for commercial 1000v systems.  In a recent install the crew wasn't properly informed and they employed Buchanan crimps (as is our standard < 600v residential solution).  A QA/QC contractor happens to have a very, very close eye on this project and has requested the submittal of the Buchanan spec sheet.  This is what prompted my question to the list.<div><br></div><div>I'm not going to lie, I was hoping Mr. Mehalic was going to answer the question with something along the lines of '<i>a rooftop j-box qualifies as a fixture and you're good to go</i>' but I was equally prepared for "<i>I do think the text on the Buchanan spec sheet in regards to voltage makes it a no-go for 1kV+ systems</i>".  </div><div><br></div><div>I wasn't expecting the tangential discussion about the use of MC4 connectors inside a junction box and I'm going to have to weigh the pros and cons of them in this application carefully.  That being said, in a decade of performing installations doing precisely that, I've opened plenty of them up years later and been very happy with what I've found inside looking neat and tidy.  And I can't think of a single arc fault in such a scenario that wasn't directly related to someone improperly torquing the connector.</div><div><br></div><div>Cheers,</div><div>Sam</div></div>