<p class="gmail-p1">I think there’s a real point of diminishing returns here. Even on whole-home backup systems, I usually skip a dedicated bypass as long as there’s a reasonable way to restore power in a true emergency.</p>
<p class="gmail-p1">For <span class="gmail-s1"><b>off-grid</b></span>, it’s definitely convenient to send generator power to the loads during inverter service. But if the generator feed is spliced to feed both the inverter and one side of a bypass switch, you still have to disconnect the inverter feed to make it safe for service, so the benefit can be marginal. The real benefit here is for clients to be able to self-service to restore power during a component failure.</p>
<p class="gmail-p1">For <span class="gmail-s1"><b>on-grid</b></span> systems, I recently dealt with an Enphase System Controller failure. There was a separate main disconnect ahead of it (no main breaker in the controller), and the load lugs fed the whole house. The controller failed with the microgrid interconnect contactor stuck open, forcing the client off-grid even though utility power was available.</p>
<p class="gmail-p1">Bypassing it took nothing more than a pair of 3/0 Polaris taps and about ten minutes to splice the line to the load. Would a 200 A bypass switch have been worth it? Not really. The quick splice worked fine, and once Enphase sent a field tech to replace the MID, I just reversed it – no big deal.</p>
<p class="gmail-p1">Back to <span class="gmail-s1">off-grid, or on-grid for that matter... T</span>his is where a well-planned wiring trough shines. You can make quick splices to bypass smart loads or even whole-house feeders when needed. On a recent grid-tied multi-Midnite AIO installation, I made sure the AC in and AC out power distribution blocks were close enough together that I could completely bypass the inverters with some quick Polaris tap splices. Or, I could quickly remove and cap off a single inverter from the distribution blocks. That's even better than a bypass because you can selectively bypass a single inverter for service. </p><p class="gmail-p1">Most bypass switches will live their entire lives never being used, so I tend to design for practical flexibility rather than theoretical perfection. There are definitely situations where a bypass switch is mandatory, in my opinion, but when there are options and the risk is low, I often save the customer a few bucks after having a conversation with them about convenience, cost, reliability/resilience, and serviceability.</p></div></div><div><div dir="ltr" class="gmail_signature"><div dir="ltr"><br>Jason Szumlanski<div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida State Certified Solar Contractor CVC56956</span></div><div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida Certified Electrical Contractor EC13013208</font></div></div></div></div><br></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Wed, Oct 15, 2025 at 11:26 AM Dave Tedeyan via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div>Hi All, </div><div><br></div><div>Now that some inverters have "smart" load capabilities, I am musing on whether to put in a separate bypass for each smart load. I am thinking specifically about the Midnite AIO inverter, where the Smart loads are powered directly from the inverter, rather than just providing a relay to cut power (like in the Avalon SEP, if anyone has used those). The Midnite AIO also has provisions to run other backed up loads directly from the inverter as well.</div><div><br></div><div>But if there was a system failure, and you have a bypass switch installed, this will only power the loads in the backed up loads panel from the grid, but not the specific loads that originate from the inverter. Are people installing bypasses for every individual load that originates in the inverter? I was just looking at William's interlock system, but I don't think that you can utilize that kind of system to have some smart loads in there as well. It seems like you can utilize the panel he labels "inverter feed" on his one line diagram to power other backed up loads, but the would not work for a smart load. </div><div><br></div><div>Cheers,</div><div>Dave</div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature"><div dir="ltr"><br style="color:rgb(34,34,34)"><div dir="ltr" style="color:rgb(34,34,34)"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"></div></div></div><div dir="ltr"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:525px;font-size:11pt;font-family:Arial,sans-serif"><tbody><tr><td width="125" valign="top" rowspan="6" style="padding:0px 10px 0px 0px;font-size:10pt;border-right:1px solid rgb(236,189,0);width:125px;vertical-align:top"><a href="https://www.sungineersolar.com/" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span id="mt-tracked-link_0_1760553392336" style="color:red"></span><img border="0" alt="Logo" width="105" src="https://sungineersolar.com/wp-content/uploads/2019/08/Logo-Image-Only-1.png" style="border: 0px; vertical-align: middle; width: 105px; height: auto;"></a></td><td style="padding:0px 0px 0px 10px"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;background-color:transparent"><tbody><tr><td valign="top" style="padding:0px 0px 5px 10px;width:400px;vertical-align:top"><span style="color:rgb(236,189,0);font-size:11pt;font-weight:700">Dave Tedeyan, P.E.<br></span><span style="font-size:11pt;font-weight:700"><font color="#ecbd00">Owner | Sungineer Solar</font><br></span></td></tr><tr><td valign="top" style="padding:5px 0px 5px 10px;font-size:10pt;vertical-align:top;line-height:17px"><span style="color:rgb(236,189,0)"><span style="font-weight:700">p: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">he | him | his</span><span style="color:rgb(236,189,0)"><span style="font-weight:700"><br>a: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">1653 Slaterville Rd.</span> <span style="font-size:10pt;color:rgb(0,0,0)">| Ithaca, NY 14850</span><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">w:</span></span><a href="http://www.sungineersolar.com/" rel="noopener" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span id="mt-tracked-link_0_1760553392338" style="color:red"></span><span style="font-size:10pt;color:rgb(0,0,0)"> www.sungineersolar.com</span></a><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">c:</span></span><span style="font-size:10pt;color:rgb(0,0,0)"> (607) 270-0370</span></td></tr></tbody></table></td></tr></tbody></table></div></div></div></div></div></div>