<div dir="ltr">On the Midnite AIO  if it loses solar or battery it will bypass AC from the AC in as long as it does not encounter a Critical error.<div>If it has an error then it will open the relay and you will lose power.</div><div><br></div><div>But with any inverter I always quote in a manual bypass. it is worth every dollar. For you and the customer.</div><div><br></div><div>Logan</div></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Wed, Oct 15, 2025 at 3:43 PM Dave Tedeyan via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;border-left-color:rgb(204,204,204);padding-left:1ex"><div dir="ltr">Jason, <div><br></div><div>While I agree that it is often fairly simple to bypass an inverter, you have to be there to do it. I am currently dealing with a Midnite system that has needed multiple firmware upgrades, and for some reason recently would not charge the batteries. No one noticed until they completely discharged, and the backed up loads turned off. We have been able to get them charging again, but it has been really nice to tell the customer to just throw the transfer switch and let the loads run off the grid while this gets sorted out. Tech support has been very helpful, and we've got the batteries charging again, and I am really glad I did not have to make an emergency trip to the site to temporarily wire the AC in to the AC out.</div><div><br></div><div>AC coupled systems with an MID seem to be a little more resilient in this fashion though. For that Enphase customer to lose power to the loads, both the System Controller AND the batteries would have to fail at the same time. I recently ran into an Avalon SEP that failed. We were able to get it to still pass through grid power and even get both the AC and DC coupled solar working immediately. Then at my leisure I was able to go to the site to troubleshoot (and eventually replace) the SEP. They just did not have backup power during that time, but at least they had power to the house.</div><div><br></div><div>Cheers,</div><div>Dave</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Oct 15, 2025 at 2:50 PM Jason Szumlanski via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;border-left-color:rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div dir="ltr"><div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">





<p>I think there’s a real point of diminishing returns here. Even on whole-home backup systems, I usually skip a dedicated bypass as long as there’s a reasonable way to restore power in a true emergency.</p>
<p>For <span><b>off-grid</b></span>, it’s definitely convenient to send generator power to the loads during inverter service. But if the generator feed is spliced to feed both the inverter and one side of a bypass switch, you still have to disconnect the inverter feed to make it safe for service, so the benefit can be marginal. The real benefit here is for clients to be able to self-service to restore power during a component failure.</p>
<p>For <span><b>on-grid</b></span> systems, I recently dealt with an Enphase System Controller failure. There was a separate main disconnect ahead of it (no main breaker in the controller), and the load lugs fed the whole house. The controller failed with the microgrid interconnect contactor stuck open, forcing the client off-grid even though utility power was available.</p>
<p>Bypassing it took nothing more than a pair of 3/0 Polaris taps and about ten minutes to splice the line to the load. Would a 200 A bypass switch have been worth it? Not really. The quick splice worked fine, and once Enphase sent a field tech to replace the MID, I just reversed it – no big deal.</p>
<p>Back to <span>off-grid, or on-grid for that matter... T</span>his is where a well-planned wiring trough shines. You can make quick splices to bypass smart loads or even whole-house feeders when needed. On a recent grid-tied multi-Midnite AIO installation, I made sure the AC in and AC out power distribution blocks were close enough together that I could completely bypass the inverters with some quick Polaris tap splices. Or, I could quickly remove and cap off a single inverter from the distribution blocks. That's even better than a bypass because you can selectively bypass a single inverter for service. </p><p>Most bypass switches will live their entire lives never being used, so I tend to design for practical flexibility rather than theoretical perfection. There are definitely situations where a bypass switch is mandatory, in my opinion, but when there are options and the risk is low, I often save the customer a few bucks after having a conversation with them about convenience, cost, reliability/resilience, and serviceability.</p></div></div><div><div dir="ltr" class="gmail_signature"><div dir="ltr"><br>Jason Szumlanski<div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida State Certified Solar Contractor CVC56956</span></div><div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida Certified Electrical Contractor EC13013208</font></div></div></div></div><br></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Oct 15, 2025 at 11:26 AM Dave Tedeyan via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left-width:1px;border-left-style:solid;border-left-color:rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div>Hi All, </div><div><br></div><div>Now that some inverters have "smart" load capabilities, I am musing on whether to put in a separate bypass for each smart load. I am thinking specifically about the Midnite AIO inverter, where the Smart loads are powered directly from the inverter, rather than just providing a relay to cut power (like in the Avalon SEP, if anyone has used those). The Midnite AIO also has provisions to run other backed up loads directly from the inverter as well.</div><div><br></div><div>But if there was a system failure, and you have a bypass switch installed, this will only power the loads in the backed up loads panel from the grid, but not the specific loads that originate from the inverter. Are people installing bypasses for every individual load that originates in the inverter? I was just looking at William's interlock system, but I don't think that you can utilize that kind of system to have some smart loads in there as well. It seems like you can utilize the panel he labels "inverter feed" on his one line diagram to power other backed up loads, but the would not work for a smart load. </div><div><br></div><div>Cheers,</div><div>Dave</div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature"><div dir="ltr"><br style="color:rgb(34,34,34)"><div dir="ltr" style="color:rgb(34,34,34)"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"></div></div></div><div dir="ltr"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:525px;font-size:11pt;font-family:Arial,sans-serif"><tbody><tr><td width="125" valign="top" rowspan="6" style="padding:0px 10px 0px 0px;font-size:10pt;border-right-width:1px;border-right-style:solid;border-right-color:rgb(236,189,0);width:125px;vertical-align:top"><a href="https://www.sungineersolar.com/" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span id="m_-5585647199380464962m_6280721900387033935mt-tracked-link_0_1760553392336" style="color:red"></span><img border="0" alt="Logo" width="105" src="https://sungineersolar.com/wp-content/uploads/2019/08/Logo-Image-Only-1.png" style="border: 0px; vertical-align: middle; width: 105px; height: auto;"></a></td><td style="padding:0px 0px 0px 10px"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;background-color:transparent"><tbody><tr><td valign="top" style="padding:0px 0px 5px 10px;width:400px;vertical-align:top"><span style="color:rgb(236,189,0);font-size:11pt;font-weight:700">Dave Tedeyan, P.E.<br></span><span style="font-size:11pt;font-weight:700"><font color="#ecbd00">Owner | Sungineer Solar</font><br></span></td></tr><tr><td valign="top" style="padding:5px 0px 5px 10px;font-size:10pt;vertical-align:top;line-height:17px"><span style="color:rgb(236,189,0)"><span style="font-weight:700">p: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">he | him | his</span><span style="color:rgb(236,189,0)"><span style="font-weight:700"><br>a: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">1653 Slaterville Rd.</span> <span style="font-size:10pt;color:rgb(0,0,0)">| Ithaca, NY 14850</span><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">w:</span></span><a href="http://www.sungineersolar.com/" rel="noopener" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span id="m_-5585647199380464962m_6280721900387033935mt-tracked-link_0_1760553392338" style="color:red"></span><span style="font-size:10pt;color:rgb(0,0,0)"> www.sungineersolar.com</span></a><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">c:</span></span><span style="font-size:10pt;color:rgb(0,0,0)"> (607) 270-0370</span></td></tr></tbody></table></td></tr></tbody></table></div></div></div></div></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br><br>
<br>
</blockquote></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>