<div dir="ltr"><div>I have done a few upgrades with Magnum inverters on newer LFP batteries (EG4 LL series if they are a 12 or 24 volt magnum, various ones Midnite and Eclipse and ReLion for 48 volt magnums).   The newer magnums (not sure exact date or firmware number) seem to be okay, other than LVD not really being adjustable high enough to function with an 8 or 16 cell LFP -- can work with a 15 cell LFP on 48 volts).  I have heard that the older magnums just will not charge properly, as a few other folks here have described. </div><div><br></div><div>I always try to have a BMK do SOC based generator control if using lithium, as voltage is very hard to get decent control with.  But... make sure you get to recalibration settings for the BMS on the lithium batteries regularly, as SOC will drift over several weeks of low SOC cycling and be massively out of reality... I've seen it drift 1 or 2% a day, which isn't much if you get back to 100% each day, but is ALOT if you keep doing this for 3 or 4 weeks... like 50% different than reality...  Best practice would be a SOC control for generator starting with a voltage catch as a backup in case SOC drifts.</div><div><br></div><div>I have not heard that Victron has any intention of introducing a split phase unit.  The US market is just not a big enough part of their worldwide sales it seems, and to them the ability to stack two 120 volt units in series solves this problem.  You can also use a 230 volt EU unit set to 60Hz, and with an autotransformer to synthesize the neutral.  Not UL listed that way, but it's another way to get 120/240 split phase from a single inverter for off grid use (not as useable on grid, as then you have to synthesize the neutral on both the input and output and the two neutrals are not exactly the same potential, so you end up having to run an isolated neutral on the backed up loads, which introduces even more code issues...</div></div>