<div dir="auto">Hi all,</div><div dir="auto"><br></div><div dir="auto">I’m finding out that some jurisdictions in Texas are requiring ESS output to be equal to or greater than the calculated load of a dwelling. For example, if backing up the whole home, and the service load is calculated at 150A, the ESS would require to continuously output 150A OR EMS is required to bring the calculated load to or below that of the ESS. AHJ’s in a few areas of Texas are dying on this hill and to actually meet the calculated load, systems would need to be significantly larger than needed. </div><div dir="auto"><br></div><div dir="auto">I know that previous versions of 706 (specifically NEC 2017) could lead one to argue this point, but Texas had adopted NEC 2023, and it’s only article 710 that indicates a system operating in isolation of the grid should has sufficient output to supply load to the largest backed up load. </div><div dir="auto"><br></div><div dir="auto">Has anyone run into this issue? And if so, what have people been doing to either meet these outdated requirements or successfully push back? </div><div dir="auto"><br></div><div dir="auto">Thanks!</div><div dir="auto"><br clear="all"><br clear="all"><div dir="auto"><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div>Chris Sparadeo</div><div><br></div><div>VT Master Electrician # EM 08220</div><div>C_802-369-4458</div><div></div></div></div></div></div></div></div>