<div dir="ltr"><div class="gmail_default" style="font-size:small">Thank you all for your comments. I am going to bat with the Sonoma County building department, and will report back.</div><div class="gmail_default" style="font-size:small">Mike</div></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Tue, Jul 29, 2025 at 3:27 PM Bradley Bassett via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr">What I used to specify for exterior disconnect for a battery bank was the MidNite MNLBC-W250. I believe you can connect larger battery cables to input and output bypassing the smaller busbar input. <div><a href="https://www.midnitesolar.com/productPhoto.php?product_ID=687&productCat_ID=9&sortOrder=1&act=p" target="_blank">https://www.midnitesolar.com/productPhoto.php?product_ID=687&productCat_ID=9&sortOrder=1&act=p</a></div><div>If rapid shutdown is also required you can substitute the breaker with a remote trip version for the main 250A breaker. It needs a 24VDC signal to trip and is manually reset so it's not ideal, but costs far less than a true DC rated disconnect. </div><div><br></div><div>However, it seems to me, agreeing with others here, that it should not be required in this case, that the breaker in the inverter should suffice.</div><div><br></div><div>Brad Bassett</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Jul 29, 2025 at 2:47 PM Blair May via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto"><div>Sue what happened to the Birdhouse. My e panel has shunt tripped 250A battery breakers that is acquitted outside the building.</div><div dir="auto">Tump </div><div><br></div><div>Blair "Tump" May</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Jul 29, 2025, 1:09 PM Sue Stankevitz via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div lang="EN-US">
<div>
<p class="MsoNormal"><span style="font-family:Calibri,sans-serif">Midnite does not offer an outdoor rated enclosure for our large breakers but if only 100a was needed as Mike was asking about our MNPV3 with an MNEPV100(100a DC breaker) would be outdoor rated
and lockable.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<div style="margin-top:12pt;margin-bottom:12pt">
<p class="MsoNormal"><span style="color:black">Sue Stankevitz</span><span style="color:black"><br>
<a href="https://www.midnitesolar.com/index.php" rel="noreferrer" target="_blank">MidNite Solar, Inc.</a><br>
</span><span style="color:black">(360) 403-7207 (XT122)</span><span style="color:black"><u></u><u></u></span></p>
</div>
<div style="margin-top:12pt;margin-bottom:12pt">
<p class="MsoNormal"><span style="color:black"><img border="0" width="123" height="68" style="width: 1.2812in; height: 0.7083in;" id="m_7174831409824040116m_4257109216041446887m_-7883920503925460775Picture_x0020_1" src="cid:ii_1985849a9a34cdccc1"><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="font-family:Calibri,sans-serif"><u></u> <u></u></span></p>
<div style="border-right:none;border-bottom:none;border-left:none;border-top:1pt solid rgb(225,225,225);padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-size:11pt;font-family:Calibri,sans-serif">From:</span></b><span style="font-size:11pt;font-family:Calibri,sans-serif"> RE-wrenches <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>>
<b>On Behalf Of </b>MD Electric & Solar via RE-wrenches<br>
<b>Sent:</b> Tuesday, July 29, 2025 12:46 PM<br>
<b>To:</b> jay <<a href="mailto:jay.peltz@gmail.com" rel="noreferrer" target="_blank">jay.peltz@gmail.com</a>><br>
<b>Cc:</b> MD Electric & Solar <<a href="mailto:mdelectricsolar@gmail.com" rel="noreferrer" target="_blank">mdelectricsolar@gmail.com</a>>; RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Subject:</b> Re: [RE-wrenches] Battery RSD<u></u><u></u></span></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">Wondering if Midnight solar makes something outdoor rated, with a typical 250ADC breaker, like this:<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Outdoor rated, lockable....<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><a href="https://www.midnitesolar.com/productPhoto.php?product_ID=76&productCat_ID=8&sortOrder=5&act=p" rel="noreferrer" target="_blank">https://www.midnitesolar.com/productPhoto.php?product_ID=76&productCat_ID=8&sortOrder=5&act=p</a><u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">On Tue, Jul 29, 2025 at 9:39<span style="font-family:Arial,sans-serif"> </span>AM jay <<a href="mailto:jay.peltz@gmail.com" rel="noreferrer" target="_blank">jay.peltz@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<blockquote style="border-top:none;border-right:none;border-bottom:none;border-left:1pt solid rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in">
<div>
<p class="MsoNormal">Maybe if you left the key on a chain to open the door, and placard with instructions on the outside that would work?<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<div>
<p class="MsoNormal"><br>
<br>
<u></u><u></u></p>
<blockquote style="margin-top:5pt;margin-bottom:5pt">
<div>
<p class="MsoNormal">On Jul 29, 2025, at 10:23<span style="font-family:Arial,sans-serif"> </span>AM, MD Electric & Solar <<a href="mailto:mdelectricsolar@gmail.com" rel="noreferrer" target="_blank">mdelectricsolar@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<div>
<p class="MsoNormal">Correct, it does not have an external disconnect, but if you open the cover, each battery has it's own disconnect and the Sol-Ark has a battery disconnect. <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Looks like I'm in the market for a 100 amp rated outdoor, lockable DC rated knife switch.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Mike<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">On Tue, Jul 29, 2025 at 9:16<span style="font-family:Arial,sans-serif"> </span>AM jay <<a href="mailto:jay.peltz@gmail.com" rel="noreferrer" target="_blank">jay.peltz@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<blockquote style="border-top:none;border-right:none;border-bottom:none;border-left:1pt solid rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in">
<div>
<p class="MsoNormal">I had to look up that battery enclosure and if I understand correctly it does not have an external breaker/disconnect so yes the inspector is correct in the need for one if I understand.<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">jay<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal"><br>
<br>
<u></u><u></u></p>
<blockquote style="margin-top:5pt;margin-bottom:5pt">
<div>
<p class="MsoNormal">On Jul 29, 2025, at 10:09<span style="font-family:Arial,sans-serif"> </span>AM, MD Electric & Solar <<a href="mailto:mdelectricsolar@gmail.com" rel="noreferrer" target="_blank">mdelectricsolar@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<div>
<p class="MsoNormal">Here is the reference, attached.<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<p class="MsoNormal">On Tue, Jul 29, 2025 at 8:49<span style="font-family:Arial,sans-serif"> </span>AM jay <<a href="mailto:jay.peltz@gmail.com" rel="noreferrer" target="_blank">jay.peltz@gmail.com</a>> wrote:<u></u><u></u></p>
</div>
<blockquote style="border-top:none;border-right:none;border-bottom:none;border-left:1pt solid rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in">
<p class="MsoNormal" style="margin-bottom:12pt">I’ll let the code experts chime in, but I would ask for the code reference they are referring to.<br>
<br>
The only one I can think of has to do with if the batteries are on the other side of a wall.<br>
<br>
Thats as clean an install as they come<br>
<br>
jay<br>
<br>
<br>
<br>
> On Jul 29, 2025, at 9:43<span style="font-family:Arial,sans-serif"> </span>AM, MDElectricSolar <<a href="mailto:mdelectricsolar@gmail.com" rel="noreferrer" target="_blank">mdelectricsolar@gmail.com</a>> wrote:<br>
> <br>
> <image0.jpeg><br>
> Michael D Nelson<br>
> MD Electric & Solar, Inc.<br>
> 707-684-0064 mobile<br>
> 707-884-1862 office<br>
> <a href="http://www.mdelectricsolar.com/" rel="noreferrer" target="_blank">www.mdelectricsolar.com</a><br>
> <a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a><br>
> <br>
> <br>
>> On Jul 29, 2025, at 8:06<span style="font-family:Arial,sans-serif"> </span>AM, Jay via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br>
>> <br>
>> <span style="font-family:Tahoma,sans-serif"></span>What is the layout of the equipment<br>
>> <br>
>> Are the batteries next to and therefore in sight of the inverter?<br>
>> <br>
>> Jay<br>
>> <br>
>>> On Jul 29, 2025, at 8:44<span style="font-family:Arial,sans-serif"> </span>AM, MDElectricSolar via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br>
>>> <br>
>>> <span style="font-family:Tahoma,sans-serif"></span>Wrenches,<br>
>>> I have a building inspector in my county of Sonoma who has just told me that we need to install a rapid shutdown switch of some type between my LFZ battery bank and my Solark 15k inverter. He mentioned some type of knife switch within 5 feet of the equipment.
I cannot find any reference to this requirement anywhere but he insists it is required. These batteries happen to be simplify or brakes and Stratton batteries and each battery has its own 80 amp breaker on the battery and the Solark has a battery disconnect
switch built-in. We do have module level RSD which kills the solar output as well as the inverter output when the button is pushed. Does anyone have any experience with this or can they point me to the correct code section or what are others doing to comply
with this requirement?<br>
>>> <br>
>>> <br>
>>> Michael D Nelson<br>
>>> MD Electric & Solar, Inc.<br>
>>> 707-684-0064 mobile<br>
>>> 707-884-1862 office<br>
>>> <a href="http://www.mdelectricsolar.com/" rel="noreferrer" target="_blank">www.mdelectricsolar.com</a><br>
>>> <a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a><br>
>>> <br>
>>> _______________________________________________<br>
>>> List sponsored by Redwood Alliance<br>
>>> <br>
>>> Pay optional member dues here: <a href="http://re-wrenches.org/" rel="noreferrer" target="_blank">
http://re-wrenches.org</a><br>
>>> <br>
>>> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
>>> <br>
>>> Change listserver email address & settings:<br>
>>> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
>>> <br>
>>> There are two list archives for searching. When one doesn't work, try the other:<br>
>>> <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
>>> <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
>>> <br>
>>> List rules & etiquette:<br>
>>> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
>>> <br>
>>> Check out or update participant bios:<br>
>>> <a href="http://www.members.re-wrenches.org/" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
>>> <br>
>> _______________________________________________<br>
>> List sponsored by Redwood Alliance<br>
>> <br>
>> Pay optional member dues here: <a href="http://re-wrenches.org/" rel="noreferrer" target="_blank">
http://re-wrenches.org</a><br>
>> <br>
>> List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
>> <br>
>> Change listserver email address & settings:<br>
>> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
>> <br>
>> There are two list archives for searching. When one doesn't work, try the other:<br>
>> <a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
>> <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
>> <br>
>> List rules & etiquette:<br>
>> <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
>> <br>
>> Check out or update participant bios:<br>
>> <a href="http://www.members.re-wrenches.org/" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
>> <u></u><u></u></p>
</blockquote>
</div>
<div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><span>-- </span><u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size:9.5pt">Michael D Nelson</span><u></u><u></u></p>
</div>
<div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">MD Electric & Solar Inc.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Office: 707-412-3181</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Cell: 707-684-0064</span><u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal"><a href="http://www.mdelectricsolar.com/" rel="noreferrer" target="_blank"><span style="font-size:9.5pt">www.mdelectricsolar.com</span></a><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white"><a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a></span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><PRMD BLD_20250728_062230.pdf><u></u><u></u></p>
</div>
</blockquote>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><span>-- </span><u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size:9.5pt">Michael D Nelson</span><u></u><u></u></p>
</div>
<div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">MD Electric & Solar Inc.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Office: 707-412-3181</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Cell: 707-684-0064</span><u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal"><a href="http://www.mdelectricsolar.com/" rel="noreferrer" target="_blank"><span style="font-size:9.5pt">www.mdelectricsolar.com</span></a><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white"><a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a></span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</blockquote>
</div>
<div>
<p class="MsoNormal"><br clear="all">
<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<p class="MsoNormal"><span>-- </span><u></u><u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-size:9.5pt">Michael D Nelson</span><u></u><u></u></p>
</div>
<div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">MD Electric & Solar Inc.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Office: 707-412-3181</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white">Cell: 707-684-0064</span><u></u><u></u></p>
</div>
</div>
<div>
<p class="MsoNormal"><a href="http://www.mdelectricsolar.com/" rel="noreferrer" target="_blank"><span style="font-size:9.5pt">www.mdelectricsolar.com</span></a><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="color:black;background:white"><a href="http://www.facebook.com/mdelectricandsolar" rel="noreferrer" target="_blank">www.facebook.com/mdelectricandsolar</a></span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><div><br clear="all"></div><div><br></div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div><span style="font-size:12.8px">Michael D Nelson</span><br></div><div><div><span style="background-color:rgb(255,255,255)">MD Electric & Solar Inc.</span></div><div><span style="background-color:rgb(255,255,255)">Office: 707-412-3181</span></div><div><span style="background-color:rgb(255,255,255)">Cell: 707-684-0064</span></div></div><div><a href="http://www.mdelectricsolar.com/" style="font-size:12.8px" target="_blank">www.mdelectricsolar.com</a><span style="background-color:rgb(255,255,255)"><br></span></div><div><span style="background-color:rgb(255,255,255)"><a href="http://www.facebook.com/mdelectricandsolar" target="_blank">www.facebook.com/mdelectricandsolar</a></span></div><div><br></div><div><br></div></div></div></div></div></div></div></div></div></div></div></div></div>