<div dir="ltr"><div dir="ltr"><div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">That is interesting. What happens if someone starts the generator manually and manually engages the transfer switch to the generator position? Will the inverter still detect it as a generator, or will that only happen if the 2-wire start is being called for?</div></div><div><div dir="ltr" class="gmail_signature"><div dir="ltr"><br>Jason Szumlanski<div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida State Certified Solar Contractor CVC56956</span></div><div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida Certified Electrical Contractor EC13013208</font></div></div></div></div><br></div><br><div class="gmail_quote gmail_quote_container"><div dir="ltr" class="gmail_attr">On Mon, Jul 7, 2025 at 4:07 PM Poole, Jharen via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div class="msg-5971354048754724763">
<div dir="ltr">
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
For a setup such as this, it is recommended that the generator is started using the inverter’s 2-wire start function rather than a manual startup. We also want to make sure that the grid signal, gen signal, and gen connected to grid input settings are enabled
on the inverter to ensure proper detection and operation. I wouldn’t recommend using this setup on a manual start with large generators rated 45kW or higher and are hospital grade. These tend to produce extremely clean power and can mistakenly be identified
as the utility grid, which can interfere with its ability to properly determine the source of the input and affect the system behavior.</div>
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
If you're using a typical residential generator with the recommended startup configuration, and the generator is called upon, the inverter will display a generator icon on the screen once it detects generator power (on the latest firmware). Although the “grid
sell” setting remains enabled, the inverter is programmed to prevent power from being exported back to the generator. During a grid outage, it will operate using generator power, and once utility power is restored and detected, the inverter will automatically
resume normal grid sell operations.</div>
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div id="m_-5971354048754724763Signature">
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Best Regards,<br>
<br>
Jharen Poole<br>
Applications Engineer II<br>
972-575-8875</div>
<div style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<img id="m_-5971354048754724763image_0" width="226" height="69" size="82287" style="width: 226px; height: 69px; max-width: 781px;" src="cid:ii_197e68ebc1a5e53039b1"></div>
</div>
<div id="m_-5971354048754724763appendonsend"></div>
<hr style="display:inline-block;width:98%">
<div id="m_-5971354048754724763divRplyFwdMsg">
<div style="direction:ltr;font-family:Calibri,sans-serif;font-size:11pt;color:rgb(0,0,0)">
<b>From:</b> RE-wrenches <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>> on behalf of Jay via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Sent:</b> Thursday, July 3, 2025 4:11 PM<br>
<b>To:</b> RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Cc:</b> Jay <<a href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a>><br>
<b>Subject:</b> Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)</div>
<div style="direction:ltr"> </div>
</div>
<table align="left" cellspacing="0" cellpadding="0" style="direction:ltr;width:100%;box-sizing:border-box;border-collapse:collapse;border-spacing:0px">
<tbody>
<tr>
<td style="direction:ltr;background-color:rgb(255,185,0);padding:5pt 2pt">
</td>
<td style="direction:ltr;background-color:rgb(255,248,229);padding:5pt 4pt 5pt 12pt;width:100%">
<div style="direction:ltr;color:rgb(34,34,34)"><b>Caution:</b> This email is from an external source.</div>
</td>
</tr>
</tbody>
</table>
<div style="direction:ltr"><br>
<br>
</div>
<div style="direction:ltr">Sounds like what they want the sol ark can’t do. </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">I think either the eg4 flexboss and MID or the AIO might work. </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<blockquote>
<div style="direction:ltr">On Jul 3, 2025, at 2:33 PM, Jason Szumlanski via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br>
<br>
</div>
</blockquote>
<blockquote>
<div style="direction:ltr"></div>
<div style="direction:ltr">That might be their recommendation, but it doesn't stop someone from manually starting the generator when the utility is down. Their wiring diagram leave a lot to be desired in terms of how program the system in this configuration.</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">Even if they strongly recommend that in webinars, it still isn't clear to me if Grid Sell is automatically disabled when the 2-wire start relay is closed. Honestly, I wouldn't trust the answer from a random tech support agent, especially
with various firmwares floating around.</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">This is just another example of poorly documented and ambiguous operational control that plagues all of the all-in-one inverters.</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
Jason Szumlanski</div>
<div style="direction:ltr"><span style="font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px;color:rgb(51,51,51)">Principal Solar Designer | Florida Solar Design Group</span><br>
<span style="font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px;color:rgb(51,51,51)">NABCEP Certified Solar Professional (PVIP)</span><br>
<span style="font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px;color:rgb(51,51,51)">Florida State Certified Solar Contractor CVC56956</span></div>
<div style="direction:ltr;font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;color:rgb(51,51,51)">
Florida Certified Electrical Contractor EC13013208</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">On Thu, Jul 3, 2025, 4:14 PM Lloyd Hoffstatter <<a href="mailto:lloyd@sunstruckconsulting.com" id="m_-5971354048754724763OWA98ecc6f3-506d-5110-6062-5391f5ea91f6" target="_blank">lloyd@sunstruckconsulting.com</a>> wrote:</div>
<blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left:1px solid rgb(204,204,204)">
<div style="direction:ltr;font-family:Aptos,Aptos_MSFontService,-apple-system,Roboto,Arial,Helvetica,sans-serif;font-size:12pt">
Sol-Ark strongly recommends only using a line side generator under inverter 2 wire control and with AC coupled inverters off, per several webinars. </div>
<div style="direction:ltr;font-family:Aptos,Aptos_MSFontService,-apple-system,Roboto,Arial,Helvetica,sans-serif;font-size:12pt">
Best regards,</div>
<div style="direction:ltr;font-family:Aptos,Aptos_MSFontService,-apple-system,Roboto,Arial,Helvetica,sans-serif;font-size:12pt">
Lloyd</div>
<div id="m_-5971354048754724763x_m_-1746362179148414471ms-outlook-mobile-body-separator-line" style="direction:ltr">
<br>
</div>
<div id="m_-5971354048754724763x_m_-1746362179148414471ms-outlook-mobile-signature">
<div style="direction:ltr">I’m lLlCOGet <a href="https://aka.ms/o0ukef" id="m_-5971354048754724763OWA0899fe18-7032-f5fd-7071-978eb59c26ba" target="_blank">
Outlook fo</a></div>
</div>
<hr style="direction:ltr;display:inline-block;width:98%">
<div id="m_-5971354048754724763x_m_-1746362179148414471divRplyFwdMsg">
<div style="direction:ltr;font-family:Calibri,sans-serif;font-size:11pt;color:rgb(0,0,0)">
<b>From:</b> RE-wrenches <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" id="m_-5971354048754724763OWA002b8f87-5196-04b8-bdf8-a8008740f784" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>> on behalf of Jason Szumlanski via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWAff2d2a8c-4670-2161-6f49-f88e96840cdd" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Sent:</b> Thursday, July 3, 2025 3:10:07 PM<br>
<b>To:</b> RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWA8d0469b9-47a8-ebde-cf34-b3531b7de39c" target="_blank">re-wrenches@lists.re-wrenches.org</a>><br>
<b>Cc:</b> Jason Szumlanski <<a href="mailto:jason@floridasolardesigngroup.com" id="m_-5971354048754724763OWAbde4606c-36cc-ddc4-8dc4-6b8387d63bb6" target="_blank">jason@floridasolardesigngroup.com</a>><br>
<b>Subject:</b> Re: [RE-wrenches] Sol-Ark 15K Gen on Grid Terminal (with GTBB)</div>
<div style="direction:ltr"> </div>
</div>
<div style="direction:ltr;font-family:arial,helvetica,sans-serif">This guy wants the smart load capability, too.</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
Jason</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">On Thu, Jul 3, 2025 at 8:42 AM Jay via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWA023f87fa-d619-1485-50ce-2d9547a738a5" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:</div>
<blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left:1px solid rgb(204,204,204)">
<div style="direction:ltr">It’s got generator input terminals. </div>
<div style="direction:ltr">Why not use them for the generator?</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<blockquote>
<div style="direction:ltr">On Jul 3, 2025, at 5:05 AM, Jason Szumlanski via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWA103e4e22-11f5-5fc7-1acd-594442e7a8d9" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br>
<br>
</div>
</blockquote>
<blockquote>
<div style="direction:ltr"></div>
<div style="direction:ltr">The attached wiring diagram from the manual shows both a generator and grid connected to the Sol-Ark Grid input with a transfer switch to select between grid and generator. </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">Question: If you program the inverter for GEN on Grid Input and allow Grid Sell, how would the inverter know what the input source is and prevent selling to the generator inadvertently?</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">I suppose if it is an automatic transfer switch and the two wire start is called for, the inverter might stop grid selling when calling for the generator (but I'm not sure if that's the case). In any case, that's not a failsafe
solution because the generator could be started and selected manually with the transfer switch and the inverter would not know it.</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">I have someone insisting that Sol-Ark supports this configuration with Grid Sell enabled. I can't imagine that is the case. At a minimum, it would be bad practice. </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">In my opinion, the interface should disallow Grid Sell altogether when GEN on Grid Input is selected. Maybe it's already doing that internally, but it isn't clear at all from the interface or the manual. </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">Of course, the Off-Grid section of the manual does tell you to not use the Grid Sell option.<br>
<br>
</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr">Jason Szumlanski </div>
<div style="direction:ltr">Florida Solar Design Group </div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><br>
</div>
<div style="direction:ltr"><Screenshot_20250703_063315_Drive.jpg></div>
<div style="direction:ltr">_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=4FvOSe4NGu37BU4qAvgNlANFr7FWsAOMt48UWtIQUPc&e=" id="m_-5971354048754724763OWAf75b040d-413f-4a22-0caa-1ab9445edd48" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWA6ecaba6f-138b-5ffa-787d-2e1ce87bad82" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_options.cgi_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=RHL10Csg2v-ABpYHW42RAqaKG3JoPnrTrYAquabj5_I&e=" id="m_-5971354048754724763OWA59027819-53af-7d10-9085-894a0ac171bd" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=https-3A__www.mail-2Darchive.com_re-2Dwrenches-40lists.re-2Dwrenches.org_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=3sMiwLKcN4gZazgTSadNd5GjkRjsabVhdoyuUjJCiL8&e=" id="m_-5971354048754724763OWA76ab0722-eea5-f62d-f569-14324b2f7739" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_pipermail_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=9u9k_VQwIOgUqWz14v2L7oIkkF5ScOkfEHJdqA9nJjU&e=" id="m_-5971354048754724763OWA2099680c-0aa2-2224-07bb-51831e79a671" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.re-2Dwrenches.org_etiquette.htm&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=_vhuVccTkS2riSys1DxXCw9M4L-3JYGPePRQp3rKzqQ&e=" id="m_-5971354048754724763OWAad7b35a3-2086-f02b-8f8a-0cd7ff715250" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.members.re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=UJIuL9RzbWJzjFwJgJEsVDzW7q8ur9_-cGCeQQDu9bQ&e=" id="m_-5971354048754724763OWA861b5f6e-8ab3-7ceb-661c-45f8868247aa" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div>
</blockquote>
<div style="direction:ltr">_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=4FvOSe4NGu37BU4qAvgNlANFr7FWsAOMt48UWtIQUPc&e=" id="m_-5971354048754724763OWAae495bf8-101d-c11f-f848-d0ce8bac2d59" target="_blank">
http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" id="m_-5971354048754724763OWAb0a6327d-d3d8-9e75-e694-ea62c7df4d16" target="_blank">
RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_options.cgi_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=RHL10Csg2v-ABpYHW42RAqaKG3JoPnrTrYAquabj5_I&e=" id="m_-5971354048754724763OWA5119995e-4739-5bbf-ba52-c086d0616e2a" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=https-3A__www.mail-2Darchive.com_re-2Dwrenches-40lists.re-2Dwrenches.org_&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=3sMiwLKcN4gZazgTSadNd5GjkRjsabVhdoyuUjJCiL8&e=" id="m_-5971354048754724763OWA9e416d37-9983-f919-44cb-48e470302abb" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.re-2Dwrenches.org_pipermail_re-2Dwrenches-2Dre-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=9u9k_VQwIOgUqWz14v2L7oIkkF5ScOkfEHJdqA9nJjU&e=" id="m_-5971354048754724763OWAc9ccb6fc-21e0-5611-b1ab-b50798ad18a6" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.re-2Dwrenches.org_etiquette.htm&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=_vhuVccTkS2riSys1DxXCw9M4L-3JYGPePRQp3rKzqQ&e=" id="m_-5971354048754724763OWA65652443-ffe7-abeb-f288-76f79c426513" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="https://urldefense.proofpoint.com/v2/url?u=http-3A__www.members.re-2Dwrenches.org&d=DwMFaQ&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=p2tHyHEAjVe2zSh4C_236V4KkHnn0z0ynUvWz0mobds&m=mxfPWzvsNzBC4eZdAQ-FGEQj_G8-9tjDnnh0oMPtW91EDTfwSm3KFOL8ZoelkNoJ&s=UJIuL9RzbWJzjFwJgJEsVDzW7q8ur9_-cGCeQQDu9bQ&e=" id="m_-5971354048754724763OWAfc557352-92f9-ee7b-506f-b90d144e961e" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div>
</blockquote>
</blockquote>
<div style="direction:ltr">_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div>
</blockquote>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div></blockquote></div></div>