    <p>I second the idea of just backing up one of the 200 A panels, and
      moving critical loads there.  The trouble I've seen with total
      backup, is that the customers are not even aware that the grid
      went down, and make no effort to curtail their usage.  Then, once
      the batteries are down, they are truly off line.  I've had
      customers even compliment our choice of circuits; they knew the
      power was out because certain things went off, but still had a
      very usable home. Also, on larger homes there are all sorts of
      loads like steam showers, etc. that really don't need to be on,
      but will drain the batteries quickly in an outage.  <br>
    </p>
    <p>Finally, unless power outages are common, a GTB system can make
      the power less reliable, not better.  I quit doing them, unless
      folks had numerous outages, like in Puerto Rico.<br>
    </p>
    <p>Ray Walters<br>
      Remote Solar<br>
    </p>
    <div class="moz-cite-prefix">On 6/29/2025 12:35 PM, Jason Szumlanski
      via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAE438R-rVFo8TuiJr6RY6oEevuerEZwP+WNDGodz007ewJg4sw@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div dir="ltr">
          <div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif">If you can
              actually run the whole house on two Sol-Ark 15K (100A
              combined output), realistically, they probably don't need
              400A service. Have you done a load calc on the home? We
              see lots of 400A services where they could have "gotten
              away" with a 200A service. </div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif"><br>
            </div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif">In these
              cases, I always encourage the homeowner to just back up
              one of the two 200A panels and move all critical loads to
              that panel. If you need more spaces, add a subpanel. If
              they have 400A service but only need 200A service
              and demand truly whole-house backup, simply disconnect one
              of the panels from the utility and instead feed it from
              the backed up 200A panel as a subpanel. There's nothing
              that says you can't have a 400A meter feeding a 200A main
              panel protected by a 200A main breaker, and use the other
              one as a subpanel, as long as the load calcs work out. You
              will just have to separate neutrals and grounds and remove
              the bonding jumper. Depending on the panel brand, you can
              usually get a 200A breaker or feed-through kit that takes
              up four spaces. </div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif"><br>
            </div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif">Even if the
              load calc for the home comes back over 200A, you can
              probably easily get the backup panel under 200A of
              calculated loads and just back that up. It makes no sense
              to try to back up a whole home that needs over 200A
              service unless you are installing a massive system, which
              would be more than two Sol-Arks can handle. We encourage
              people to choose non-critical loads to leave out, like
              electric dryers, pool heaters, pool pumps (although this
              is nice to have on a smart load), EV chargers, electric
              ranges and cooktops, outdoor kitchens, hot tubs, electric
              saunas, etc. This should easily get the backup panel under
              200A. If you present it as a value engineering option,
              it's relatively easy to get people to move away from their
              "whole home or nothing" mentality.</div>
            <br clear="all">
          </div>
          <div>
            <div class="gmail_default"
              style="font-family:arial,helvetica,sans-serif">With that
              said, if I am truly backing up a 400A service here in
              Florida, I'm installing at least four 15K inverters, 35kW
              of PV, and 120 kWh of battery capacity. And I'm
              still dumping EV chargers and pool heaters during
              a utility outage. I would put a 400A main service
              disconnect ahead of the inverters and install a 400A DPDT
              transfer switch for bypass purposes. Auxiliary generator
              input goes directly to the Sol-Arks, unless the owner
              wants to spring for another DPDT transfer switch to send
              generator power directly to the house in the event of grid
              and inverter failure.</div>
            <br>
          </div>
          <div>
            <div dir="ltr" class="gmail_signature">
              <div dir="ltr"><br>
                Jason Szumlanski
                <div><span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal
                    Solar Designer | Florida Solar Design Group</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                  <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP
                    Certified Solar Professional (PVIP)</span><br
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">
                  <span
style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida
                    State Certified Solar Contractor CVC56956</span></div>
                <div><font color="#333333"
face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida
                    Certified Electrical Contractor EC13013208</font></div>
              </div>
            </div>
          </div>
          <br>
        </div>
        <br>
        <div class="gmail_quote gmail_quote_container">
          <div dir="ltr" class="gmail_attr">On Fri, Jun 27, 2025 at
            3:06 PM scot.arey--- via RE-wrenches <<a
              href="mailto:re-wrenches@lists.re-wrenches.org"
              moz-do-not-send="true" class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>>
            wrote:<br>
          </div>
          <blockquote class="gmail_quote"
style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
            <div class="msg-1349004728057898872">
              <div dir="ltr">
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  Seeking your feedback and best practices.</div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  We have a existing customer who wants to add ESS for
                  whole house backup. He has a 400-amp meter box with
                  two 200-amp panels on each side of the meter can. We
                  want to use Sol-Ark and HomeGrid which is our go-to
                  solution. Today, we have two 10KW ground mounts
                  feeding a grid-tied system with Fronius inverters
                  aggregated at the array with single set of conductors
                  back to the house and meter</div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  Option 1: Add a SolArk 15KW and HomeGrid '4-stack' per
                  each 200-amp panel and in essence have two separate
                  systems each backing up their own panelboard. Seems
                  easy but I know the panels are not totally balanced
                  and this seems like I'm having excess capacity at the
                  panel that powers circuits to run less than all the
                  time.</div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  Brings me to option 2:</div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  Install two <span style="font-size:16px">paralleled </span>SolArks
                  with two batteries again (and now a battery combiner)
                  and add a 400-amp transfer switch and take grid output
                  from meter and bring to ATS first. The GEN inputs on
                  ATS will be fed by aggregated LOAD outputs of the
                  SolArks so if grid fails, the ATS "sees" 240V and
                  transfers to the inverters only  and opens circuit to
                  grid. When grid power is there, all is grid-tied and
                  bi-directional. I've done similar setup with Outback
                  Radian and ASCO 200A ATS for whole house backup.</div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  But this seems really complicated with lots of extra
                  boxes. </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  <br>
                </div>
                <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                  Take the simple-easy route even if one inverter is a
                  bit too much for one of the 200-amp panels? Ot
                  aggregate and use ATS so we can put two SolArks to
                  work together to address full load as one operating
                  output? Wall space for this is pretty good for both
                  options.</div>
                <div id="m_-1349004728057898872Signature">
                  <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                    <br>
                  </div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    <b>Howard "Scot" Arey</b></div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    <b>Owner, Solar CenTex</b></div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    <br>
                  </div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    NABCEP PV Installation Professional</div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    TECL 29755</div>
                  <div
style="direction:ltr;text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-size:15px;color:rgb(36,36,36)">
                    254-300-1228 </div>
                  <div
style="text-align:left;text-indent:0px;background-color:rgb(255,255,255);margin:0px;font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                    <img id="m_-1349004728057898872x_image_0"
                      width="105" height="105"
style="width: 105px; height: 105px; max-width: 722px; min-width: auto; min-height: auto; margin: 0px;"
                      src="cid:part1.pnmLfXDY.BwO7579I@solarray.com"
                      class=""></div>
                  <div
style="font-family:Aptos,Aptos_EmbeddedFont,Aptos_MSFontService,Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
                    <br>
                  </div>
                </div>
              </div>
              _______________________________________________<br>
              List sponsored by Redwood Alliance<br>
              <br>
              Pay optional member dues here: <a
                href="http://re-wrenches.org" rel="noreferrer"
                target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
              <br>
              List Address: <a
                href="mailto:RE-wrenches@lists.re-wrenches.org"
                target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Change listserver email address & settings:<br>
              <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                rel="noreferrer" target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              There are two list archives for searching. When one
              doesn't work, try the other:<br>
              <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                rel="noreferrer" target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
              <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                rel="noreferrer" target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
              <br>
              List rules & etiquette:<br>
              <a href="http://www.re-wrenches.org/etiquette.htm"
                rel="noreferrer" target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out or update participant bios:<br>
              <a href="http://www.members.re-wrenches.org"
                rel="noreferrer" target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
              <br>
            </div>
          </blockquote>
        </div>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>