<div dir="ltr"><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif">Now that I have a single inverter installation and a triple inverter installation under my belt, I'm ready to share my first impressions. Here they are in no particular order. Both systems were in off-grid settings with backup generators connected to the generator smart input. The single inverter is paired with Pytes batteries in closed loop. The second has Lithionics batteries using voltages only.</span><br clear="all"></div><div><br></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif">I hope this information and some of these tips are helpful to others.</span></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></span></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif">The monitoring system is seriously underwhelming. I was shocked to find out that you can only view each inverter in a system individually. You can't see the total plant solar production or consumption. This makes data gathering pretty useless with this inverter system for multi-inverter installations. Even with single inverter installations, the data is not very robust. And there is no download option (unless you want a picture of a chart, which has very limited utility). On a good note, the programming interface in the app is speedy and fairly intuitive. There is no way to resend login information to the system owner. You can't have multiple logins for people to view the system. The owner has to share their credentials if multiple people want to view data. I know this is all in development, but I feel much of this should have been in place before this product was launched, especially the combined inverter data. "Use Solar Assistant" is not an acceptable workaround for me. I don't need more devices out there to manage. That is the whole appeal of an AIO.<br><br>I have had issues with connecting all four inverters installed to date to WiFi. They will not work with networks with no password (which Starlink can often be in remote settings). They only play with 2.4 GHz. On my Samsung Galaxy Fold 5, you can't see some information on the connections screen when the phone is open, and you cannot see other information when the screen is closed. I had issues with this device, but also tried with a new iPhone, and it still didn't work. Setting up WiFi immediately after a Factory Reset seemed to work, so maybe that is a best practice.<br><br>The inverters do strange things at times when "reconnecting" after an off/on cycle, even in an off-grid scenario. Sometimes when you switch a paralleled inverter on, it will start counting down from 900, although it will turn on when the others turn on.<br><br>Some settings are unclear and not well-documented, if at all. For example, with parallel inverters, you can set a maximum generator input power, which is then propagated to all inverters. But when I set the maximum charge from the generator, it did not seem to propagate that setting, so I changed it manually on each inverter. Maybe this is by design, since you might want to limit charging from the generator on an inverter that has heavy smart loads. I'm just speculating here. I'm still not clear on whether these settings are system-level or per inverter. I have not had enough time to play with the settings and test it out.<br><br>I had to factory reset inverters in a triple inverter setup when they simply would not turn on, even when taking them out of parallel mode. This might have been due to out of date firmware, which seemed to resolve this issue. <br><br>The firmware update process performed remotely from Midnite was pretty quick and painless. It factory reset the inverters, but reprogramming goes pretty quickly once you get accustomed to the interface.</span></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></span></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif">For some strange reason, in the single inverter system, the smart load output did not energize immediately as expected. It came on suddenly after at least 30 minutes with no explanation why. <br><br>The app persistently throws an error message that says Generator Abnormal when the generator is off in a off-grid system, even if the generator is supposed to be off.<br><br>The app has no options for alerts of any kind (push/text/email).<br><br>There is a real lack of battery integration information out there. Midnite doesn't seem compelled to put out integration guides or offer up much support in this area, understandably because they would want to promote their own batteries. To be fair, Sol-Ark only provides information for battery manufacturers that have partnered with them to establish reliable closed loop comms. When the AIO inverter(s) do "talk" to the battery, there is no obvious indication that closed loop communications have been established. There is no information screen or tab that displays battery information received through the communication bus.<br><br>The AC wiring is easy and obvious. I really like the simplicity. However, do the AC connections AFTER the AC connections if you want to keep swearing to a minimum. For the individual PV strings, it is hard to read the +/- inputs, and they are hard to see in an awkward location in the enclosure. The order of the battery connections from left to right is +/-. However, the individual PV string inputs are ordered -/+. The combination of these issues makes the PV connections difficult and borderline dangerous. Fortunately, there are test probe holes for each input. Sadly, they are so close together that it is not easy to ensure you have the right one, and it is difficult to get larger probes into them side by side. The parallel communication wiring terminals should be illegal. They are ridiculously hard to get wires into. The terminal block should be removable at a minimum.<br><br>The plastic bushings supplied are too large for my 2" punch kit. The bushings fit through the AIO openings, but not the wiring trough knockouts I made. I had to use chase nipples instead. The 1-1/4" bushings worked fine with my knockouts.<br><br>The battery torroids are too small. I had to wrestle with getting two 4/0 cables through the torroid with MagnaLugs, which are a bit thicker than other brands. If you have the option to install lugs after pushing the cables through the torroid, do that.<br><br>Pro Tip: Install the WiFi dongles before you set your inverters on a wiring trough, especially if you don't have a stubby Phillips screwdriver handy. You will thank me later.<br><br>Bonus Tip: Don't try to bring the battery cables into the enclosure through any knockout other than the leftmost pre-knocked-out opening.<br><br></span></div><div><span class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></span></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><br>Jason Szumlanski<div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida State Certified Solar Contractor CVC56956</span></div><div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida Certified Electrical Contractor EC13013208</font></div></div></div></div><div dir="ltr"><div><br></div><div><br></div><div><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"></div></div></div></div>