<div dir="ltr"><div><div>Hi all,</div><div>     I need some help with a generator overvoltage troubleshoot.  I'm working on an outback offgrid system that consists of 2 x Radian GS8048a, 1 x MATE3S controller, 1 x FM 80 charge controller, 1 x 55kw single phase propane AC cummins generator, about 4kw of solar *not sufficient enough to keep up with the load, and 24 x 4v Rolls batteries series/paralleled to make 48v.  The generator was rebuilt and the batteries replaced about a year ago and since then, the generator has been faulting due to overvoltage.  I had help and first found that the MATE needed calibrating so that was done, but the generator still was faulting.  I found changing the AC Input Charging from 30a to 20a seemed to work.  I put a power monitor on the generator output and found that, with the AC Input Charging set at 30a, noticed that there was a voltage spike up to 300+V at about a 70a draw.  The generator company put a load bank on and verified the generator may not be at fault and the problem is after the generator.  Has anyone encountered a problem like this and have suggestions?  I've attached a PDF with a timeline of what I've done for troubleshooting so far.</div></div><div><br></div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr">Jim with Gowdy Electric<div>Cambria, Ca 93428</div><div>business  805 927 2630</div><div>cell  805 975 5279</div></div></div></div>