    Hi Mark,<br>
    <br>
    One thing to be aware of is capacitance inrush current, quite common
    with DC-DC converters.<br>
    If you are running the converters off of the Prostar controller load
    circuit, the inrush current might<br>
    be sufficient to trigger a high current shutdown of the load
    circuit.<br>
    <br>
    A single low current converter will probably be fine, especially if
    using the 30 amp Prostar.<br>
    <br>
    If you do decide to use the Tristar and go with a 48 volt
    configuration, 2 converters will not<br>
    be an issue because the Tristar has no load circuit, your loads will
    be powered off of the battery.<br>
    <br>
    I'll put my installer hat back on here and say that I always prefer
    the least complex solution.<br>
    The 24 volt configuration with the single converter would be that
    solution and also provide LVD.<br>
     <br>
    <pre class="moz-signature" cols="72">Roy Butler
Morningstar Technical Support

                
</pre>
    <div class="moz-cite-prefix">On 12/19/2024 9:51 AM, Mark Frye via
      RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:DM8P220MB04872E57583573506AC11D55B1062@DM8P220MB0487.NAMP220.PROD.OUTLOOK.COM">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator"
        content="Microsoft Word 15 (filtered medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri",sans-serif;
        color:windowtext;}.MsoChpDefault
        {mso-style-type:export-only;
        mso-ligatures:none;}div.WordSection1
        {page:WordSection1;}</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal">My equipment has both 12 V and 24 V each at
          about 60W.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I was planning to run a Prostar at 24V and
          then use a DC DC converter for the 12 V load.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">That looked like 2 x 285 AH AGM and 2x 320
          W PV.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Now I have to go to a darker place and may
          have to double the battery and the PV.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">That would mean I could run a Tristar at
          48V and have a two DC DC converters, one for the 24V loads and
          one for the 12V loads.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Somehow it makes sense to me to run the
          supply side at 48V for lower currents and more battery cells
          even if it means an additional converter on the load side.<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Any thoughts one way or the other?<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Thanks,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Mark Frye <o:p></o:p></p>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>