<p>Just goes to my rule for off grid, forget the comms. Regardless
of the Manu, I've been advised during trouble shooting to
disconnect the comms, and it almost always fixes the problem.
Honestly, I forgot what comms were supposed to fix in the first
place. I almost never even bother now. Mate 3 with HUB? Only if I
have to. Midnite "Follow Me"? pulled the cables. All my systems
are open communication. Even battery to battery comms causes
problems. <br>
</p>
<p>Oh, and I recently had to buy a $400 PC laptop, just to do
trouble shooting, and firmware updates on batteries. I don't miss
the acid burns in my jeans, but I'm not sure if I like my job as
much, in the twilight years of my off grid career. I'm spending
as much time installing, as I am babysitting LiPO4 batteries that
are supposed to operate maintenance free for 8000 cycles. Yeah.
Just yeah. I'd be amazed at 800 cycles without having to truck
out there to F with them. Haven't seen a brand yet that has
worked without some kind of trouble. Blue Ion, Simpliphi,
Fortress, Homegrid, EG4..... major trouble with everyone of them.
Complete system shutdowns. Rotting food in the fridge.<br>
</p>
<p>I've heard acid burned jeans are coming back in fashion.....</p>
<p>Ray Walters<br>
Remote Solar<br>
</p>
<div class="moz-cite-prefix">On 11/8/2024 1:42 PM, Chris Sparadeo
via RE-wrenches wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CAAdbmLYH2b5amFjV_qDv951Z7-wjtDhZPGyY9jJ5PiMADQd8-Q@mail.gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
Hey wrenchers,
<div dir="auto"><br>
</div>
<div dir="auto">I have an off-grid customer with a pair of VFX
3648 inverters, a FM 100 charge controller and two eVault
classics in open loop. The issue is when the generator is
charging the batteries, incoming amperage is all over the place
and periodically, gradually drops to 0A then ramps back up. This
is creating really long generator run times. When I turn off PV
input, same results. When I turn off both PV input and charge
controller output (turning off the CC entirely) the inverters
hold a steady charge. If I remove the charge controllers comms
cable from the hub, they both play nicely and charge
cooperatively. This obviously sounds like a communication issue,
but unfortunately, without the help of OB tech support, I am
left speculating. I have checked all settings with a fine comb
and nothing looks to be out of place. Has anyone experienced
something similar to this?<br clear="all">
<br>
Thanks! </div>
<div dir="auto"><br clear="all">
<div dir="auto">
<div dir="ltr" class="gmail_signature"
data-smartmail="gmail_signature">
<div dir="ltr">
<div dir="ltr">
<div dir="ltr">
<div>Chris Sparadeo</div>
<div><br>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="moz-mime-attachment-header"></fieldset>
<pre wrap="" class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>
</pre>
</blockquote>
</body>
</html>