<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div dir="ltr"></div><div dir="ltr">Hi Jeremy</div><div dir="ltr"><br></div><div dir="ltr">There are two issues I think. </div><div dir="ltr"><br></div><div dir="ltr">1 is that the inverter won’t connect. </div><div dir="ltr">And I don’t have an answer why the inverter won’t in sell mode but will in gen mode. Maybe the generator is slightly out of the more narrow window for grid. I presume you’ve checked hz and volts and they are in spec for grid?  I know sometimes the frequency control can be slightly variable without a load. I’ve had success in the past getting inverters to connect to a generator with putting some dumb loads on it. Like incandescent lights or small heater. </div><div dir="ltr"><br></div><div dir="ltr">2. Maybe it’s a good thing it won’t because if it did connect wouldn’t it be possible for the inverter to try to sell to the generator?  If you didn’t have to change grid to Gen?</div><div dir="ltr"><br></div><div dir="ltr">Jay</div><div dir="ltr"><br><blockquote type="cite">On Oct 23, 2024, at 8:47 PM, Jeremy Rodriguez via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">

<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">



<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Wrenches, </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
We have a client that has brought utility power in and we now have the system hooked up to the utility.</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
In setting the system up, I've experienced that the inverter will sell and function fine with all the settings set up as<b> Grid Tied</b> mode, but it does not play nice when the grid is gone , and the Generator is brought in as the AC source.</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
We have installed an external transfer switch to switch the inverters' AC input, from either the utility or the existing backup generator ( if the grid fails), automatically. </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
The manual states that the inverter's two input selections can be programmed for seperate input modes, via the<b> Input</b>
<b>Type</b> menu. Ive not been able to get this accomplished. </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
When simulating a grid outage, thus changing the AC input to the inverter being from the Generator, the inverter will not synch to the AC power to charge the batteries. </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
The only way that I can get the inverter to synch, is to switch the input mode to
<b>GEN</b> from <b>GRID.</b></div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
This is not ideal since the client would need to be present to make the button push, even though the generator will be started automatically if the grid were to go down (hopefully) , just as it did before.</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
 </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
With no way to contact Outback , can someone advise how to properly program the inverter/ MATE3S for this project?   </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Equipment onsite:</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Single VFXR3648 inverter</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Two FM60 CCs</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Hub4</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
MATE3S</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
ATS with Dual Relays 50A </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
L.A. Battery bank</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Here's how we would like it to work:</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Utility power ON: </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Sell excess power once the batteries have gone through the Absorb cycle. Batteries remain full in case of a utility failure. </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Utility Outage: </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
ATS now feeds Inv AC input via Generator if needed.</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Inverter runs the home as it did , off grid.</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
If the battery voltage drops and the AGS is engaged, the inverter will use that input to charge the batteries as usual.  If the grid comes back on and the gen is running, the generator can still run, with no connection to the inverter.  With the grid now charging
 the battery bank, and the AGS will enventually shut off the Gen. Based on voltage.  </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Contact me off list if necessary</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Jeremy Rodriguez</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
All Solar Inc. </div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Penrose, CO</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
719-276-4954</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>


<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address & settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules & etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></body></html>