<div dir="ltr"><div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">I absolutely have a 400A bypass switch here. In fact, there is also a 200A DPDT switch that allows you to select between two generators!</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">If someone was able to be there during or after the storm, we could have gotten the power back on, for sure. I think the inverters would even pass through power without flipping the switch. I was apprehensive to use the Gen Force function remotely with nobody there, especially because I might not be able to turn it off if connectivity is lost.</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">Tomorrow will probably be our earliest possibility of getting out there, but there is a lot of debris in the water, so it's risky.</div><div><div dir="ltr" class="gmail_signature"><div dir="ltr"><br>Jason Szumlanski<div><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Principal Solar Designer | Florida Solar Design Group</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">NABCEP Certified Solar Professional (PVIP)</span><br style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px"><span style="color:rgb(51,51,51);font-family:Roboto,RobotoDraft,Helvetica,Arial,sans-serif;font-size:13px">Florida State Certified Solar Contractor CVC56956</span></div><div><font color="#333333" face="Roboto, RobotoDraft, Helvetica, Arial, sans-serif">Florida Certified Electrical Contractor EC13013208</font></div></div></div></div><br></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Oct 10, 2024 at 5:35 PM Dave Tedeyan via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto">Yikes! I cannot speak to the AIO's in general. <div dir="auto">However, I do still always install some sort of inverter bypass in battery based systems. Then in case of a failure like this you can at least continue to power the house off the generator as long as someone is there to throw the switch.</div><div dir="auto"><div dir="auto"><br></div><div dir="auto">Cheers,</div><div dir="auto">Dave</div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Thu, Oct 10, 2024, 4:58 PM Jason Szumlanski via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div style="font-family:arial,helvetica,sans-serif">We have been talking a lot recently about all-in-ones. I just had a massive fail during Hurricane Milton with a quad Sol-Ark 15K off-grid system that deserves some discussion about whether AIO is a good idea if it can't build in some resilience to errors. I'm not sure if the new Midnite unit is better in this respect, but this is what happened to the Sol-Ark system...</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif">Four inverters, each with 4 strings of PV paralleled to 2 MPPT per inverter. One of the slave units developed some sort of PV DC fault during the storm. This caused the slave inverter to shut down and throw an error, which in turn caused a parallel fault across all four inverters. Power output ceases at that point. Apparently the system keeps resetting because I have a cell modem that uploads data to Sol-Ark, but that cell modem is powered by the inverter outputs, so it must be getting power at least intermittently. The rest of the loads are basically flatlined according to the Sol-Ark data. It's mostly air conditioners, so they probably can't turn on fast enough before the PV fault causes another shutdown.</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif">So, in essence, one of 16 strings of PV develops a fault, and that causes all four inverters to malfunction? What is the point of redundancy if a fault of one results in a fault of all?! If there is a true PV input fault, shouldn't that just shut down that MPPT, or perhaps all of the PV DC input to that inverter? And why can't this inverter continue to invert power from the batteries and charge from a generator when there is a DC input fault that could be programmatically isolated and ignored?</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif">This is a bad design in my opinion, and something I hadn't considered. If the faulted inverter can't function with a DC input fault, it should just take itself out of the game. (This is 120/240 split phase, BTW). Is this how all AIO inverters work? One inverter fault on the DC side kills all paralleled units' AC output? Not good.</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif">This is a completely off-grid system on a remote island with no vehicle access, so it's not exactly easy to do a "truck roll" on this one, especially post-hurricane. To make matters worse, the generator was running at the time of the fault, as it was being signaled to run because the battery had reached the assigned charge voltage. The fault also killed the 2-wire start signal from the master, so the system also stopped passing through generator power to the loads. The house is dark.</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif"><br></div><div style="font-family:arial,helvetica,sans-serif">Jason Szumlanski</div><div style="font-family:arial,helvetica,sans-serif">Florida Solar Design Group</div><div style="font-family:arial,helvetica,sans-serif"><br></div><div><div dir="ltr" class="gmail_signature"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b></b></div></div></div></div></div></div></div></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div>