<div dir="auto">Out of curiosity, what battery form factor i.e. FLA, Lithium and manufacturer are your OB inverters running on?<div dir="auto"><br></div><div dir="auto">Christopher</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Sep 30, 2024, 19:52 Wayne Irwin via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div dir="ltr">
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Hurricane Helene has taught us the hard way that Enphase batteries with anything other than IQ8's won't restart.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
The issue is that when the batteries try to restart (at the non-programmable time of 9:AM) if there are any significant loads, the batteries will not stay on long enough (300+ seconds) for any non-IQ8 micros to energize. The battery will attempt multiple times,
but if there is a load, (such as a well pump) the draw from the load will essentially prohibit the batteries from energizing the micros long enough to engage and produce. The only solution is to have a load controller or turn off all loads once the power goes
out. Otherwise, during these "attempts to turn on" power in the house will momentarily turn on and back off and potentially drain the batteries down to lower than the point of which they can even attempt to restart. I spoke at length with Enphase upper engineering
(not tech support) about this today. They now know that most of the tech support staff does not know this important information. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
Once the batteries are dead, they are very difficult if not impossible to jump start with a generator. At the recommendation of tech support we tried multiple times with the "approved" inverter generator which ultimatly just wasted our time. Even though the
controller/switch will accept the gen power and pass the energy to the loads, it will not energize the combiner or batteries. If your goal is to have an autonomous system with Enphase, it's only going to happen with the IQ8's (at this point).</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
This is a significant issue with retrofitting older systems. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
By the way:</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
- We've received numerous desperate calls from (orphaned) Powerwall owners whose systems also won't turn back on. </div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
- ALL of our Outback systems were issue free.</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
I hope this helps some of you. Good Luck out there!</div>
<div style="font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
<div id="m_5729517380481300664Signature">
<div style="direction:ltr;font-size:12pt"><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">Wayne Irwin</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">President</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">License #CVC56695</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">State Licensed Solar Contractor</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:calibri,helvetica,sans-serif;color:rgb(6,64,12);background-color:rgba(0,0,0,0);line-height:normal">Pure Energy Solar</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)"> International
Inc.</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">Wayne@PureEnergySolar.com</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<a href="http://pureenergysolar.com/" id="m_5729517380481300664OWA447103e2-20dc-453e-b1f2-8c87350fa4cf" title="http://pureenergysolar.com/" target="_blank" rel="noreferrer">PureEnergySolar.com</a><br>
<a href="http://solarchargingstation.com/" id="m_5729517380481300664OWA474bd1c8-194e-e2f6-b0bb-14bbad4133e1" title="http://solarchargingstation.com/" target="_blank" rel="noreferrer">SolarChargingStation.com</a><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">352 377-6527 Office</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">352 336-3299 Fax</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<br>
<br>
</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(6,64,12)">The Sun Is Always Shining!</span><span style="font-family:Calibri,Helvetica,sans-serif;color:rgb(0,0,0)"><br>
<br>
The content of this message is Pure Energy Solar Confidential. If you are not the intended recipient and have received this message in error, any use or distribution is prohibited. Please notify me immediately by reply e-mail and delete this message from your
computer system. Thank you.</span></div>
<div style="direction:ltr;font-family:Calibri,Helvetica,sans-serif;font-size:12pt;color:rgb(0,0,0)">
<br>
</div>
</div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>