    <p>I've gotten word back from Fortress on this issue.  Here's what
      they said:</p>
    <p><i>The problems you were describing align with an issue in the
        earlier eVault Max batteries that we call "ghosting." Batteries
        with this issue would turn off like you described when being
        idle or taking very little current, for an extended amount of
        time.   A firmware update should resolve this issue.</i></p>
    <p>Thought you all should know.  I'll keep you updated on how the
      firmware update goes.</p>
    <p>Thanks,</p>
    <p>Ray Walters<br>
      Remote Solar<br>
    </p>
    <div class="moz-cite-prefix">On 8/27/2024 4:20 PM, Ray Walters via
      RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:424fd157-7f1b-4b9f-b166-bee47e929980@solarray.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>I have both controllers set to the Fortress recommended absorb
        settings of 54.4 vdc for 2 hrs.  Its always possible that there
        was voltage over swing or something.  I did check that the
        voltage on the controllers was within a0.1 vdc of the battery
        voltage at the Fortresses. I'm now using a pair of Midnite
        Hampton Bay Controllers.  They're rated to 90 amps, but I set
        them down to 85 A output, just to provide some head room.  I
        don't mind the very occasional clipping.  The array is two
        strings of Jinko 425s, 10 per series string, so 4250 w per
        controller. <br>
      </p>
      <p>I wonder if the voltage that causes trouble for Fortress might
        have changed due to the possible lightning surge?<br>
      </p>
      <p>Ray<br>
      </p>
      <div class="moz-cite-prefix">On 8/27/2024 3:46 PM, jay wrote:<br>
      </div>
      <blockquote type="cite"
        cite="mid:8874459D-456F-4B57-AD14-281425B0530E@gmail.com">
        <meta http-equiv="Content-Type"
          content="text/html; charset=UTF-8">
        I have a buddy in tech support at Fortress.
        <div class=""><br class="">
        </div>
        <div class="">I asked him and he said that elevated absorb volts
          above 55.2 could cause this situation.  </div>
        <div class="">And then the power cycle would reboot the BMS.</div>
        <div class=""><br class="">
        </div>
        <div class="">I am presuming its open loop, and the fact you
          mentioned that there was more PV and then the shut down sure
          might be connected.  </div>
        <div class="">You might check the charge voltages/time to make
          sure they are correct and I can’t remember if the classic has
          battery sense wire connections. </div>
        <div class=""><br class="">
        </div>
        <div class="">jay</div>
        <div class=""><br class="">
        </div>
        <div class=""><br class="">
        </div>
        <div class=""><br class="">
        </div>
        <div class=""><br class="">
        </div>
        <div class=""><br class="">
        </div>
        <div class=""><br class="">
          <div><br class="">
            <blockquote type="cite" class="">
              <div class="">On Aug 27, 2024, at 2:51 PM, Ray Walters via
                RE-wrenches <<a
                  href="mailto:re-wrenches@lists.re-wrenches.org"
                  class="moz-txt-link-freetext" moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>>
                wrote:</div>
              <br class="Apple-interchange-newline">
              <div class="">
                <meta http-equiv="Content-Type"
                  content="text/html; charset=UTF-8" class="">
                <div class="">
                  <p class="">The SPD was on one of the PV inputs before
                    it came into the house.  There were two Classics,
                    each fed with its own PV input and SPD.  It actually
                    caused an underground splice to fail (high
                    resistance) which I replaced the splice and restored
                    full voltage, and both Classics were working fine. 
                    Just seems unlikely ( but not impossible) that the
                    surge would make it past the Classic without damage,
                    but then damage the Fortress BMS in an otherwise
                    imperceptible manner.   That is our current best
                    theory at the moment though.   I added an SPD on the
                    48 v buss, before this latest total shutdown.    <br
                      class="">
                  </p>
                  <p class="">Ray Walters<br class="">
                  </p>
                  <div class="moz-cite-prefix">On 8/27/2024 2:35 PM,
                    Dave Angelini Offgrid Solar via RE-wrenches wrote:<br
                      class="">
                  </div>
                  <blockquote type="cite"
                    cite="mid:73b67fe1b3d521cc295be424ab132127@sti.net"
                    class="">
                    <meta http-equiv="Content-Type"
                      content="text/html; charset=UTF-8" class="">
                    <div id="signature" class="">When I have had someone
                      lose an SPD (I assume it was on DC buss) there is
                      often latent damage (shows up later) to many of
                      the devices.  In a Hi Rel mode, it is recommended
                      to replace it all. Most offgrid is not that
                      critical but try telling that to someone with
                      rotten food.</div>
                    <div class=""> </div>
                    <div class="">The freezers and reefers are often
                      full of spoils that smells never go away. YUK !<br
                        class="">
                      <pre class=""> </pre>
                      <pre class=""><strong class=""><span
                      style="font-size: small;" class="">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" rel="noopener"
                      moz-do-not-send="true" class="">  </a><a
style="color: blue; font-size: 11px; font-family: 'Lucida Grande', Verdana, Arial, Helvetica, sans-serif; font-weight: 400; background-color: #ffffff;"
                      href="https://offgridsolar1.com/"
                      rel="noopener noreferrer" moz-do-not-send="true"
                      class=""><span style="font-size: 12pt;" class="">https://offgridsolar1.com/</span></a><a
                      href="http://members.sti.net/offgridsolar/"
                      rel="noopener" moz-do-not-send="true" class=""> </a>
e-mail  <a href="mailto:offgridsolar@sti.net" moz-do-not-send="true"
                      class="moz-txt-link-freetext">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
                    </div>
                    <p class=""><br class="">
                    </p>
                    <p id="reply-intro" class="">On 2024-08-27 1:02 pm,
                      Ray Walters via RE-wrenches wrote:</p>
                    <blockquote type="cite"
style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0"
                      class="">
                      <div class="pre"
style="margin: 0; padding: 0; font-family: monospace">Greetings All;<br
                          class="">
                        <br class="">
                        I have Fortress Battery installation with a pair
                        of E Vault batteries set up in a Master/ Slave
                        arrangement.  Its been working fine for over a
                        year, but the customer just had a complete
                        shutdown of the batteries which left multiple
                        freezers, and refrigerator with rotting food.  
                        When he rebooted the batteries by turning on/off
                        the main breaker on each, they both come up and
                        showed 100% SOC on the Master, and 98% on the
                        other.    There were no fault codes.   I just
                        recently installed a larger PV array, and so the
                        system has been reaching full charge every
                        morning.<br class="">
                        <br class="">
                        I have multiple calls in to Fortress, but not
                        hearing anything back from them at all.  We did
                        have a lightning surge event a few months ago,
                        that damaged a Midnite SPD (first ever for me),
                        and took out the control board on the
                        generator.  One VFX inverter has an LED out, but
                        we only use two inverters of the Quad stack, so
                        I just switched to another inverter.  All other
                        equipment appeared fine: Midnite controllers,
                        rest of the Outback VFX quad stack, and never
                        any issues seen with the Fortress batteries.<br
                          class="">
                        <br class="">
                        The other odd thing, is since he rebooted the
                        batteries, the system is working fine, and
                        recharging to 100%  by 9:30 am as before.    Is
                        it possible the Fortress BMS were damaged and
                        are now having an intermittent shutdown issue? 
                        I did ask him to temporarily disconnect the
                        comms between batteries, in case it is a bad BMS
                        on one, it will isolate it from the other.<br
                          class="">
                        <br class="">
                        This is a tough one to figure out, since it
                        hasn't happened again, and there are no fault
                        codes.  The Mate 3 shows a low frequency AC
                        code, but that's usually just from the generator
                        shutting down.    Any help, ideas, experiences,
                        would be greatly appreciated.<br class="">
                        <br class="">
                        Thanks,<br class="">
                        <br class="">
                        Ray Walters<br class="">
                        Remote Solar<br class="">
                        <br class="">
                        _______________________________________________<br
                          class="">
                        List sponsored by Redwood Alliance<br class="">
                        <br class="">
                        Pay optional member dues here: <a
                          href="http://re-wrenches.org/" target="_blank"
                          rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">http://re-wrenches.org</a><br
                          class="">
                        <br class="">
                        List Address: <a
href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true"
                          class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br
                          class="">
                        <br class="">
                        Change listserver email address & settings:<br
                          class="">
                        <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                          target="_blank" rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br
                          class="">
                        <br class="">
                        There are two list archives for searching. When
                        one doesn't work, try the other:<br class="">
                        <a
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                          target="_blank" rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br
                          class="">
                        <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                          target="_blank" rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br
                          class="">
                        <br class="">
                        List rules & etiquette:<br class="">
                        <a
href="http://www.re-wrenches.org/etiquette.htm" target="_blank"
                          rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br
                          class="">
                        <br class="">
                        Check out or update participant bios:<br
                          class="">
                        <a href="http://www.members.re-wrenches.org/"
                          target="_blank" rel="noopener noreferrer"
                          moz-do-not-send="true"
                          class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br
                          class="">
                        <br class="">
                      </div>
                    </blockquote>
                    <br class="">
                    <fieldset class="moz-mime-attachment-header"></fieldset>
                    <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext"
                    href="http://re-wrenches.org/"
                    moz-do-not-send="true">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated moz-txt-link-freetext"
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext"
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                    moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                    moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext"
                    href="http://www.re-wrenches.org/etiquette.htm"
                    moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext"
                    href="http://www.members.re-wrenches.org/"
                    moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
                  </blockquote>
                </div>
                _______________________________________________<br
                  class="">
                List sponsored by Redwood Alliance<br class="">
                <br class="">
                Pay optional member dues here: <a
                  href="http://re-wrenches.org"
                  class="moz-txt-link-freetext" moz-do-not-send="true">http://re-wrenches.org</a><br
                  class="">
                <br class="">
                List Address: <a
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  class="moz-txt-link-freetext" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br
                  class="">
                <br class="">
                Change listserver email address & settings:<br
                  class="">
                <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  class="moz-txt-link-freetext" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br
                  class="">
                <br class="">
                There are two list archives for searching. When one
                doesn't work, try the other:<br class="">
                <a class="moz-txt-link-freetext"
href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                  moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br
                  class="">
                <a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                  moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br
                  class="">
                <br class="">
                List rules & etiquette:<br class="">
                <a class="moz-txt-link-freetext"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a><br
                  class="">
                <br class="">
                Check out or update participant bios:<br class="">
                <a class="moz-txt-link-freetext"
                  href="http://www.members.re-wrenches.org"
                  moz-do-not-send="true">http://www.members.re-wrenches.org</a><br
                  class="">
                <br class="">
              </div>
            </blockquote>
          </div>
          <br class="">
        </div>
      </blockquote>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>