<html>
<head>
<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<style type="text/css" style="display:none;"> P {margin-top:0;margin-bottom:0;} </style>
</head>
<body dir="ltr">
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
If all the 120 VAC loads have their neutrals land in the main meter panel then there is no need to run a neutral from there to the sub panel, as long as the inverter does have a neutral connection back to the meter panel.  </div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Especially when the inverter goes off grid it needs that neutral connection to the loads neutral in the meter panel. </div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Don Barch</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
Energy Solar</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div class="elementToProof" style="font-family: Aptos, Aptos_EmbeddedFont, Aptos_MSFontService, Calibri, Helvetica, sans-serif; font-size: 12pt; color: rgb(0, 0, 0);">
On Mon, Jul 29, 2024 at 11:53?PM William Miller via RE-wrenches<br>
<re-wrenches@lists.re-wrenches.org> wrote:<br>
><br>
> Friends:<br>
><br>
> I found a grid-tie battery-backup system with a 120/240 VAC critical loads sub-panel that has no neutral run to it.  All of the 120 VAC loads have their neutrals land in the meter panel.<br>
><br>
> I have always felt instinctively that the neutrals should land in the breaker panel that feeds the circuit.  I have looked through the NEC to find a passage that spells this out but I can seem to find one.<br>
><br>
> Is this a code requirement?  Is this recommended practice?<br>
><br>
> Thanks in advance.<br>
><br>
> William Miller<br>
><br>
> Miller Solar<br>
><br>
> 17395 Oak Road, Atascadero, CA 93422<br>
><br>
> 805-438-5600<br>
><br>
> <a href="http://www.millersolar.com" target="_blank" id="OWAa0a47e3d-95fd-ffb9-4618-1cfbb5ce8096" class="OWAAutoLink" rel="noopener noreferrer" data-auth="NotApplicable" data-linkindex="0">
www.millersolar.com</a><br>
<br>
</div>
</body>
</html>