<div dir="auto">Can anybody clarify the following instruction from the manual?<div dir="auto"><br></div><div dir="auto">"GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"</div><div dir="auto"><br></div><div dir="auto">Does this mean do not connect the array equipment grounding conductor to the grounding terminal in the inverter? Where would be the suggested place to connect the equipment grounding conductor, and why does it make a difference? It would still be electrically bonded to the grounding terminal in the inverter. </div><div dir="auto"><br></div><div dir="auto">I'm asking because I do, in fact, have an equipment grounding conductor from the array connected to the ground terminal in the inverter at a home. I am getting an F08 GFDI fault. The manual doesn't say anything about the DC side with respect to this error. It suggests it is an AC current leakage to ground. But Sol-Ark tech support suggested that I disconnect the PV to rule it out as a source of the fault.</div><div dir="auto"><br></div><div dir="auto"><br></div><div dir="auto"><br></div><div dir="auto">Jason Szumlanski </div><div dir="auto">Florida Solar Design Group </div></div>