<div dir="ltr">Good Morning Wrenches,<div><br></div><div>I am working through a design with existing PV and a proposed small battery bank backup.  We are pairing existing IQ7As with the System Controller 3, and a single 5P battery.  We are well above the 150% oversizing of PV to battery capacity that Enphase allows so I need to open some of my branch circuits when off-grid.</div><div><br></div><div>Is there a good reason not to use the grid side of the system (NO relays) to detect and open 2 of my branch circuits as opposed to using the aux relay contacts in the IQ System controller to open when off-grid?  Is there ever a time when the System controller would bring the excess PV online?  It seems cheaper and better to use the grid voltage to perform this logic to me but I may be missing something.</div><div><br></div><div>Thanks for your input</div><div><div><br></div><span class="gmail_signature_prefix">-- </span><br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div><br></div><div><font color="#305A78" face="'times new roman', serif"><br></font></div><div><br></div>Mac Lewis<br><br><span style="font-family:'Times New Roman';font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3"><p align="left"><font color="#000000" face="Verdana, Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="'times new roman', serif">"Yo solo sé que no sé nada." </font><span style="font-weight:700;color:rgb(104,104,104)"><font face="'times new roman', serif">-Sócrates</font></span></span></span></font></p></font></b></span></div></div></div>