<div dir="auto"><div>I had a similar issue once with a Sol-Ark 12k, triple stack.  The issue ended up being that the phase relationship got reversed during the installation. AC out and AC in need to be carefully phased out. I don't really understand why, but it's an easy thing to check. </div><div dir="auto"><br></div><div dir="auto">Let us know what you find. </div><div dir="auto"><br></div><div dir="auto">Good luck<br><br><div class="gmail_quote" dir="auto"><div dir="ltr" class="gmail_attr">On Thu, Oct 26, 2023, 9:03 AM White, Will via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">





<div lang="EN-US" link="#0563C1" vlink="#954F72" style="word-wrap:break-word">
<div class="m_-4257783654505742629WordSection1">
<p class="MsoNormal">Don,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Your Fluke clamp meter should indicate the current flow by showing a negative or positive current reading unless you’ve got an old meter. On the top of the meter inside the jaw is an arrow that points in the direction of current flow if
 the reading is positive. If it’s negative, the current is flowing in the opposite direction of the arrow.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Thanks,<u></u><u></u></p>
<p class="MsoNormal">Will<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div style="border:none;border-top:solid #e1e1e1 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b>From:</b> RE-wrenches <<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches-bounces@lists.re-wrenches.org</a>>
<b>On Behalf Of </b>don <a href="http://energysolarnow.com" target="_blank" rel="noreferrer">energysolarnow.com</a> via RE-wrenches<br>
<b>Sent:</b> Wednesday, October 25, 2023 5:17 PM<br>
<b>To:</b> <a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a><br>
<b>Cc:</b> don <a href="http://energysolarnow.com" target="_blank" rel="noreferrer">energysolarnow.com</a> <<a href="mailto:don@energysolarnow.com" target="_blank" rel="noreferrer">don@energysolarnow.com</a>><br>
<b>Subject:</b> [EXTERNAL] [RE-wrenches] Sol-Ark phantom loads<u></u><u></u></p>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
<p><strong><span style="font-size:10.0pt;font-family:"Calibri",sans-serif;color:#cc3300;background:#ffd480">CAUTION:</span></strong><span style="font-size:10.0pt;color:black;background:#ffd480"> This email originated from outside of the organization. Do not
 click links or open attachments unless you recognize the sender and know the content is safe.</span><u></u><u></u></p>
<p> <u></u><u></u></p>
<div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Just spent yesterday debugging a Sol-Ark 15 kW inverter phantom load weirdness.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">With Work Mode set at Limited Power To Home it seemed to get a bit schizo, pulling around 6kW in from the grid on leg L1 and around 13 kW on the other L2 leg, with
 7kW of PV added. No house loads were involved. The monitoring called this a 13 kW load. <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">I measured something like 50 amps on L2 and neutral; 120 Volts on L1 and 125 Volts on L2 at the house. My Fluke clamp-on amp meter does not say which way AC current
 is flowing. The utility meter showed it as  power coming in.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">At the main meter panel about 150 ft away from the house the voltages were better balanced; probably due to proximity to the utility transformer. Those leg voltages
 were balanced when the inverter was shut down.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Oddly, this phantom loading decreased with decreasing PV production later in the day.</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Working with Sol-Ark tech support we (of course) downloaded new firmware, then changed Work Mode to Limited Power To Load. After a couple of resets this had the effect
 of allowing the inverter to cover just the loads in the battery-backed subpanel; not those at the house main panel where the CT sensors are located. The phantom 13kW load has not recurred.
<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Has anyone seen an inverter try to mix import and export on different legs by creating phantom loads?<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Don Barch<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black">Energy Solar<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-size:12.0pt;font-family:"Aptos",sans-serif;color:black"><u></u> <u></u></span></p>
</div>
</div>
</div>
<hr>
<p style="font-size:8pt;line-height:10pt;font-style:italic;font-family:'Cambria','times roman',serif">
Please be advised that this email may contain confidential information. If you are not the intended recipient, please notify us by email by replying to the sender and delete this message.</p>
</div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div></div>