Friends, <br>
<br>
I'm currently onsite with a system. Just replaced 4 XW + 6848's
with 4 XW Pros. Updated the Gateway to rev. 1.17 and the Pros to
2.04. Have some questions/observations so far.<br>
<br>
System: Off Grid with 4 XW Pros, 18 MPPT 80 600s, 2 SCPs, 1 Gateway,
1 Battery Monitor, 1 AGS. 3000 ahr of NiFe batteries. 36 kW Kubota
Genset.<br>
<br>
I tried using the Inverter SCP to program settings on the new
inverters and it took everything but when I checked on InsightLocal
the settings had not changed. They were all still default so I had
to go through it again one at a time through insightlocal. I'm
guessing the SCP no longer works for programming with the Gateway?
Can anyone confirm? Programming used to work through the SCP with
the old XW+ inverters and firmware. <br>
<br>
Tried using the Solar SCP to change settings on the charge controls
but had to use insight local to change each individually. Used to
be able to use the "copy from" function which was a real time
saver. Wondering if anyone else has run into the same problem, or
if it works for them, what am I missing? Is there a cool way to
change one setting with insightlocal and get it to change the other
17? <br>
<br>
Observations:<br>
- looking at the CC's via insightlocal,<br>
under configuration -> advanced ->controls - I set all
chargers "enabled" but the next day or so they all go to
"disabled". They all still work though. Doesn't seem to affect
operations. <br>
<br>
under configuration -> advanced ->charger settings - I
have the first CC set to "primary" and the rest to secondary. No
idea if that's right or not. seems to work. Options are
"stand-alone, primary, secondary and echo". I could not find
definitions in the manual on them. <br>
<br>
- looking at the XW Pros via insight local,<br>
under configuration -> advanced ->controls -> Backup
Mode - I disabled BAckup mode since I'm not backing up the grid. <u>System
shut down immediately.</u> Backup mode must be enabled when
you're off grid. <br>
<br>
Thanks in advance : )<br>
<br>
Greg Egan<br>