    Friends, <br>
    <br>
    I'm currently onsite with a system.  Just replaced 4 XW + 6848's
    with 4 XW Pros.  Updated the Gateway to rev. 1.17 and the Pros to
    2.04.  Have some questions/observations so far.<br>
    <br>
    System: Off Grid with 4 XW Pros, 18 MPPT 80 600s, 2 SCPs, 1 Gateway,
    1 Battery Monitor, 1 AGS.  3000 ahr of NiFe batteries.  36 kW Kubota
    Genset.<br>
    <br>
    I tried using the Inverter SCP to program settings on the new
    inverters and it took everything but when I checked on InsightLocal
    the settings had not changed.  They were all still default so I had
    to go through it again one at a time through insightlocal.  I'm
    guessing the SCP no longer works for programming with the Gateway? 
    Can anyone confirm?  Programming used to work through the SCP with
    the old XW+ inverters and firmware.  <br>
    <br>
    Tried using the Solar SCP to change settings on the charge controls
    but had to use insight local to change each individually.  Used to
    be able to use  the "copy from" function which was a real time
    saver.  Wondering if anyone else has run into the same problem, or
    if it works for them, what am I missing?  Is there a cool way to
    change one setting with insightlocal and get it to change the other
    17?  <br>
    <br>
    Observations:<br>
    - looking at the CC's via insightlocal,<br>
        under configuration -> advanced ->controls - I set all
    chargers "enabled" but the next day or so they all go to
    "disabled".  They all still work though.  Doesn't seem to affect
    operations.  <br>
    <br>
        under configuration -> advanced ->charger settings - I
    have the first CC set to "primary" and the rest to secondary.  No
    idea if that's right or not.  seems to work.  Options are
    "stand-alone, primary, secondary and echo".  I could not find
    definitions in the manual on them.  <br>
    <br>
    - looking at the XW Pros via insight local,<br>
        under configuration -> advanced ->controls -> Backup
    Mode - I disabled BAckup mode since I'm not backing up the grid. <u>System
      shut down immediately.</u>  Backup mode must be enabled when
    you're off grid.  <br>
    <br>
    Thanks in advance : )<br>
    <br>
    Greg Egan<br>