<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto"><div dir="ltr"></div><div dir="ltr">Certainly could be the meter or how it’s being used. Like is the Electrican checking the main or output from the inverter?</div><div dir="ltr"><br></div><div dir="ltr">If the inverter output shows these numbers I’d check to make sure the inverter is in the correct grid connection  setting. </div><div dir="ltr"><br></div><div dir="ltr">Jay</div><div dir="ltr"><br><blockquote type="cite">On Apr 27, 2023, at 5:13 PM, Dave Angelini Offgrid Solar via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr"><meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
<div id="signature">My metrology experience is he needs to prove it with a second meter. In a lab setting, at least 2 of 3 calibrated meters need to agree.</div>
<div> </div>
<div>I would also ask Fluke. They have been really good over the years. Good Luck.<br>
<pre> </pre>
<pre><strong><span style="font-size: small;">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" rel="noopener">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
</div>
<p><br></p>
<p id="reply-intro">On 2023-04-27 2:10 pm, August Goers via RE-wrenches wrote:</p>
<blockquote type="cite" style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0">
<div id="replybody1">
<div dir="ltr">Hi Wrenches,
<div> </div>
<div>We have a residential site with grid tied solar where there is an electrician involved who has gotten into taking site readings and thinks there is a power factor problem. My gut on it is that there is some sort of measurement reading error, and that the power factor should be around 1. </div>
<div> </div>
<div>The electrician is using a Fluke 3540FC power monitor and has provided a spreadsheet comparing active power to apparent power and calculating power factor. See below (you might have to open the image and zoom in to read it). This measurement was taken with a PV system running, presumably sending some power back to the grid.  Note that the phase B active power measurement is negative (PV exporting to grid) and that the apparent power is positive. This nets in a power factor that is crazy low of 0.05.</div>
<div> </div>
<div>Does anyone have experience about whether a meter like this can properly measure these readings - maybe there is a setting error or it can't deal with negative readings?</div>
<div> </div>
<div><div><image.png></div></div>
<div> </div>
<div>Best,</div>
<div> </div>
<div>August</div>
<div>Luminalt</div>
</div>
</div>
<br>
<div class="pre" style="margin: 0; padding: 0; font-family: monospace">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noopener noreferrer">http://re-wrenches.org</a><br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for searching. When one doesn't work, try the other:<br><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noopener noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">http://www.members.re-wrenches.org</a><br><br></div>
</blockquote>

<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address & settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules & etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></body></html>