<div dir="ltr">480.7 is Disconnect Methods, and addresses different scenarios and voltages<div>(A) is for batteries "with a voltage over 60 volts dc" requiring a disconnect accessible to and within sight of the battery</div><div>(B) is in regards to 1- and 2-family dwellings, and doesn't specify a voltage, just that an external, emergency disconnect is required</div>(C) is segmenting strings into 240 Vdc nominal or less segments, and on it goes to (G)<div><br></div><div>I don't agree with the earlier statement in this chain (and I didn't dig up the original thread to see it in context) - based on how the Section is arranged; if the 60 volt requirement applied to both (A) and (B) then they would most likely be (A)(1) and (A)(2), under an (A) heading that included a statement to the effect of "For stationary storage batteries of 60 volts blah blah the following shall apply."<div><br></div><div>As it is now, the emergency disconnect requirement (B) doesn't specify a voltage above which it applies, and the voltage specification in (A) doesn't apply to (B). </div><div><br></div><div><div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div>Cheers,</div><div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV Installation Professional™ R031508-59</div><div>National Electrical Code® CMP-4 Member</div><div>(520) 204-6639<br><div><br></div><div><div><div>Solar Energy International<br><a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div><div><br></div></div></div></div></div></div></div></div></div></div></div></div><br></div></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Feb 20, 2023 at 11:40 AM James Jarvis via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr">Did they ever explain why they were requiring it on a nominal 48 volt system? NEC 480.7(B) (from memory, I think that is the right article) says it is for nominal voltage of 60 volts or higher. IE your 48 volt system is exempt.<div><br></div><div>Jay pointed this out on February 3rd.<br><div><br></div><div><br clear="all"><div><div dir="ltr"><div dir="ltr"><div>-James Jefferson Jarvis<br>APRS World, LLC<br>+1-507-454-2727<br></div><a href="http://www.aprsworld.com/" target="_blank">http://www.aprsworld.com/</a><br></div></div></div><br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Feb 20, 2023 at 12:36 PM William Miller via RE-wrenches <<a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div><div lang="EN-US"><div><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif"">Friends:</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif""> </span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif"">Here is how this resolved for my upcoming project:  I submitted a request to the building department to waive the requirement for a DC disconnect. I based the justification on the need to keep a pressure pump for the fire sprinklers and a fire alarm operational.  I will supply an external AC disconnect to de-energize all premise wiring except those circuits mentioned above.  The request was granted.</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif""> </span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif"">William</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Verdana,"sans-serif""> </span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Arial,"sans-serif"">Miller Solar</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Arial,"sans-serif"">17395 Oak Road, Atascadero, CA 93422</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Arial,"sans-serif"">805-438-5600</span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Arial,"sans-serif""><a href="http://www.millersolar.com/" target="_blank">www.millersolar.com</a></span></p><p class="MsoNormal"><span style="font-size:12pt;font-family:Arial,"sans-serif"">CA Lic. 773985</span></p><p class="MsoNormal"> </p><p class="MsoNormal"> </p></div></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</div></blockquote></div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn't work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>