    Chris,<br>
    I also found Kirk's response to capture what I would've checked
    first. Ray is correct about multiple neutral-ground bonds, but
    there's a point that I think has been missed. You didn't identify
    the generator, and I'm going to assume that it's a portable gasoline
    unit. They have GFCIs on the AC output because they're almost never
    connected to a solid ground, and that's the safest they can make the
    output - they internally bond neutral to the chassis of the gennie
    and run the output through a GFCI. When they're connected to an off
    grid home there's always going to be a ground loop in a correctly
    wired installation, because the Powercenter is the first point of
    disconnect and is thus where the overall system neutral-ground bond
    should be made. <br>
    <br>
    In my experience there is no fully Code-compliant solution to this.
    At least, I never came up with one, and many years ago neither could
    John Wiles when I discussed it with him. You don't want to
    disconnect the bond in the E-Panel because if the gennie is the only
    bond point and it's disconnected (by unplugging it) your system
    ground becomes unbonded. Stationary generators generally separate
    the bond, or at least allow it to be separated (small Kohler units
    always allowed this), because of this very issue - for prime power
    (non-solar) applications the bond is made at the source, but where
    it's a secondary source it needs to be separated. Portable
    generators don't give this option.<br>
    <br>
    The best solution John and I came up with is to treat the gennie as
    a separately derived system: ground it to its own rod; put it far
    enough from the home that you can't touch it and anything grounded
    in the home at the same time; bond normally in the E-Panel; and
    eliminate or disconnect and tie off the bonding conductor between
    the gennie and the PV system. Only by treating it as a separately
    derived system can you get around the requirement that all service
    equipment must be bonded.<br>
    <br>
    And if the gennie has a separable neutral-ground bond that's been
    opened, I have no idea how to solve your issue... 😉<br>
    Allan<br>
    -- <br>
    <b><span style="font-size:12.0pt;font-family:"Times New
        Roman",serif;
        mso-fareast-font-family:"Times New Roman"">Allan
        Sindelar</span></b><span
      style="font-size:12.0pt;font-family:"Times New
      Roman",serif;mso-fareast-font-family:
      "Times New Roman""><br>
    </span><a href="mailto:allan@sindelarsolar.com"><span
        style="font-size:10.0pt;
        font-family:"Times New
        Roman",serif;mso-fareast-font-family:"Times New
        Roman"">allan@sindelarsolar.com</span></a><span
      style="font-size:12.0pt;font-family:"Times New
      Roman",serif;mso-fareast-font-family:
      "Times New Roman""><br>
    </span><span style="font-size:10.0pt;font-family:"Times New
      Roman",serif;
      mso-fareast-font-family:"Times New Roman"">(Former)
      NABCEP Certified PV Installation
      Professional<br>
      New Mexico EE98J Journeyman Electrician<br>
      Founder (Retired), <span style="mso-bidi-font-weight:bold">Positive
        Energy, Inc<span class="GramE">.<br>
          Founder (Retired), Sindelar Solar<br>
        </span></span>
      <b>505 780-2738 cell</b></span>
    <div class="moz-cite-prefix"><br>
      On 12/16/2022 12:44 PM, Ray Walters via RE-wrenches wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:d1f19250-0f06-44ad-36b0-d17fa2ab0e10@solarray.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>Undoing the N-G bond at the E panel may not do it either.  Are
        you sure neutral isn't also bonded in the main distribution
        panel?  It usually is bonded at the generator, so you definitely
        have to unbond there.  I'd say 60 to 70% of off grid systems are
        not bonded correctly that I've seen.  Just what Kirk said: it
        should only be bonded N-G at one and only one spot.  Check sub
        panels too.  My record was seven N-G bonds on one site.  It
        caused the shower to be energized; the customer thought that was
        normal....(don't touch the shower head!?!).....That site even
        had a N-G bond in the well pump wiring!  Took 3 days of
        unF***ing that wiring to finally get it.<br>
      </p>
      <p>It ain't safe, until it's right.  The GFCI is doing its job,
        and so is the Magnum.  Now the electrician has to do his job. 
        Unless you wired the whole house, you're On to fix it. 
        Especially off grid, I see an amazing bunch of DIY garbage. 
        Find out who did the original wiring.  Probably not a pro.<br>
      </p>
      <p>Ray Walters<br>
        Remote Solar<br>
      </p>
      <div class="moz-cite-prefix">On 12/16/2022 11:35 AM, Kirk Herander
        via RE-wrenches wrote:<br>
      </div>
      <blockquote type="cite"
cite="mid:CADN4JrcEge2w9FFu=2kKySJ4AsQx=Yyn9HJdYTjZM6HmSk4RLg@mail.gmail.com">
        <meta http-equiv="content-type" content="text/html;
          charset=UTF-8">
        <div dir="ltr">You may have neutral and ground connected at more
          than 1 location, meaning at the genset and in house panel,
          which means the ground is carrying current back to the
          generator in parallel with the neutral.
          <div><br>
            <div>I remember with some Honda portables we had to float
              the neutral at the genset or the inverter would trip the
              generator's GFI when trying to charge the batteries.</div>
          </div>
          <br>
          <div class="gmail_quote">
            <div dir="ltr" class="gmail_attr">On Fri, Dec 16, 2022 at
              1:16 PM Dave Angelini Offgrid Solar via RE-wrenches <<a
                href="mailto:re-wrenches@lists.re-wrenches.org"
                target="_blank" moz-do-not-send="true"
                class="moz-txt-link-freetext">re-wrenches@lists.re-wrenches.org</a>>
              wrote:<br>
            </div>
            <blockquote class="gmail_quote" style="margin:0px 0px 0px
              0.8ex;border-left:1px solid
              rgb(204,204,204);padding-left:1ex">
              <div
                style="font-size:12pt;font-family:Verdana,Geneva,sans-serif">
                <div
                  id="m_-6322699239123822814m_1613139528423491230signature">
                  <pre><span style="font-size:12pt">The easy answer is try another genset !  You have to be more specific, did it ever work? Is it new? etc.  Good Luck !</span></pre>
                  <pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" rel="noopener" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net" target="_blank" moz-do-not-send="true" class="moz-txt-link-freetext">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
                </div>
                <p
                  id="m_-6322699239123822814m_1613139528423491230reply-intro">On
                  2022-12-16 10:04 am, Chris Daum via RE-wrenches wrote:</p>
                <blockquote type="cite" style="padding:0px
                  0.4em;border-left:2px solid rgb(16,16,255);margin:0px">
                  <div
                    style="margin:0px;padding:0px;font-family:monospace">Hi
                    folks:<br>
                    <br>
                    We have a new Magnum MS4024 mounted on an E-Panel
                    using a MidNite Classic 150 and Whiz-Bang JR with
                    power coming from an array of Trina
                    TSM365-De06X-05(II) (three strings of three) with
                    the ME-RC50 and a HUP SolarOne 6-85-14/24 battery.<br>
                    When we attempt to use the PFC (Power Factored
                    Charger), the Gen Set’s GFCI outlets trip.  Thus far
                    we have verified the connections are secure, assured
                    that the gen set is grounded, disconnected the
                    jumper within the E-Panel between the ground buss
                    and neutral, checked AC voltages, removed the
                    MNSPD’s from the buss(s)…  Stumped now on what an
                    appropriate next step should be.  How do we get the
                    PFC to function properly?  What are we missing?<br>
                    <br>
                    Best,<br>
                    <br>
                    Chris Daum<br>
                    Oasis Montana Inc.<br>
                    406-777-4309 or 4321<br>
                    406-777-4309 fax<br>
                    <a href="http://www.oasismontana.com" rel="noopener
                      noreferrer" target="_blank" moz-do-not-send="true">www.oasismontana.com</a>
                    <br>
                    <br>
                    _______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    Pay optional member dues here: <a
                      href="http://re-wrenches.org" rel="noopener
                      noreferrer" target="_blank" moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://re-wrenches.org</a><br>
                    <br>
                    List Address: <a
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      target="_blank" moz-do-not-send="true"
                      class="moz-txt-link-freetext">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Change listserver email address & settings:<br>
                    <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="noopener noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    There are two list archives for searching. When one
                    doesn't work, try the other:<br>
                    <a
                      href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                      rel="noopener noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                    <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                      rel="noopener noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List rules & etiquette:<br>
                    <a href="http://www.re-wrenches.org/etiquette.htm"
                      rel="noopener noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out or update participant bios:<br>
                    <a href="http://www.members.re-wrenches.org"
                      rel="noopener noreferrer" target="_blank"
                      moz-do-not-send="true"
                      class="moz-txt-link-freetext">http://www.members.re-wrenches.org</a><br>
                  </div>
                </blockquote>
              </div>
            </blockquote>
          </div>
          <br clear="all">
          -- <br>
          <div dir="ltr">
            <div dir="ltr">
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt"><a
                    name="m_-6322699239123822814_SignatureSanitizer__MailAutoSig"
                    moz-do-not-send="true"><b>Kirk Herander / </b></a><b><a
                      href="mailto:kirkh@vermont.solar" title="Send an
                      email to kirkh@vermont.solar; Send an email to
                      kirkh@vermont.solar" style="color:blue"
                      target="_blank" moz-do-not-send="true"
                      class="moz-txt-link-freetext">kirkh@vermont.solar</a></b></span></p>
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt"><b>Owner|Principal,
                    VT Solar, LLC</b></span></p>
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt"><b><i>Celebrating
                      our 31<sup>st</sup> Anniversary 1991-2022!!</i></b></span></p>
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt"><a
href="https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0"
                    title="Click to open in a new window or tab
https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb...;
                    Click to open in a new window or tab
https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb..."
                    target="_blank" moz-do-not-send="true"><b><span
                        style="color:blue">www.vermont.solar</span></b></a></span></p>
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt">dba Vermont
                  Solar Engineering</span></p>
              <p class="MsoNormal"
                style="color:rgb(0,0,0);font-family:Arial;font-size:16px;margin:0in
                0in 0.0001pt"><span style="font-size:10pt">802.863.1202</span></p>
            </div>
          </div>
        </div>
      </blockquote>
    </blockquote>
    <div class="moz-signature"><span
        style="font-size:10.0pt;font-family:"Times New
        Roman",serif;
        mso-fareast-font-family:"Times New Roman""></span><span
        style="font-size:12.0pt;font-family:"Times New
        Roman",serif;
        mso-fareast-font-family:"Times New Roman""><o:p></o:p></span>
      <div class="WordSection1">
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
    </div>
  </body>
</html>