<div dir="auto">I have a commercial 208 volt job where four of 11 fully populated strings of IQ7A had breakers that were tripped as reported by the client. They were able to reset two of them. They also reported that the two they were not able to reset we're very hot. The other two were warm.  By the time I got to the site, all four breakers had permanently failed. <div dir="auto"><br></div><div dir="auto">Once I got replacements, I was able to install them and they turned on without any faults. I gave it about 15 minutes and then put my infrared camera on it. To my surprise, the breaker immediately above two of the failed breakers and across from the other two failed breakers was clearly hot. I'm thinking this might have been the bad breaker all along causing the heat issue on the bus bar which made adjacent breakers fail. But this hot breaker did not fail.</div><div dir="auto"><br></div><div dir="auto">Does this seem like a plausible scenario, and if so, any ideas on what might have caused it? All of the breaker bolts were tight, but a couple were not torqued to spec. I just find it strange that one breaker that didn't fail would cause other adjacent breakers to heat up enough to fail.</div><div dir="auto"><br></div><div dir="auto">Flir image attached. This was after I replaced the four failed breakers.</div><div dir="auto"><br></div><div dir="auto">Jason Szumlanski</div><div dir="auto">Florida Solar Design Group </div></div>