Jay,<br>
Well, yes, they do need heaters, and I tried the Utah installer's
solution suggested by Nick and it worked perfectly.<br>
This was a job high up in the San Pedro Mountains. Shortly after I
installed a single 16 kWh cabinet, a plumber set up an electric
heater in an unheated space to protect pipes, which of course
drained the batteries. This was an unoccupied home. The BMS shut off
the batteries, which shut off the 24W (total) heating pads and
allowed the batteries to drop below freezing, so that the array
couldn't recharge them. It took running the heater on a portable
generator to heat the batteries, and at 33<font size="1">1/2</font>
degrees they came back on. <br>
<br>
I have attached the pdf of a PowerPoint Kyle sent me that discusses
doing this. The batteries haven't shut down due to temperature
before or since this one occurrence.<br>
Allan<br>
<br>
<div class="moz-cite-prefix">On 7/22/2022 6:39 AM, Jay via
RE-wrenches wrote:<br>
</div>
<blockquote type="cite"
cite="mid:14174B60-1AFA-4A9B-A495-26CC97B286D7@gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div dir="ltr">Hi Michael <br>
</div>
...<br>
<div dir="ltr">As to the blue planet, I don’t think they need
heaters. I was working on a system with one and the battery
housing was darn warm, much warmer than anything else in the
inverter room. Surprising actually. <br>
</div>
<div dir="ltr">Jay</div>
</blockquote>
<div class="moz-cite-prefix">On 7/22/2022 12:06 AM, Nick A Lucchese
via RE-wrenches wrote:<br>
</div>
<blockquote type="cite"
cite="mid:7BD6B1E9-0723-4856-A371-68FC077235BD@me.com">
<pre class="moz-quote-pre" wrap="">Greetings Jay,
I’ve been using Blue Ions exclusively for the last 5 years almost. Most of my sites sit around 1800-3000’ and only had two shutdowns due to cold temps. Since it takes such significant periods of time for that much mass to get to get below the temps of concern it really just hasn’t been a problem. Of my two shutdowns, one was my own where I’ve intentionally left the cabinet in an unconditioned area where my old L-16’s sat and the power was only out from 5:00 am to 8:30 am a couple Februarys ago. My first site that had been effected was at a client’s where the cabinet sits in an unconditioned multi-use power shed and the door to the building had been left wide open by mistake throughout the evening and the temperature logger had recored 17 degrees by 4 AM. By 10 AM by the time I had made it to the site the power was back and we’ve not had a problem since.
Back when Kyle was at Blue Planet he said there was a dealer in Utah that placed a small seedling or reptile heating mat in the cabinet along with lining the sides and bottom with Reflectix. From what I recall they had reported great success with that effort. I think they might have even crafted a little support document showing their strategy. I’ve been keeping that one in mind for any potential project that might push the limits but seems like for most of us the instances where it would be a problem will be rare.
Best of luck, Nick
</pre>
</blockquote>
<blockquote type="cite"
cite="mid:14174B60-1AFA-4A9B-A495-26CC97B286D7@gmail.com">
<blockquote type="cite">
<div dir="ltr">
<div class="gmail_quote">
<blockquote class="gmail_quote" style="margin:0px 0px 0px
0.8ex;border-left:1px solid
rgb(204,204,204);padding-left:1ex">
On 7/21/2022 2:30 PM, jay via RE-wrenches wrote:<br>
> HI All,<br>
> As I get more calls for offgrid designs with lithium
batteries I”m wondering what you all are doing to keep the
batteries warm when it gets cold. For some of you 0 F
will seem mild, others super cold.<br>
> Doing a battery box and heating that or heating the
whole inverter/battery shed?<br>
> I’m definitely not looking at batteries like battle
born with the built in heaters.<br>
> Simpliphi, Discover, some of the newer server rack
ones ( UL listed), etc.><br>
> Thanks in advance<br>
> Jay<br>
</blockquote>
</div>
</div>
</blockquote>
</blockquote>
<div class="moz-signature">-- <br>
<meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
<meta name="ProgId" content="Word.Document">
<meta name="Generator" content="Microsoft Word 15">
<meta name="Originator" content="Microsoft Word 15">
<link rel="File-List"
href="Allan%20SS%20signature%20block%202017_files/filelist.xml">
<!--[if gte mso 9]><xml>
<o:DocumentProperties>
<o:Author>Allan Sindelar</o:Author>
<o:Template>Normal</o:Template>
<o:LastAuthor>Allan Sindelar</o:LastAuthor>
<o:Revision>2</o:Revision>
<o:TotalTime>0</o:TotalTime>
<o:Created>2017-04-03T01:19:00Z</o:Created>
<o:LastSaved>2017-04-03T01:19:00Z</o:LastSaved>
<o:Pages>1</o:Pages>
<o:Words>41</o:Words>
<o:Characters>191</o:Characters>
<o:Lines>3</o:Lines>
<o:Paragraphs>1</o:Paragraphs>
<o:CharactersWithSpaces>231</o:CharactersWithSpaces>
<o:Version>15.00</o:Version>
</o:DocumentProperties>
<o:OfficeDocumentSettings>
<o:AllowPNG/>
</o:OfficeDocumentSettings>
</xml><![endif]-->
<link rel="themeData"
href="Allan%20SS%20signature%20block%202017_files/themedata.thmx">
<link rel="colorSchemeMapping"
href="Allan%20SS%20signature%20block%202017_files/colorschememapping.xml">
<!--[if gte mso 9]><xml>
<w:WordDocument>
<w:SpellingState>Clean</w:SpellingState>
<w:GrammarState>Clean</w:GrammarState>
<w:TrackMoves>false</w:TrackMoves>
<w:TrackFormatting/>
<w:PunctuationKerning/>
<w:ValidateAgainstSchemas/>
<w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
<w:IgnoreMixedContent>false</w:IgnoreMixedContent>
<w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
<w:DoNotPromoteQF/>
<w:LidThemeOther>EN-US</w:LidThemeOther>
<w:LidThemeAsian>X-NONE</w:LidThemeAsian>
<w:LidThemeComplexScript>X-NONE</w:LidThemeComplexScript>
<w:Compatibility>
<w:BreakWrappedTables/>
<w:SnapToGridInCell/>
<w:WrapTextWithPunct/>
<w:UseAsianBreakRules/>
<w:DontGrowAutofit/>
<w:SplitPgBreakAndParaMark/>
<w:EnableOpenTypeKerning/>
<w:DontFlipMirrorIndents/>
<w:OverrideTableStyleHps/>
</w:Compatibility>
<m:mathPr>
<m:mathFont m:val="Cambria Math"/>
<m:brkBin m:val="before"/>
<m:brkBinSub m:val="--"/>
<m:smallFrac m:val="off"/>
<m:dispDef/>
<m:lMargin m:val="0"/>
<m:rMargin m:val="0"/>
<m:defJc m:val="centerGroup"/>
<m:wrapIndent m:val="1440"/>
<m:intLim m:val="subSup"/>
<m:naryLim m:val="undOvr"/>
</m:mathPr></w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:LatentStyles DefLockedState="false" DefUnhideWhenUsed="false"
DefSemiHidden="false" DefQFormat="false" DefPriority="99"
LatentStyleCount="371">
<w:LsdException Locked="false" Priority="0" QFormat="true" Name="Normal"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 1"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 2"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 3"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 4"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 5"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 6"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 7"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 8"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 9"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 9"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 1"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 2"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 3"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 4"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 5"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 6"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 7"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 8"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 9"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footnote text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="header"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footer"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index heading"/>
<w:LsdException Locked="false" Priority="35" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="caption"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="table of figures"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="envelope address"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="envelope return"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footnote reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="line number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="page number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="endnote reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="endnote text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="table of authorities"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="macro"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="toa heading"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 5"/>
<w:LsdException Locked="false" Priority="10" QFormat="true" Name="Title"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Closing"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Signature"/>
<w:LsdException Locked="false" Priority="1" SemiHidden="true"
UnhideWhenUsed="true" Name="Default Paragraph Font"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Message Header"/>
<w:LsdException Locked="false" Priority="11" QFormat="true" Name="Subtitle"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Salutation"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Date"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text First Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text First Indent 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Note Heading"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Block Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Hyperlink"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="FollowedHyperlink"/>
<w:LsdException Locked="false" Priority="22" QFormat="true" Name="Strong"/>
<w:LsdException Locked="false" Priority="20" QFormat="true" Name="Emphasis"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Document Map"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Plain Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="E-mail Signature"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Top of Form"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Bottom of Form"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal (Web)"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Acronym"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Address"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Cite"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Code"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Definition"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Keyboard"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Preformatted"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Sample"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Typewriter"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Variable"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal Table"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation subject"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="No List"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Contemporary"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Elegant"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Professional"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Subtle 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Subtle 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Balloon Text"/>
<w:LsdException Locked="false" Priority="39" Name="Table Grid"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Theme"/>
<w:LsdException Locked="false" SemiHidden="true" Name="Placeholder Text"/>
<w:LsdException Locked="false" Priority="1" QFormat="true" Name="No Spacing"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading"/>
<w:LsdException Locked="false" Priority="61" Name="Light List"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 1"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 1"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 1"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 1"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 1"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 1"/>
<w:LsdException Locked="false" SemiHidden="true" Name="Revision"/>
<w:LsdException Locked="false" Priority="34" QFormat="true"
Name="List Paragraph"/>
<w:LsdException Locked="false" Priority="29" QFormat="true" Name="Quote"/>
<w:LsdException Locked="false" Priority="30" QFormat="true"
Name="Intense Quote"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 1"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 1"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 1"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 1"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 1"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 1"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 1"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 1"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 2"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 2"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 2"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 2"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 2"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 2"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 2"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 2"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 2"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 2"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 2"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 2"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 2"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 2"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 3"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 3"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 3"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 3"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 3"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 3"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 3"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 3"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 3"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 3"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 3"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 3"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 3"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 3"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 4"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 4"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 4"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 4"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 4"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 4"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 4"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 4"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 4"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 4"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 4"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 4"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 4"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 4"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 5"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 5"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 5"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 5"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 5"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 5"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 5"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 5"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 5"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 5"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 5"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 5"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 5"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 5"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 6"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 6"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 6"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 6"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 6"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 6"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 6"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 6"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 6"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 6"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 6"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 6"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 6"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 6"/>
<w:LsdException Locked="false" Priority="19" QFormat="true"
Name="Subtle Emphasis"/>
<w:LsdException Locked="false" Priority="21" QFormat="true"
Name="Intense Emphasis"/>
<w:LsdException Locked="false" Priority="31" QFormat="true"
Name="Subtle Reference"/>
<w:LsdException Locked="false" Priority="32" QFormat="true"
Name="Intense Reference"/>
<w:LsdException Locked="false" Priority="33" QFormat="true" Name="Book Title"/>
<w:LsdException Locked="false" Priority="37" SemiHidden="true"
UnhideWhenUsed="true" Name="Bibliography"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="TOC Heading"/>
<w:LsdException Locked="false" Priority="41" Name="Plain Table 1"/>
<w:LsdException Locked="false" Priority="42" Name="Plain Table 2"/>
<w:LsdException Locked="false" Priority="43" Name="Plain Table 3"/>
<w:LsdException Locked="false" Priority="44" Name="Plain Table 4"/>
<w:LsdException Locked="false" Priority="45" Name="Plain Table 5"/>
<w:LsdException Locked="false" Priority="40" Name="Grid Table Light"/>
<w:LsdException Locked="false" Priority="46" Name="Grid Table 1 Light"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark"/>
<w:LsdException Locked="false" Priority="51" Name="Grid Table 6 Colorful"/>
<w:LsdException Locked="false" Priority="52" Name="Grid Table 7 Colorful"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 1"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 1"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 1"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 1"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 1"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 2"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 2"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 2"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 2"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 2"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 3"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 3"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 3"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 3"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 3"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 4"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 4"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 4"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 4"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 4"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 5"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 5"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 5"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 5"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 5"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 6"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 6"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 6"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 6"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 6"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="46" Name="List Table 1 Light"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark"/>
<w:LsdException Locked="false" Priority="51" Name="List Table 6 Colorful"/>
<w:LsdException Locked="false" Priority="52" Name="List Table 7 Colorful"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 1"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 1"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 1"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 1"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 1"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 2"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 2"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 2"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 2"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 2"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 3"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 3"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 3"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 3"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 3"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 4"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 4"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 4"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 4"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 4"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 5"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 5"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 5"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 5"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 5"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 6"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 6"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 6"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 6"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 6"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 6"/>
</w:LatentStyles>
</xml><![endif]-->
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;
mso-font-charset:0;
mso-generic-font-family:roman;
mso-font-pitch:variable;
mso-font-signature:-536870145 1107305727 0 0 415 0;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;
mso-font-charset:0;
mso-generic-font-family:swiss;
mso-font-pitch:variable;
mso-font-signature:-536870145 1073786111 1 0 415 0;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{mso-style-unhide:no;
mso-style-qformat:yes;
mso-style-parent:"";
margin-top:0in;
margin-right:0in;
margin-bottom:8.0pt;
margin-left:0in;
line-height:107%;
mso-pagination:widow-orphan;
font-size:11.0pt;
font-family:"Calibri",sans-serif;
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-fareast-font-family:Calibri;
mso-fareast-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-bidi-font-family:"Times New Roman";
mso-bidi-theme-font:minor-bidi;}
a:link, span.MsoHyperlink
{mso-style-noshow:yes;
mso-style-priority:99;
color:blue;
text-decoration:underline;
text-underline:single;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-noshow:yes;
mso-style-priority:99;
color:#954F72;
mso-themecolor:followedhyperlink;
text-decoration:underline;
text-underline:single;}
span.GramE
{mso-style-name:"";
mso-gram-e:yes;}
.MsoChpDefault
{mso-style-type:export-only;
mso-default-props:yes;
font-family:"Calibri",sans-serif;
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-fareast-font-family:Calibri;
mso-fareast-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-bidi-font-family:"Times New Roman";
mso-bidi-theme-font:minor-bidi;}
.MsoPapDefault
{mso-style-type:export-only;
margin-bottom:8.0pt;
line-height:107%;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;
mso-header-margin:.5in;
mso-footer-margin:.5in;
mso-paper-source:0;}
div.WordSection1
{page:WordSection1;}
-->
</style><!--[if gte mso 10]>
<style>
/* Style Definitions */
table.MsoNormalTable
{mso-style-name:"Table Normal";
mso-tstyle-rowband-size:0;
mso-tstyle-colband-size:0;
mso-style-noshow:yes;
mso-style-priority:99;
mso-style-parent:"";
mso-padding-alt:0in 5.4pt 0in 5.4pt;
mso-para-margin-top:0in;
mso-para-margin-right:0in;
mso-para-margin-bottom:8.0pt;
mso-para-margin-left:0in;
line-height:107%;
mso-pagination:widow-orphan;
font-size:11.0pt;
font-family:"Calibri",sans-serif;
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;}
</style>
<![endif]--><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026"/>
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1"/>
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal"
style="mso-margin-top-alt:auto;mso-margin-bottom-alt:auto;
line-height:normal"><b><span
style="font-size:12.0pt;font-family:"Times New
Roman",serif;
mso-fareast-font-family:"Times New Roman"">Allan
Sindelar</span></b><span
style="font-size:12.0pt;font-family:"Times New
Roman",serif;mso-fareast-font-family:
"Times New Roman""><br>
</span><a href="mailto:allan@sindelarsolar.com"><span
style="font-size:10.0pt;
font-family:"Times New
Roman",serif;mso-fareast-font-family:"Times New
Roman"">allan@sindelarsolar.com</span></a><span
style="font-size:10.0pt;font-family:"Times New
Roman",serif;
mso-fareast-font-family:"Times New Roman""><br>
New Mexico EE98J Journeyman Electrician<br>
Founder (Retired), <span style="mso-bidi-font-weight:bold">Positive
Energy, Inc<span class="GramE">.</span></span><br>
<b>505 780-2738 cell</b></span><span
style="font-size:12.0pt;font-family:"Times New
Roman",serif;
mso-fareast-font-family:"Times New Roman""><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
</div>
</body>
</html>