<div dir="auto"><div>To follow up on Jerry's note,if the SI is shifting to regulate the incoming charge from the AC coupled inverter, and you don't want this to happen, I believe there is a software switch that will turn this feature off.</div><div dir="auto">And Jerry, have you seen the SI replacement you referred to? Can you say anything else about it?</div><div dir="auto">Howie<br><br><div data-smartmail="gmail_signature" dir="auto">Howie Michaelson<br>NABCEP Certified Solar PV Installer™<br>Sun Catcher, LLC<br>Solar Energy Systems Sales and Service<br>VT Solar Electric Incentive Partner<br>802-272-0004</div><div class="gmail_extra" dir="auto"><br><div class="gmail_quote">On Sep 18, 2017 10:14 PM, "Jerry Shafer" <<a href="mailto:jerrysgarage01@gmail.com">jerrysgarage01@gmail.com</a>> wrote:<br type="attribution"><blockquote class="quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div dir="auto">Luminalt<div dir="auto">As l recall the SI will move the freq around to regulate the SMA inverter, not having a SMA it may be attempting to force the inverter down. You can widen the freq programming on the ABB inverter to prevent the shut down but this will not prevent the volts from bouncing around, you may want to adjust the inverter AC volts to get past the wave.. FYI, SMA will shortly have a replacement for the SI thats 240 vac and alot smarter too.</div><font color="#888888"><div dir="auto">Jerry</div></font></div><div class="elided-text"><div class="gmail_extra"><br><div class="gmail_quote">On Sep 18, 2017 1:26 PM, "Peter Giroux" <<a href="mailto:pgiroux@mindspring.com" target="_blank">pgiroux@mindspring.com</a>> wrote:<br type="attribution"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>





<div bgcolor="#ffffff">
<div><font size="2">August</font></div>
<div><font size="2"></font> </div>
<div><font size="2">  We had something similar happen a few years ago on an 
AC coupled application using a 5048 Sunny Island ( with transformer ) and a 
Sunny Boy 7000. In a grid down scenario the Sunny boy dropped off 
line.  After a few calls with SMA sharing the error codes it 
turned out the Sunny Island was not delivering 60 hertz, not even 59, so we had 
to reprogram the Sunny Boy to recognize and run on 57 hertz.</font></div>
<div><font size="2"></font> </div>
<div><font size="2">  SMA was gracious enough to share the "magic code " and 
walk me through the programming. Once the Sunny Boy was reset to operate on the 
lower hertz range everything worked great. You may have a similar situation, not 
sure if the ABB folks will help with the hertz adjustment but you should give it 
a try before springing for a sunny boy.</font></div>
<div><font size="2"></font> </div>
<div><font size="2">Peter Giroux</font></div>
<div><font size="2">ASAE</font></div>
<blockquote style="BORDER-LEFT:#000000 2px solid;PADDING-LEFT:5px;PADDING-RIGHT:0px;MARGIN-LEFT:5px;MARGIN-RIGHT:0px">
  <div style="FONT:10pt arial">----- Original Message ----- </div>
  <div style="FONT:10pt arial;BACKGROUND:#e4e4e4"><b>From:</b> 
  <a title="august@luminalt.com" href="mailto:august@luminalt.com" target="_blank">August 
  Goers</a> </div>
  <div style="FONT:10pt arial"><b>To:</b> <a title="re-wrenches@lists.re-wrenches.org" href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches</a> </div>
  <div style="FONT:10pt arial"><b>Sent:</b> Monday, September 18, 2017 5:48 
  PM</div>
  <div style="FONT:10pt arial"><b>Subject:</b> [RE-wrenches] Sunny Island grid 
  tie battery back and backup stability issues with ABB</div>
  <div><br></div>
  <div dir="ltr">Hi Wrenches -
  <div><br></div>
  <div>We have an ~3 year old grid tied battery backup system with a SMA Sunny 
  Island 4548 and Power-One (now ABB) PVI-5000 inverter. There is also an 
  Outback PSX-240 to boost the Sunny Island voltage to 240 volts. </div>
  <div><br></div>
  <div>We recently returned to the site for an annual service call and tested 
  the system by simulating a power outage. The Sunny Island kicked in just fine 
  and provided stable voltage for the backup loads. However, the ABB tries to 
  connect and immediately we see that voltage and frequency of the Sunny Island 
  grid start to rapidly fluctuate. I have a feeling that my Fluke meter is not 
  capturing the fluctuations properly, but I was seeing voltage fluctuate in the 
  238 to 242 volt range and frequency rapidly fluctuate between 59 and 61 
  Hz. </div>
  <div><br></div>
  <div>The ABB connects for a minute or two and then gives us a grid out of 
  range error. This occurs when we have lots of irradiance and also under 
  relatively low light conditions. I've already been on the phone with SMA tech 
  support several times and verified that all the Sunny Island settings are 
  good.</div>
  <div><br></div>
  <div>Has anyone else seen this type of instability issue and did you find a 
  fix? We might need to install a Sunny Boy. <br>
  <div class="gmail_extra"><br></div>
  <div class="gmail_extra"><br></div>
  <div class="gmail_extra">Thanks,</div>
  <div class="gmail_extra"><br></div>
  <div class="gmail_extra">August<br clear="all">
  <div>
  <div class="m_-3005531380123884282m_651005448706805140gmail_signature" data-smartmail="gmail_signature">
  <div dir="ltr">
  <div dir="ltr">
  <p><b><span style="FONT-FAMILY:'Century Gothic','sans-serif';FONT-SIZE:9pt">August 
  Goers</span></b></p>
  <p><span style="FONT-FAMILY:'Century Gothic','sans-serif';FONT-SIZE:8pt">Luminalt</span></p>
  <p><br></p>
  <p> </p></div></div></div></div><br></div></div></div>
  <p>
  </p><hr>

  <p></p>______________________________<wbr>_________________<br>List sponsored by 
  Redwood Alliance<br><br>List Address: 
  <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<wbr>org</a><br><br>Change listserver email address & 
  settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/o<wbr>ptions.cgi/re-wrenches-re-wren<wbr>ches.org</a><br><br>List-Archive: 
  <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re<wbr>-wrenches@lists.re-wrenches.or<wbr>g/maillist.html</a><br><br>List 
  rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br><br>Check out 
  or update participant 
bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br><br><p></p></blockquote></div>
<br>______________________________<wbr>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/o<wbr>ptions.cgi/re-wrenches-re-wren<wbr>ches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re<wbr>-wrenches@lists.re-wrenches.or<wbr>g/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div></div>
</div><br>______________________________<wbr>_________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.<wbr>org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/<wbr>options.cgi/re-wrenches-re-<wbr>wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/<wbr>re-wrenches@lists.re-wrenches.<wbr>org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.<wbr>htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br></div></div></div>